West Coast Canuck
New Member
- Joined
- Dec 15, 2020
- Messages
- 36
I am building a 48v 272ah Lishen battery pack with mpp solar Lv6548 in two Phases. Please review my hand made simple schematic and any comments would be greatly appreciated. The 1st phase is one LV 6548 and 120 volt to critical load subpanel. It will have a 16s 48v 272ah battery storage. 2nd Phase will add a second LV 6548 and another 16s 48v 272ah battery backup. All A/C wiring to critical Subpanel and connections to LV 6548 are complete by electrician and are not shown in drawings, solar Panels will start this spring and I will get into the design after Phase 1 and 2. Items needed from members are:
Main T type fuse size I calculate 200amp
Wire size for system I calculate 2/0
Shunt with monitor I calculate 200 amp
Bus bars for Pos and Neg for Phase 1 and 2 I have 48v 300 amp Cllena 4post 3/8 studs
ANL fuse at each LV 6548 I calculate 154a max current * 1.20 =184amp so use 180a fuse
Please any comments would be wonderful !!
Main T type fuse size I calculate 200amp
Wire size for system I calculate 2/0
Shunt with monitor I calculate 200 amp
Bus bars for Pos and Neg for Phase 1 and 2 I have 48v 300 amp Cllena 4post 3/8 studs
ANL fuse at each LV 6548 I calculate 154a max current * 1.20 =184amp so use 180a fuse
Please any comments would be wonderful !!