SMA put out a bulletin, apparently some SB/SI hardware software combinations were experiencing catastrophic hardware failure when used as grid backup. Seems settled now. Just wanted to get some real world input if the REC complicated this.
Have a link? I'd like to read it.
Solar power isn't being pushed, it's being drawn.
If the load goes away. No more power is drawn.
No different from unplugging a vacuum cleaner, without turning it off. Current just stops flowing.
Voltage is "push".
If load has a non-infinite impedance, current flows due to that push. If there is source impedance, voltage is split across source and load impedance.
In a GT PV inverter, current through an inductor helps it deliver a sine wave from PWM switching.
So long as it is connected to a bottomless grid, it pushes sine wave current into sine wave voltage.
In an island grid, the power goes into loads and battery inverter. If load suddenly shuts off, current through inductor causes voltage rise because it sees higher impedance.
Battery inverter can run its own switching power supply and start pulling down current to keep island grid voltage regulated. It (Sunny Island in this case) should do that for a few seconds until it has raised frequency to readjust GT PV output to match reduced load.
If battery can't accept that current (say 100A for 3 seconds), voltage would rise and GT PV inverter might drop offline. But voltage could spike rather high, not sure what inductor would do.
I have AGM so expect it to accept almost anything. Lithium BMS might not. I would think setting target max SoC a bit lower would help.
The Sunny Island raises line frequency and the Sunnyboy(s) reduce output to zero. Battery voltage momentarily raises for the few seconds this takes. This is why SMA spec a certain size battery bank / kw of PV.
100 Ah per kW of PV. Mine is about 1/3 that size.
Sunny boys will be likely set for CA rule 21.
Oh it's normally a grid tie system, but the SI is manually backfed during outages.
Newer Sunny Boys, either Rule 21 for on-grid and grid-backup, or off-grid for strictly off-grid.
Older ones with RS-485 switch between on and off grid parameters. Except, at least some fail to implement all off-grid correctly in this scheme.