Oh my!I started to dig into the bank because this is what I saw when I connected to the BMS (RadioB Tech 4s 120a, model RB-124S120A):
View attachment 229612
I will probably just disassemble the pack and put it back together in the correct configuration with bus bars. I don't see a problem with the fuse but am happy to be corrected.
Wait, so in addition to the weird wiring, one of the (parallel sets of) cells is at zero and two are at 5+ volts? #It'sDeadJimI started to dig into the bank because this is what I saw when I connected to the BMS (RadioB Tech 4s 120a, model RB-124S120A):
View attachment 229612
B- terminal connected to the bank reads 13.2x V, and the C- terminal coming out of the BMS is 12.8x V, so a discrepancy there as well.
I will probably just disassemble the pack and put it back together in the correct configuration with bus bars. I don't see a problem with the fuse but am happy to be corrected.
Yeah, I would certainly recommend paralleling one of each type cell for each position. So each cell group is then one wide post and one narrow post cell.DOH! the two at BOTH ends are different.
Yes please show us how they put panels rated 24v and 12v in series with a 36v parallel.Thank you guys so much for the help. Now to see how they have all the solar hooked up...
BOOM! Replacing the ring terminals on the BMS sense wires fixed the problem! We are in business LOL... everything working normally from what I can see.
Strange how it worked on the 4S setup but not on the 2P4S until the terminals were changed but hey, no complaints. The two battery styles were indeed paired with each other.
Thank you guys so much for the help. Now to see how they have all the solar hooked up...