So, I am not an electrical engineer or an electrician. I have been in home remodeling business for 30 years so I thought I would be capable of a DIY solar power project on my 29 YO Diesel Pusher.
RV world originally with Heart 20D inverter on an inverter loop. Incoming shore power would go to the 100 amp split panel with one circuit getting per from inverter in an "inverter loop". This would power basics plus a microwave directly off one side of inverter.
MY plan: to wire the whole panel from a split phase 5000 watt 24v inverter, to have a 10000 watt battery bank consisting of 8 Lifepo4 100ah 12v batteries wired in series and parallel. I used a 60 amp LiTime MPPT with 6 250 watt Renogy type N panels. Panels in series and parallel 2+2+2.
My system worked great with solar power only and Ran 2 rooftop AC with no problem. Shunt keeping score. However when I plugged into shore power I got smoke and a failure code from the inverter.
Lots to unpack in finding this problem
1. shore power was a 50 amp Nema 1450 R
2. Shore power had a 50 to 30 dog one followed by an inline tester/supressor. Lights on device indicate normal.
3. 25' RV cord with another adapter back to 50 amp gen type plug on rv.
4. Power in goes through auto switch with generator power leads. Generator leads have a go between wire original from manufacturer so not true 240.
5. New 240v inverter input has Ground+Hot+Hot.
Output Has Neutral plus hot plus hot. Case has a ground. Pics below.
6. I have not plugged in with 50/50 cord. Only the 30.
7. Inverter company engineer says failure related to "angle of phase".
8. Bypassed inverter and used RV on shore power.
Trying to not burn up another inverter. I have no 240 devices to power.
RV world originally with Heart 20D inverter on an inverter loop. Incoming shore power would go to the 100 amp split panel with one circuit getting per from inverter in an "inverter loop". This would power basics plus a microwave directly off one side of inverter.
MY plan: to wire the whole panel from a split phase 5000 watt 24v inverter, to have a 10000 watt battery bank consisting of 8 Lifepo4 100ah 12v batteries wired in series and parallel. I used a 60 amp LiTime MPPT with 6 250 watt Renogy type N panels. Panels in series and parallel 2+2+2.
My system worked great with solar power only and Ran 2 rooftop AC with no problem. Shunt keeping score. However when I plugged into shore power I got smoke and a failure code from the inverter.
Lots to unpack in finding this problem
1. shore power was a 50 amp Nema 1450 R
2. Shore power had a 50 to 30 dog one followed by an inline tester/supressor. Lights on device indicate normal.
3. 25' RV cord with another adapter back to 50 amp gen type plug on rv.
4. Power in goes through auto switch with generator power leads. Generator leads have a go between wire original from manufacturer so not true 240.
5. New 240v inverter input has Ground+Hot+Hot.
Output Has Neutral plus hot plus hot. Case has a ground. Pics below.
6. I have not plugged in with 50/50 cord. Only the 30.
7. Inverter company engineer says failure related to "angle of phase".
8. Bypassed inverter and used RV on shore power.
Trying to not burn up another inverter. I have no 240 devices to power.
Attachments
-
f2e50d86-2188-4acf-b2fe-8ab5cecea347.jpg407.9 KB · Views: 9
-
PXL_20250413_204410672.jpg284.8 KB · Views: 9
-
PXL_20250419_144058299.MP.jpg224.9 KB · Views: 11
-
PXL_20250419_144118168.MP.jpg279.2 KB · Views: 10
-
PXL_20250426_125258147.jpg124.2 KB · Views: 9
-
PXL_20250426_125044974.jpg150.7 KB · Views: 11
-
PXL_20250426_124946030.jpg318.8 KB · Views: 11
-
PXL_20250426_125300636.jpg107.5 KB · Views: 13
-
PXL_20250426_125403029.jpg190.4 KB · Views: 13
-
PXL_20250426_125407884.jpg215.4 KB · Views: 14
-
PXL_20250426_124955274.jpg211.5 KB · Views: 13
-
PXL_20250426_125154178.jpg193.3 KB · Views: 11