I agree, but if a ground from the utility meter goes to the main panel and to the growatts then we have the same issue that Ian’s video showed with the neutral circling amps due to varying 120v loads.As shown, if a fault develops in a GroWatt (or AC In panel, or AC Out panel, or Load panel),
and "L1" shorts to chassis, chassis of all those devices goes to 120VAC.
The only path back to utility meter is through the earth. Your added ground rod is at 120VAC, ground rod by utility meter is zero volts. Current flows, but not enough to trip a breaker feeding GroWatt (Faults downstream of GroWatt might trip a breaker or shut off GroWatt, but faults through AC Input of GroWatt will not.
The earthworms will frantically wriggle to the surface.
I believe this is wrong. A ground wire from utility meter providing continuity to case of GroWatt case is required, so fault causes breaker to clear.
what is suggested to do this right. Was it an isolation transformer?