Hello,
I've got an existing DIY set of 48v LiFePO4 batteries with a JK Inverter BMS on each. (4 total batteries) They're also in closed loop communication with my Sol-Ark 15k. I'm looking to add 2 more of the same type battery to my setup and I'm looking for a safe way to add them without taking my system offline.
I've got a victron lynx power for my buss and will be adding another. Each battery connection is fused at that point. The BMS is set to limit charge/discharge to 100a for each pack. The batteries also have a disconnect on them and the new cables will be the same length as the original.
Here is my plan: (During a period of low battery use. I'm thinking around 1pm on a nice day when the batteries are full and there's plenty of sun left.)
I've been through this in my mind a few times and it seems like this is a safe way to add the batteries without taking down my system.
Thoughts?
I've got an existing DIY set of 48v LiFePO4 batteries with a JK Inverter BMS on each. (4 total batteries) They're also in closed loop communication with my Sol-Ark 15k. I'm looking to add 2 more of the same type battery to my setup and I'm looking for a safe way to add them without taking my system offline.
I've got a victron lynx power for my buss and will be adding another. Each battery connection is fused at that point. The BMS is set to limit charge/discharge to 100a for each pack. The batteries also have a disconnect on them and the new cables will be the same length as the original.
Here is my plan: (During a period of low battery use. I'm thinking around 1pm on a nice day when the batteries are full and there's plenty of sun left.)
- Get all the settings on the 2 new batteries/bms correct and set charge/discharge to disabled.
- Connect the 2 new batteries to the bus and make sure the inverter communication is working.
- Make sure the original battery packs are all at 100%.
- Disable discharge on 3 of the previous battery packs.
- Close the disconnect on the new batteries.
- Enable discharge on the new batteries. (This allows my Sol-Ark to still operate off the batteries without seeing interruption.)
- Disable discharge on the last original battery.
- Enable Charge on the new batteries. (The new batteries will now be charging from PV.)
- Wait till everything says 100% / no real current flow.
- Enable discharge on the original batteries.
- Sit back and smile at 50% more capacity.
I've been through this in my mind a few times and it seems like this is a safe way to add the batteries without taking down my system.
Thoughts?