Hello everyone!
I've had quite a lot of interest in adding these Schneider Insight devices to Schneider solar installations that don't have them. Many of the clients have either EG4 Lifepower or EG$_LL V2 batteries, and without the Insight they can't make SOC determinations for starting the Generator or system shutdown etc.
Anyways, I've successfully gotten the Insight to work with the Conext XW+, the XWPro and with both of the EG4 battery types LifePower4 and EG4_LL V1 and V2.
However, I'm running into an issue and I'm hoping the community might be able to help me.
I have a installation let's call it "site 3" and at this site, the owner has a Connext XW+ with 6 EG4_LL V2 batteries. I have the Insight Home with firmware 1.18 which I believe is required to support EG4 batteries in closed loop. (I'm realizing that the download below the one I have highlighted says XW+ systems
)

Anyways... everything is working pretty good, the system is reporting SOC from the batteries and it's able to be accessed via the mobile and website versions of Insight cloud.
The issue I have is that when I enable the BMS to control the charge controllers the system shuts down saying it's exceeding the discharge value.
When I enable this.

I get this.

The challenge is when I look at the BMS data we're clearly way less than the maximum discharge current of 400 amps.

The unit then shows this error and shutdown power to the loads.
On the systems with the XWPro, I have this enabled and there is no issue, so I'm confused at why it doesn't work with the "Connext XW+" inverters also.
Anyways, if anyone has run into this before or has any ideas I'd really appreciate the help.
Thank you!
I've had quite a lot of interest in adding these Schneider Insight devices to Schneider solar installations that don't have them. Many of the clients have either EG4 Lifepower or EG$_LL V2 batteries, and without the Insight they can't make SOC determinations for starting the Generator or system shutdown etc.
Anyways, I've successfully gotten the Insight to work with the Conext XW+, the XWPro and with both of the EG4 battery types LifePower4 and EG4_LL V1 and V2.
However, I'm running into an issue and I'm hoping the community might be able to help me.
I have a installation let's call it "site 3" and at this site, the owner has a Connext XW+ with 6 EG4_LL V2 batteries. I have the Insight Home with firmware 1.18 which I believe is required to support EG4 batteries in closed loop. (I'm realizing that the download below the one I have highlighted says XW+ systems


Anyways... everything is working pretty good, the system is reporting SOC from the batteries and it's able to be accessed via the mobile and website versions of Insight cloud.
The issue I have is that when I enable the BMS to control the charge controllers the system shuts down saying it's exceeding the discharge value.
When I enable this.

I get this.

The challenge is when I look at the BMS data we're clearly way less than the maximum discharge current of 400 amps.

The unit then shows this error and shutdown power to the loads.
On the systems with the XWPro, I have this enabled and there is no issue, so I'm confused at why it doesn't work with the "Connext XW+" inverters also.
Anyways, if anyone has run into this before or has any ideas I'd really appreciate the help.
Thank you!