I am missing what is in paralleled in your comment.
the Pro does qualify incoming AC before syncing to it. If it does not pass vetting, it won't sync. As to actually vetting mechanics, IDK
Based on experience with the older XW+ model, the Schneider does not shut down it just does not qualify the Gen input on AC2, the relay does not close so power comes from only from batteries (and solar if you are DC coupled and have charge controllers) until the batteries reach the LBCO setting. On the XW+ there are user settings in the AC Settings menu for high & low voltage limits as well as high & low frequency limits.If so, what are the specific cutoff points where the Schneider box shuts down?
Being old school, MSW doesn’t have a lot of appeal to me and a lot of the genjunk I see still appears to be on a race to the bottom.I would take the money you would spend on a separate charger and buy a sinewave generator.
One of the advantages of XW inverter is it has good efficiency and AC input power factor when charging from AC input source.
Most lower cost chargers have just rectifier-filter capacitor AC to DC input conversion. They have very poor AC input power factor and not too great input to output conversion efficiency.
Yes! Back in the 80s I worked for a pipeline where we built batt rooms w sixty 2v C&D 1000ah cells and those old chargers were lucky to make 0.6pf and they buzzed you crazy. Techs hated tending all of it but they worked rock solid. ?Understand what a poor power factor charger means before you go shopping for a charger.
Ah, perfect. Excellent diagram!Inverter is operating in parallel with AC input once sync'd and pass-through relay closes. XW has two sets of ACin relays and two separate AC inputs, typically for grid input and generator input, but only one is used at a time, with AC1 (grid input) taking priority if both AC inputs are present.
View attachment 117802
'qualify' is a pretty general term.
The LF inverter really only synchronizes zero crossing and rms voltage, before it closes pass-through relay. It may not connect if the rms voltage, or frequency, of the input source is out of range of inverter tracking limits.
Other common reason for not connecting is with a synchronous conventional generator which output frequency is dependent on engine rpm. Inverter phase tracking is slow, purposely, to avoid sudden phase shifting on inverter AC output. When a synchronous generator engine rpm governor control is unstable causing engine rpm to vary the inverter will be unable to track and lock to it.
Once it does connect, if AC input waveform is so different from inverter's sinewave, it will cause overload current spikes on inverter that will be detected and cause it to open the pass-through relay releasing from the AC input connect.
Same thing happens when grid goes down or glitches. It overloads inverter causing it to disconnect pass through relay.
It will then start the sync, connect, overload, and release process all over again.
Flashing ACin green LED mean AC voltage detected, and inverter synchronizing in process. Farther away AC input frequency is from inverter span range center frequency, the longer this sync'g time will be.
Solid ACin green LED (along with 'clunk' of relay) happens when pass-through relay connects.
There are even more things involved. Here is a short course on XW hybrid inverters.Ah, perfect. Excellent diagram!
This raises two possibly obvious questions:
1. If there is no grid and no gen on the XW Pro’s two AC inputs, I presume there is a mode where the relays get locked out and the inverter can operate in off grid mode … correct?
2. With grid or gen pwr qualified, relays pulled in and the inverter actually synchronized/paralleled directly with the source, what keeps inverter current from flowing back to the grid or genset?
(This also seems particularly important in the situation where there would be a relay driver failure (or stuck software bit), putting 220 back on the pwrco transformer, heating up the primary voltage back where a lineman is clearing a tree break.)
Schneider Engineers have to have a fail safe mode in here somewhere. Presuming something like the software looks for current sense indication of energy flowing back into to inputs and shutting down the inverter entirely. I’d like to hear
a Schneider XW Engineer explain how their software/hardware design here fills the safety bill.
I appreciate your assist!!!
B
Do not use a modified sinewave input to a hybrid sinewave inverter.
Hybrid inverters synchronize to AC input before closing connect relay and inverter runs in parallel with AC input.
Paralleling a hybrid sinewave inverter from a modified sinewave source input will cause high current spikes in both inverter and MSW source.
Have you went to AC settings and looked at AC2 there you can adjust high and low voltage and frequency. Seems like you also have to set the breaker size for generator. Hope this helps.RCinFLA - from pix & comments you’re obviously knowledgeable...
Are you familiar w/ Schneider XW Pro AC2 issue of not qualifying? I have a small off-grid sys w/ 2 XW Pro inverters. I haven’t connected charge controllers. Too late in season.
My master-slave config works. My batter bank is working. I can pull power from battery bank factory pre-charge through inverters to power house but I can’t get inverter to qualify AC2 generator as source to charge batteries. Some say to switch generator to AC1 but that doesn’t make sense given Schneider was supposedly designed off-grid. Any ideas on settings?
Yes. I have. Thx.