No-one-&-Not-Important
From Nebulae to Neighbors: One Photon at time!
Note: NO affiliate links below; just highlighting which products I'm using.
*** IMPROVEMENTS MADE SINCE ORIGINAL POST BASED ON COMMENTS ***
Thanks
@TM48 &
@green-river @CJ Solar for the notes.
in advance.
_______________________________________
Location: San Jose, CA, PoCo: PGE (
).
Profession: DIYer, Electrical Engineer + Product Manager (SW/HW) in hi-tech
Environment: Zero shading
Battery Draw: Current model implies max battery current/power: <61A (maximum of 7.3kW)
Phase 2: Connect PoCo as AC input; PoCo will be generator backup
To bypass PoCo rules & procedures legally, I'll install a new interior load center (LC) in the garage (~3ft from exterior LC) & move all circuit breakers from exterior to interior LC. PoCo feed remains connected to old LC (with no circuits). By designing to minimize grid dependence, I'll need <100 kWh/year from a generator (over 46 hour period across 7 days, occurs when battery SOC is 20%; calculated using a "1h granularity" model, 24hrs x 365days PVWatts data, weather data from past 10 years to estimate hourly granularity gen vs property consumption data from the past THREE (3) years). I'll have to refill the generator ~7x (part of maintenance anyway). Is it cost effective? $4/gallon for 8kWh ~equivalent to PoCo $0.50/kWh's fees.
Read the following threads
1. https://diysolarforum.com/threads/12000xp-off-grid-setup-overloads.95717/
2. https://diysolarforum.com/threads/eg4-12000xp-off-grid-option.92732/
*** IMPROVEMENTS MADE SINCE ORIGINAL POST BASED ON COMMENTS ***
Thanks


- CRITICAL: Upgrade from 28kWh to 64kWh battery capacity to ensure you have enough current coming from batteries to power loads
- Be conservative in how close you get to inverter peak (and surge). It's one way to wear them out quickly.
- Use a combiner LC for both inverters to enable powering down the inverters one at a time for maintenance; requires loading and storing two configs for each inverter so one can be running even if other is down.
- Balance strings better; 9-10 panels per string
- Add batteries in parallel to BOTH inverters via busbar so they can be charged by both
- 12000XP can't pull from battery and AC input simultaneously. So plan accordingly.
QUESTIONS
- Re: my config (below), would you please share warnings, comments or "gotchas" (e.g.: monitoring, batteries, FW, AHJ issues, etc...)?
- Besides what's in the 12000XP spec (read it), has anyone had experience with the AC input function on the 12000XP and its limitations?
- Any one have PoCo issues with 12000XP import only?
- What happens when voltage exceeds the MPPT operating voltage range spec (385V) but is below the max of 480V?
- Does anyone know what the 12000XP battery surge spec (couldn't find it in the spec sheet)?

_______________________________________
Location: San Jose, CA, PoCo: PGE (

Profession: DIYer, Electrical Engineer + Product Manager (SW/HW) in hi-tech
Environment: Zero shading

SYSTEM & USAGE DESCRIPTION (EDITED GIVEN BELOW FEEDBACK)
System
- Inverter: 2x 12000XP
- Battery: 4 x 16kWh batt (DIY, All 4 connected to inverters)
- Solar PV: 14.4kW (Hyperion 400W x 36, 4 strings: 1 x 2.4kW + 3 x 4kW strings), Voc = 37.1V/panel up to 41.7V at -8°C/18°F.
- Generator: 2kW generator which can supply 1kW for 8 hr sustained, reviewed in detail here incl. engine wear, has clean sine wave output.
Battery Draw: Current model implies max battery current/power: <61A (maximum of 7.3kW)
ONE PHASE INSTALL - TWO PHASE TO CONNECT GRID
Phase 1: I will install inverters, batteries and solar PV panels. And connect to a NEW interior load center (LC). I will move all property circuits to interior LC from current main+meter LC (on the exterior). There will be no grid connection to interior LC or inverter. I will operate after City AHJ approval. I will use generator to supplement battery power when neededPhase 2: Connect PoCo as AC input; PoCo will be generator backup
MAIN OPERATING MODE
- Solar PV provide energy to non-battery LOADS --> store excess solar PV energy in batteries
- When batteries at 100%, DO NOT EXPORT to PoCo (ZERO EXPORT)
- When no Solar PV energy, use batteries for non-battery LOADS until battery SOC is 20% --> Use generator to charge batteries
- [Phase 2] Draw energy from PoCo to supply LOADS as a backup to the generator
To bypass PoCo rules & procedures legally, I'll install a new interior load center (LC) in the garage (~3ft from exterior LC) & move all circuit breakers from exterior to interior LC. PoCo feed remains connected to old LC (with no circuits). By designing to minimize grid dependence, I'll need <100 kWh/year from a generator (over 46 hour period across 7 days, occurs when battery SOC is 20%; calculated using a "1h granularity" model, 24hrs x 365days PVWatts data, weather data from past 10 years to estimate hourly granularity gen vs property consumption data from the past THREE (3) years). I'll have to refill the generator ~7x (part of maintenance anyway). Is it cost effective? $4/gallon for 8kWh ~equivalent to PoCo $0.50/kWh's fees.
Read the following threads
1. https://diysolarforum.com/threads/12000xp-off-grid-setup-overloads.95717/
2. https://diysolarforum.com/threads/eg4-12000xp-off-grid-option.92732/
Last edited: