8800 ÷ 48 =184.4 so 193amp breaker if you can find one if not 200amp, wire calc with a 3% drop at 2meter runs says AWG4/0 so 107mm² which seems madness lemme check a decent sourceHi All,
Can anyone please tell me what breaker did they use between Seplos battery pack (304A) to the Sunsynk 8.8kw and what cable size?
They who?Hi All,
Can anyone please tell me what breaker did they use between Seplos battery pack (304A) to the Sunsynk 8.8kw and what cable size?
I meant you (corrected)They who?
I'll translate I well versed in English.Hi All,
Can anyone please tell me what breaker did you (corrected) use between Seplos battery pack (304A) to the Sunsynk 8.8kw and what cable size?
I use a 250a MCCB for my 12k sunsynk, as I have 2 and they never pull their full pull.I'll translate I well versed in English.
Hello wonderful forum members,
Can you please explain to me what breaker and cable size I should use between a 304amp Seplos battery and a 8.8kw Sunsynk inverter?
these are the ones i use, they are a bit "on the edge" as your inverter can pull 240 Amps, but i am fine with the 10A buffer...@SeaGal
@houseofancients
i am now ready to add my second seplos mason 280L battery (ive been very busy with other stuff!) i would like it up and running now we're getting into the UK winter, to take advantage of the overnight low tariff - i will then have 28.6kw at 48v - would your recommendation be for the https://a.aliexpress.com/_EHQA65h 250A please? Thanks
actually , mine are 12kthanks for the fast response, my inverter is 5kw, not 8kw, though i would like to upgrade to 8kw in the future, so 'future proofing' is def on the agenda
For a 5 kw 95mm is overkill..95mm cable?? That's massive isn't it?
Will 95mm fit into the connections on the Sunsynk? I was looking at using at least 35mm or even 50mm cable, but 95mm???
@houseofancients
LOL... I assume he meant 95mm²95mm cable?? That's massive isn't it?
Unfortunately they're quoting one month delivery to the UK, can you suggest an option I can order a lot quicker pleaseI use a 250a MCCB for my 12k sunsynk, as I have 2 and they never pull their full pull.
These a bi directional