I'm starting to regret my purchase after watching Will's review, but at this point it is what it is. We are off-grid and living in our rv trailer while we build our house. I purchased the 6000ex instead of the 6500 expecting that I could use a single one to power everything and then bought a second one as backup in case the first one went down. The only thing we actually need 240 for right now is our well pump which is only run for a few hours at a time once or twice a week. Unfortunately, though, a single RV A/C unit jumps the output capacity over 75%! We have a second trailer here and visitors coming soon to help work with us and I'm sure they'll want the A/C on in that trailer, too. Even turning on the microwave, blender, or toaster while the A/C is on can flip it out. I guess I should have just gone with 2 6500s.

But now this is our situation.

So in order to power the second A/C unit without killing everything I think I need to set up what was supposed to be the backup inverter. For someone who's never dealt with solar or anything much electrical, though, I'm having a really hard time figuring out how to put the second inverter up. I've read the manual, I've watched videos, but I'm still lost. Do I have to have the batteries connected to both inverters or can I just have them going to one? If both: I have 4/0 cable running from my batteries to my first inverter - do I need to also use 4/0 cable going to the second?

I'm sorry, I'm just frustrated with the system and confused about what to do.
 
Do you have microair soft starters on your A/C? Most RV A/C run about 1500W continuous, but their surge can be brutal - 5X that. Microair soft starters significantly reduce the startup surge.
I don't. But the 75% is showing while running, not just at startup
 
If the well pump is the only 240V load then the RV A/C is 120V? The 75% load value may be based on a capacity percentage for that leg only. So the calculation would be 3000W x 0.75 = 2,250W which would be closer to the expected consumption for a roof top RV A/C.

Theoretically, if the 2nd AC was connected to the other leg and neutral you could run both units at the same time. Soft starters would be essential at that point.
 
If the well pump is the only 240V load then the RV A/C is 120V? The 75% load value may be based on a capacity percentage for that leg only. So the calculation would be 3000W x 0.75 = 2,250W which would be closer to the expected consumption for a roof top RV A/C.

Theoretically, if the 2nd AC was connected to the other leg and neutral you could run both units at the same time. Soft starters would be essential at that point.

I totally overlooked that... very good points.
 
If the well pump is the only 240V load then the RV A/C is 120V? The 75% load value may be based on a capacity percentage for that leg only. So the calculation would be 3000W x 0.75 = 2,250W which would be closer to the expected consumption for a roof top RV A/C.

Theoretically, if the 2nd AC was connected to the other leg and neutral you could run both units at the same time. Soft starters would be essential at that point.
Oooh I love that idea! So have trailer 1 out of breaker 1 connected to L1 from the inverter, then trailer 2 out of breaker 2 connected to L2 from the inverter?
 