Shipping Container Kitchen Mod

TimmehTim

New Member
Joined
Apr 23, 2022
Messages
61
I'm building my mother a kitchen out of a shipping container. She wants solar power so I thought I'd make it happen.

Building a 48V 5kw system with a PowMr hybrid all in one inverter charger. Are my basics on the diagram correct?
 

Attachments

  • KitchenSolar.jpg
    KitchenSolar.jpg
    399 KB · Views: 45
Your fuse is a little small for a 5Kw system. Go with 5000w / 48v = 104a * 85% efficiency loss = 120a * 120% overhead = 144a, round to 150a to avoid bogus annoying trips/pops. A breaker would probably be better so you can disconnect the 48v if needed.

Remember, that fuse putting power INTO the battery is the same fuse for power coming OUT OF the battery.

You're also going to want 150a Class-T fuses on each battery bank. Worst case scenario you can disconnect 1 bank and still have full wattage at half the run time while you're waiting for a replacement battery.

Might help to have a breaker for your PV if you can find a 600v DC rated 15a for servicing and troubleshooting.

Have you picked out the batteries yet and verified their BMS's/specs say they can be connected up the way you want?


Other than that it looks pretty simple and straight forward. I'm guessing you're going to feed the AC into a breaker box?
 
Last edited:
After posting this I read the recommended connections for the PowMr.
PowMr recommends a 25a DC 2-pole breaker between the panels and inverter. They recommend a 200a DC 2-pole breaker between the batteries and inverter. And they recommend using a 63a AC 2-pole breaker before the breaker box.

With respect to the Class T fuses on each string of batteries, could I use a 150a breaker instead?

I'll be using MightyMax ML4D-LI. I assumed they could be configured any way. I cant find specs on the BMS.
 

Attachments

  • KitchenSolar.jpg
    KitchenSolar.jpg
    463.1 KB · Views: 13
PowMr recommends a 25a DC 2-pole breaker between the panels and inverter. They recommend a 200a DC 2-pole breaker between the batteries and inverter. And they recommend using a 63a AC 2-pole breaker before the breaker box.
Seems fair if a little large on the battery breaker. I wouldn't argue with any of that other than 63a is WWAAYYY too big for a 10a array.


With respect to the Class T fuses on each string of batteries, could I use a 150a breaker instead?
The concern is that when an ANL fuse breaks, it forms a small gap between the terminals inside. With the amount of power a LFP battery can dump instantaneously that could jump that air gap and continue to feed the short/burn/whatever that was causing the problem.

Class-T and the like are rated to have a much larger air gap (respectively) and can stop that current from jumping the terminals. The fuse is there to protect the wire, not the device.

I'll be using MightyMax ML4D-LI. I assumed they could be configured any way. I cant find specs on the BMS.
That's not going to work. According to their web page :
Designed to be used in parallel with a maximum of 4 identical batteries. Do not connect in series.

So, back to the drawing board with that one.
 
well aint that a b!t(h... I hope they'll let me cancel the order and order the right batteries. I did advise them what I was ordering the batteries for and they didnt stop me. Thanks for catching it.
 
I wouldn't argue with any of that other than 63a is WWAAYYY too big for a 10a array.
The 63amp breaker that they recommend is on the AC output side. The PV has a 25A breaker.
The concern is that when an ANL fuse breaks, it forms a small gap between the terminals inside. With the amount of power a LFP battery can dump instantaneously that could jump that air gap and continue to feed the short/burn/whatever that was causing the problem.

Class-T and the like are rated to have a much larger air gap (respectively) and can stop that current from jumping the terminals. The fuse is there to protect the wire, not the device.
Would a Blue Sea 285 series 150A breaker be better than a fuse?
 
You really should get 48V batteries. So much simpler and easier than putting 4 12V batteries in series. Probably a lot cheaper too. Will has a page on these:


For a 48V LiFePO₄ battery bank you definitely want a Class T main battery fuse close to the batteries. 5000W / 48V / 85% = 122A. Use 1AWG or 1/0AWG between the batteries and inverter. The fuse should be 150A though a 200A Class T would work fine on 1AWG or larger. Using a 200A breaker could be added as well to act as a disconnect switch. Just make sure it is DC rated for at least 60VDC.

The PV breaker is only there to act as a disconnect. Make sure it is a breaker rated for at least 600VDC (or more). Any amperage over 25A is fine since it is not there to protect the wire, just act as a disconnect.
 
You really should get 48V batteries. So much simpler and easier than putting 4 12V batteries in series. Probably a lot cheaper too. Will has a page on these:

For a 48V LiFePO₄ battery bank you definitely want a Class T main battery fuse close to the batteries. 5000W / 48V / 85% = 122A. Use 1AWG or 1/0AWG between the batteries and inverter. The fuse should be 150A though a 200A Class T would work fine on 1AWG or larger. Using a 200A breaker could be added as well to act as a disconnect switch. Just make sure it is DC rated for at least 60VDC.

The PV breaker is only there to act as a disconnect. Make sure it is a breaker rated for at least 600VDC (or more). Any amperage over 25A is fine since it is not there to protect the wire, just act as a disconnect.
I will be purchasing 4 of the EG4 LifePower4 batteries to solve my battery issue. I've also included a 200a Class T Fuse at the battery.
For the battery bank I will be using 3/0 wire as I already have a bit of it. From the battery to the inverter I will use 1/0 wire.
 

Attachments

  • KitchenSolar.jpg
    KitchenSolar.jpg
    449.8 KB · Views: 8
Besides putting the 4 48V batteries in parallel instead of series, I would also avoid having the main battery fuse and the inverter disconnect breaker being the same amperage. I'd use a 150A Class T fuse and then you can keep the 200A 2-pole DC breaker. At that point the breaker is only there to act as a disconnect. Also, make sure the Class T fuse and the breaker are rated for at least 60VDC. A lot of fuses and breakers can't be used on 48V system that actually get close to 60V when charging.

What is the point of the 2-pole 63A AC breaker? The AC breaker panel should have a main breaker and then a set of branch breakers. The 2-pole breaker seems redundant with the main breaker.

Your diagram only shows 2 wires for the AC side. Remember that AC has three wires, typically black, white, and green.
 
What is the point of the 2-pole 63A AC breaker? The AC breaker panel should have a main breaker and then a set of branch breakers. The 2-pole breaker seems redundant with the main breaker.
I believe that breaker would then continue on to feed the lugs inside the breaker box rather than feeding into another breaker. If he went breaker to breaker then the 63a called for would be the one plugged into the power panel, but that would put the L1 and N lines on either leg... bad thing.

@TimmehTim IIRC that unit is a single leg of 120v power and a Neutral line. If you feed that to a standard breaker panel you'll need to install a jumper between the 2 main legs to feed both sides OR just use 1 side of the panel and ignore the other side. The Neutral wire and the Ground wire screw from the AIO will have their own bus bars inside the panel to connect to.
 
Besides putting the 4 48V batteries in parallel instead of series, I would also avoid having the main battery fuse and the inverter disconnect breaker being the same amperage. I'd use a 150A Class T fuse and then you can keep the 200A 2-pole DC breaker. At that point the breaker is only there to act as a disconnect. Also, make sure the Class T fuse and the breaker are rated for at least 60VDC. A lot of fuses and breakers can't be used on 48V system that actually get close to 60V when charging.
Does a breaker not have enough of an air gap to prevent arcing once its blown? Would a breaker alone not provide enough protection?
What is the point of the 2-pole 63A AC breaker? The AC breaker panel should have a main breaker and then a set of branch breakers. The 2-pole breaker seems redundant with the main breaker.
I plan on using the 63a breaker as my main breaker and I will have four (4) 15amp breakers in a subpanel.
Your diagram only shows 2 wires for the AC side. Remember that AC has three wires, typically black, white, and green.
Yes. The panel only provides a Live (L) and a Neutral (N) connection. The grounding line is ran separately apparently.
 
I believe that breaker would then continue on to feed the lugs inside the breaker box rather than feeding into another breaker. If he went breaker to breaker then the 63a called for would be the one plugged into the power panel, but that would put the L1 and N lines on either leg... bad thing.

@TimmehTim IIRC that unit is a single leg of 120v power and a Neutral line. If you feed that to a standard breaker panel you'll need to install a jumper between the 2 main legs to feed both sides OR just use 1 side of the panel and ignore the other side. The Neutral wire and the Ground wire screw from the AIO will have their own bus bars inside the panel to connect to.
The subpanel I have only has 1 Live leg, so this will be perfect... i think... right?
 
Not being provided a grounding lug... how are my appliances going to be grounded? Is this where I need a ground rod dug into the ground??
 

Attachments

  • 20220528_135545.jpg
    20220528_135545.jpg
    178.6 KB · Views: 4
Does a breaker not have enough of an air gap to prevent arcing once its blown? Would a breaker alone not provide enough protection?
A 48V LiFePO₄ battery can push out a huge amount of current if there was a short. A Class T fuse is the best defense against that high current. With that fuse in place there is no need for the breaker at all other than if you want to use it as a disconnect.
 
Still showing it all series-connected for the batteries. You need all the reds connected to each other and all the blacks connected to each other, not red->black.
Are looking at the solar panels in that diagram? The diagram in post #14 shows the 48V batteries in parallel and the solar panels in series.
 