My current system is a Sol-Ark 15k with 36 solar panel (10 year old) with two EG4 battery and it is running great, but the Center Point of Energy, a Houston utility company, disapproved my distributed generation (DG) application because the service disconnect which I am using as described in the subject title.
The argument of the utility company is that it is invisible to the service personnel as follows: "Complainant' s Exceptions state that his proposed disconnect device should be approved, because it has a visible on-off switch. He does not dispute that the actual break is enclosed in a molded plastic case and not visually accessible. Only distributed generation disconnect mechanisms that have a visual break are permitted by the Commission' s rule 16 TAC § 25.212(b)(8) to be connected to a utility's electrical system."
Just wonder if anyone can figure out what the utility company, Center Point of Energy, is saying?
The argument of the utility company is that it is invisible to the service personnel as follows: "Complainant' s Exceptions state that his proposed disconnect device should be approved, because it has a visible on-off switch. He does not dispute that the actual break is enclosed in a molded plastic case and not visually accessible. Only distributed generation disconnect mechanisms that have a visual break are permitted by the Commission' s rule 16 TAC § 25.212(b)(8) to be connected to a utility's electrical system."
Just wonder if anyone can figure out what the utility company, Center Point of Energy, is saying?