There should be no issues with this. In an AC coupled system, it's essentially treated as a completely off grid system.Can I use one of these together with an AC Coupled system, for example Enphase IQ7+ Microinverters?
I have 13.2kw of inverter capacity, all Enphase
enphase put in a lock code on the iq7 not sureThere should be no issues with this. In an AC coupled system, it's essentially treated as a completely off grid system.
I'll research, wasn't aware they did this.enphase put in a lock code on the iq7 not sure
I didn't think so.we do not have that on this model
I think you can. But, you (or apparently SigSolar) have to figure out how the unit handles N-G Bond and then maybe make some wiring changes or remove a bonding screw?Wait, What? so that means that we cannot connect the inverter grid-tie & have Automatic UPS backup?
If I understand the manual correctly, less than 325a imbalance at full load? What about half loads or 1/4 loads?Quite interested in a pair of these to run my house (normal 200a split phase service).
What's the maximum imbalance between each leg?
Ie, can I have 3000 watts on one inverter and 5000 on the other?
What's the maximum surge capacity and time?
My well pump pulls ~37a inrush on each leg, 4440 watts; runs ~9a. Will it have any issues with this?
They would be wired as the primary feed to my main panel, feeding 2 subs. Grid would be fed to the inverters for backup / support only.
Also interested how they would handle table saws, miter saws and a 240V 1.5hp air compressor, obviously not all running at the same time.
Very simple there are videos out there I used the micro Airsoft start. Make sure you turn off the disconnect for your AC do not touch the top of the capacitors. and you're good to goAny idea how easy this is to do, or do I need to get an electrician so he could charge me an arm and a leg?
I believe the phases are not shared, in that each leg would just be dependent on the capabilities of that inverter. So you could have L1 at 0w and L2 at 6000w with no issues. You could add an autotransformer at the panel to help with a leg that exceeds the limit of the inverter so same scenario, 0w on L1 but 9000w on L2. The AT would allow L1 inverter to add 3000w to L2. Again this is just a guess based on the setup & type of inverter (single phase, 120v)If I understand the manual correctly, less than 325a imbalance at full load? What about half loads or 1/4 loads?
If the specs are correct it will handle the well pump, but how much imbalance will they tolerate?
If I were running 2,000w on L1, 3,500w on L2 and the well pump kicked on pulling a brief ~4,400w on each leg would the inverters handle it? Assuming ample battery and grid connected with solar / bat as priority.
nothing to do with any of that I was referring to sell-back hybrid,I think you can. But, you (or apparently SigSolar) have to figure out how the unit handles N-G Bond and then maybe make some wiring changes or remove a bonding screw?
As far as regulatory approval goes, there isn't a difference between ETL, TUV, and UL listings. Inspectors treat them equally as they are all approved by the US Government as NRTLs. The inverter has TUV certification.
Maybe a conflict of interest given there is now an affiliate link on the inverter. Agree with @robby some one is going to get screwed by their town if they demand that the equipment is listed vs tested to ul specs.. anyone pulling a permit for an install would be best suited to get pre approval prior to purchase.Just a warning you guys that are thinking of buying this Inverter to get it Grid Tied and certified by your local power company, you better make sure it will pass before you drop the money and find out something different.
The 6500EX is not UL Listed as @Will Prowse claimed in his first video, only the EG4 LifePo4 Battery pack is UL listed. The EG4LL is not UL Listed.
I am a member of the UL Database so I looked it up. I noticed in Wills second video he carefully says when referring to the Inverter and Battery and says "Everything you see on this wall is either UL listed or Compliant". That is now an accurate statement since the Inverter is compliant but is not listed. Therefore it is not going to Pass any kind of Inspection is if it not listed in the UL database.
This comes from another thread.
It's kind of funny you say that Richard because the MPP LV6548 has been TUV certified for a long time and everybody has stated that you cannot get it Grid certified because it is not UL listed. People including Will Prowse.
_________________________________________________________________________________________________________________________
View attachment 95993
_____________________________________________________________________________________________________________________________
Now all of a sudden because SS is selling it, that same certification will work. Can we get a pledge from Signature Solar that if it cannot be certified that all the customer who bought it based on that claim will get back their money?
Just a warning you guys that are thinking of buying this Inverter to get it Grid Tied and certified by your local power company, you better make sure it will pass before you drop the money and find out something different.
The 6500EX is not UL Listed as @Will Prowse claimed in his first video, only the EG4 LifePo4 Battery pack is UL listed. The EG4LL is not UL Listed.
I am a member of the UL Database so I looked it up. I noticed in Wills second video he carefully says when referring to the Inverter and Battery and says "Everything you see on this wall is either UL listed or Compliant". That is now an accurate statement since the Inverter is compliant but is not listed. Therefore it is not going to Pass any kind of Inspection is if it not listed in the UL database.
This comes from another thread.
It's kind of funny you say that Richard because the MPP LV6548 has been TUV certified for a long time and everybody has stated that you cannot get it Grid certified because it is not UL listed. People including Will Prowse.
_________________________________________________________________________________________________________________________
View attachment 95993
_____________________________________________________________________________________________________________________________
Now all of a sudden because SS is selling it, that same certification will work. Can we get a pledge from Signature Solar that if it cannot be certified that all the customer who bought it based on that claim will get back their money?