PaulLad New Member Joined Jul 14, 2020 Messages 173 Jan 9, 2024 #1 So if your wire supports 20A (12ga) but you have a 10A inverter, the fuse should be 25-30A correct?
J JJJJ Aspiring apprentice Joined Feb 25, 2021 Messages 1,592 Jan 9, 2024 #2 Fuse should always be lower than wire. Fire prevention.
OffGridInTheCity Solar Wizard Joined May 23, 2021 Messages 2,143 Location Southern Oregon Jan 9, 2024 #3 12ga = 20a breaker (not 25-30a). As @JJJJ said, a fuse or breaker is to protect the wire! (not the devices or loads). Devices, such as an inverter, will have their own protection if they need it.
12ga = 20a breaker (not 25-30a). As @JJJJ said, a fuse or breaker is to protect the wire! (not the devices or loads). Devices, such as an inverter, will have their own protection if they need it.
T time2roll Solar Wizard Joined Mar 20, 2021 Messages 6,772 Location SoCal Jan 9, 2024 #4 PaulLad said: So if your wire supports 20A (12ga) but you have a 10A inverter, the fuse should be 25-30A correct? Click to expand... I would be more in the 15-20 amp zone.
PaulLad said: So if your wire supports 20A (12ga) but you have a 10A inverter, the fuse should be 25-30A correct? Click to expand... I would be more in the 15-20 amp zone.
S Skypower Solar Wizard Joined Aug 23, 2021 Messages 2,784 Jan 9, 2024 #5 I fuse to the lesser, component or cable.
T timselectric If I can do it, you can do it. Joined Feb 5, 2022 Messages 25,271 Jan 9, 2024 #6 The purpose of OCP (Over Current Protection) is to protect the conductors.