New to solar, and looking at the MPP "all in one" inverters. Trying to figure out how large I need to go, so I measured inrush and running current on the 4 things I plan to run (a well pump, oil furnace, sump pump and fridge). My question is: do I need to size the inverter to accommodate the worst case of all 4 things starting at the same time? (i.e. do I size to inrush or running?)
For info:
Load / Inrush / Running
Fridge - 1.1A - .87A
Furnace - 28.9A - 7A
Sump pump - 16.88A - 9.4A
Well Pump (240 V) L1 - 23.1A - 6.5A
Well Pump (240v) L2 - 22.5A - 6.6A
(yes, I know the two legs on the well pump should probably be the same, so I chalk that up to the meter, or one of the legs being used for control of pump)
Based on this, total inrush amperage (if everything started at once) is 92.48A which is 11,097 watts (I think)
Total running amps is 30.27A (if everything is on at the same time) which would be 3,632 watts
My concern is the house is normally not inhabited. If everything happened to start at the same time, I don't want to overload the inverter and have it shutdown. If I lived there, I could go down and shed some load and start it back up; but since I'm mostly not there, the inverter might just sit there in the fault state and I would have no heat.
Advice/help/corrections to any mistakes or assumptions above are all appreciated.
My followup question is going to ask about opinions about paralleling two inverters vs just buying the units that are really two units paralleled inside (like the MPP LVX6048). So feel free to opine on that as well if you like.
Thanks in advance!
For info:
Load / Inrush / Running
Fridge - 1.1A - .87A
Furnace - 28.9A - 7A
Sump pump - 16.88A - 9.4A
Well Pump (240 V) L1 - 23.1A - 6.5A
Well Pump (240v) L2 - 22.5A - 6.6A
(yes, I know the two legs on the well pump should probably be the same, so I chalk that up to the meter, or one of the legs being used for control of pump)
Based on this, total inrush amperage (if everything started at once) is 92.48A which is 11,097 watts (I think)
Total running amps is 30.27A (if everything is on at the same time) which would be 3,632 watts
My concern is the house is normally not inhabited. If everything happened to start at the same time, I don't want to overload the inverter and have it shutdown. If I lived there, I could go down and shed some load and start it back up; but since I'm mostly not there, the inverter might just sit there in the fault state and I would have no heat.
Advice/help/corrections to any mistakes or assumptions above are all appreciated.
My followup question is going to ask about opinions about paralleling two inverters vs just buying the units that are really two units paralleled inside (like the MPP LVX6048). So feel free to opine on that as well if you like.