Hello Forum members, this is my first post and I am looking for assistance reconnecting my SMA SI 5048US inverters to my solar system using SOK 48/100 LiFePo4 batteries.
Here is a description of my solar system:
2 X SMA Sunny Boy 5000US grid tied inverters.
2 X SMA Sunny Island 5048US battery inverters.
26 REC 370W solar modules
48V backup battery system
1 X SMA Sunny Webbox.
1 X Generac 14kW whole hose standby generator.
1 X Generac 200A Nexus Smart auto transfer switch.
My system is grid tied net metering. The grid tied function has never been a problem however I have never been satisfied the performance of the battery backup side. The original batteries were FLA and as they aged they became problematic. I was working internationally at the time and the system shut down completely several times while I was away due to low battery voltage with the FLA batteries, to over come this problem I replaced the FLA batteries with AGM batteries but they became unreliable after 1 battery developed an internal fault (2012). Since I was still working internationally at the time I removed the SI’s and the batteries from the system and went grid tied only with no battery backup. My system has operated reliably grid tied since. In 2009 hurricane Laura damaged my original REC modules which were 44 REC 215W panels and roof. My standby generator ran for 37 days continuous except for maintenance before grid power was reestablish. Now that I have replaced my roof and panels and retired I wish to add the SMA Sunny Islands back to the system with 5 X SOK 48/100 Batteries. My 2 SMA Sunny Islands are Circa 2008/2009 and were built pre lithium batteries with BMS. I have corresponded with SMA on the issue of using early SI’s with lithium batteries and the best advice I received was yes you can in open loop if you are using batteries with BMS which I am, and you must upgrade the Firmware which SMA has supplied. I have received my batteries and they are now racked and connected in parallel and fully charged. I am ready to reconnect the batteries to the Sunny Boys and now asking Forum members especially those who my have a similar systems for guidance and assistance. One additional correction I want to make is move the standby generator two wire start from the Generac Nexus switch to the Master Sunny Boy. This is how the original installer wired it and I left it wired this way because I was not aware the SI’s could control the generator start until I started researching to repowering the SI’s. Here is how I plan to proceed:
1. Check with utility RE: net metering agreement. Done, no concern on their part as this is not an increase in original net metering agreement capacity.
2. Check with city permit office for electrical concerns, Done, call for inspection when batteries are replaced for visual inspection and approval.
3. Reconnect batteries to the DC side of SI’s Reconnect Sunny Sunny boys to the AC side of Si’s, reestablish comms between SI’s and Sunny Boys.
4. Wake up Si’s with 48V battery power. Question is should I use the Quick Configuration Guide to view and change parameters and accept the previous defaults as this is a battery change only. Also I plan to select VRLA battery parameter as I will not have the parameter LION with BMS function. The SOK batteries charging voltage range is 57.6 to 58.4 Vdc. I know that I have to make changes first in the Slave SI first then the Master. To prevent overloading this post I will close it with this information and wait for a response from forum members especially regarding specific SI’s parameters I should be concerned for this this setup and being grid tied with batteries and backup generator.
Thanks to all in advance for review and comments.
Here is a description of my solar system:
2 X SMA Sunny Boy 5000US grid tied inverters.
2 X SMA Sunny Island 5048US battery inverters.
26 REC 370W solar modules
48V backup battery system
1 X SMA Sunny Webbox.
1 X Generac 14kW whole hose standby generator.
1 X Generac 200A Nexus Smart auto transfer switch.
My system is grid tied net metering. The grid tied function has never been a problem however I have never been satisfied the performance of the battery backup side. The original batteries were FLA and as they aged they became problematic. I was working internationally at the time and the system shut down completely several times while I was away due to low battery voltage with the FLA batteries, to over come this problem I replaced the FLA batteries with AGM batteries but they became unreliable after 1 battery developed an internal fault (2012). Since I was still working internationally at the time I removed the SI’s and the batteries from the system and went grid tied only with no battery backup. My system has operated reliably grid tied since. In 2009 hurricane Laura damaged my original REC modules which were 44 REC 215W panels and roof. My standby generator ran for 37 days continuous except for maintenance before grid power was reestablish. Now that I have replaced my roof and panels and retired I wish to add the SMA Sunny Islands back to the system with 5 X SOK 48/100 Batteries. My 2 SMA Sunny Islands are Circa 2008/2009 and were built pre lithium batteries with BMS. I have corresponded with SMA on the issue of using early SI’s with lithium batteries and the best advice I received was yes you can in open loop if you are using batteries with BMS which I am, and you must upgrade the Firmware which SMA has supplied. I have received my batteries and they are now racked and connected in parallel and fully charged. I am ready to reconnect the batteries to the Sunny Boys and now asking Forum members especially those who my have a similar systems for guidance and assistance. One additional correction I want to make is move the standby generator two wire start from the Generac Nexus switch to the Master Sunny Boy. This is how the original installer wired it and I left it wired this way because I was not aware the SI’s could control the generator start until I started researching to repowering the SI’s. Here is how I plan to proceed:
1. Check with utility RE: net metering agreement. Done, no concern on their part as this is not an increase in original net metering agreement capacity.
2. Check with city permit office for electrical concerns, Done, call for inspection when batteries are replaced for visual inspection and approval.
3. Reconnect batteries to the DC side of SI’s Reconnect Sunny Sunny boys to the AC side of Si’s, reestablish comms between SI’s and Sunny Boys.
4. Wake up Si’s with 48V battery power. Question is should I use the Quick Configuration Guide to view and change parameters and accept the previous defaults as this is a battery change only. Also I plan to select VRLA battery parameter as I will not have the parameter LION with BMS function. The SOK batteries charging voltage range is 57.6 to 58.4 Vdc. I know that I have to make changes first in the Slave SI first then the Master. To prevent overloading this post I will close it with this information and wait for a response from forum members especially regarding specific SI’s parameters I should be concerned for this this setup and being grid tied with batteries and backup generator.
Thanks to all in advance for review and comments.