SMA Sunny Boy 5kw-SP-US-41 purchased last fall (2020)...Cannot change active feed in limitations, will not accept changes after saving all. Under events now getting the above "information" not an error or warning. Tried turning off system completely for 5 mins and reboot and also overnite. still frozen....Owners manual just lists code 10120 but not how to reset.....
That exact code happened to me and it was easy to fix, but for the life of me, I can't remember what I did to fix it.
I can tell you this, it was just a matter of going into the menu, and finding a specific drop down box that had an option for doing a "reset" or "relearning".
In my case, I had added a second identical inverter to my solar array when I expanded. I went from 3 strings on a single inverter to 4 strings feeding two inverters. When I did that, I had moved one string from inverter A to inverter B and inverter A (the original) wasn't happy that it was missing a string. It kept popping an error code on the user interface. It was still making power just fine, but that big RED notification was annoying. So I had gone into the menu and figured out how to reset the error code, and each time I did that, it counted as one "parameter change" and eventually locked me out..
With more research and some help from someone on a forum group somewhere (I honestly thought it was Hedges but apparently not), I found a drop down menu box with an option to "relearn". This action caused the inverter to sort of reinitialize itself but it didn't lose anything I was concerned with.
Inside the menu, under "DEVICE" then under "OPERATION", you should find a drop down box for "Reset" this or that.. Pick one that seems best and see if it works.