I'm struggling to get 2 48V Ampere Time Lifepo4 batteries to work with my Sunny Island 6048 and hoping to get some advice on how to program the Sunny Island correctly. This is what I tried:
1. Configure the batteries as Lithium. This doesn't work because it requires communication between the SI and the battery BMS. The Ampere Time batteries are a black box. No BMS communication possible.
2. Configure the batteries as VRLA with battery voltage set at 48V and battery capacity at 200Ah. The inverter starts correctly and everything seems to work fine, except that the SOC readings are off. I did a test with a 2.5 kW load on a fully charged battery (10kWh) and the inverter shut down after 75 minutes when the SOC reached 0%. The batteries were far from drained. The voltage on the batteries was around 53V, which is about 70% charged. That's in line with what one would expect given the load.
3. Configure the batteries as 'Other', with following parameters:
- BattCapNom: 200Ah
- Batt Charge Voltage Manual: 55.2V
- Batt Charge Current Max: 150A
- Batt Di Voltage: 43.2V
- Batt Di Voltage St: 49.6 V
- Batt Di Ch Current Max: 150 A
When starting the system, I'm getting an error on the SMA: F141 Malfunction InvVolLow
Any recommendations on how to fix this? It seems to me that the best solution would be to configure the batteries as 'other', so I can set the disconnect voltage correctly. That setting is not available when you configure the batteries as VRLA. However, I haven't figured out how to avoid the F141 error...
1. Configure the batteries as Lithium. This doesn't work because it requires communication between the SI and the battery BMS. The Ampere Time batteries are a black box. No BMS communication possible.
2. Configure the batteries as VRLA with battery voltage set at 48V and battery capacity at 200Ah. The inverter starts correctly and everything seems to work fine, except that the SOC readings are off. I did a test with a 2.5 kW load on a fully charged battery (10kWh) and the inverter shut down after 75 minutes when the SOC reached 0%. The batteries were far from drained. The voltage on the batteries was around 53V, which is about 70% charged. That's in line with what one would expect given the load.
3. Configure the batteries as 'Other', with following parameters:
- BattCapNom: 200Ah
- Batt Charge Voltage Manual: 55.2V
- Batt Charge Current Max: 150A
- Batt Di Voltage: 43.2V
- Batt Di Voltage St: 49.6 V
- Batt Di Ch Current Max: 150 A
When starting the system, I'm getting an error on the SMA: F141 Malfunction InvVolLow
Any recommendations on how to fix this? It seems to me that the best solution would be to configure the batteries as 'other', so I can set the disconnect voltage correctly. That setting is not available when you configure the batteries as VRLA. However, I haven't figured out how to avoid the F141 error...