It is a puzzle, because no voltage should be present on AC2 input until supplied externally (from grid or generator)
It would seem like Master has the relay incorrectly stuck closed. But I'll assume some sort of "installer error" which could be corrected by moving a wire.
With both Sunny Island shut off, measure ohms from AC1 L to AC2 L of both master and slave. Should be open circuit. If not, disconnect wires and try again. Then you'll know if it is Sunny Island or your wiring.
Some people have had these wired together, trying to supply loads upstream.
Since you're seeing voltage where you shouldn't, good to figure that out before connecting the generator!
Earlier you wrote, "My problem is I am getting a 10V reading on the AC2 Gen/Grid Neutral connection of the Sunny Island Master."
A voltage reading requires connecting meter to two different points. One point is "Neutral" of AC2. Where is the other point?
Referencing page 22 from the manual and depicted in above message showing AC1 and AC2 connections on the Sunny Islands. I have A/C loads connected to AC1 Master and Slave as shown in the manual. All is working well for 1700 hours so far.
"Master and Slave" meaning one is configured as Master, one as Slave 1, and they have a data cable between them?
Considering that in the following sentences you talk about planning to bridge neutral and ground between AC2 terminals of master and slave, what neutral and ground connections have you had for the 1700 hours so far?
Is a ground rod already installed? Are neutral and ground already bonded in AC load box (which is presumably wired to AC1)?
I want to hook up my genset to the AC2 terminals labeled Gen/Grid. I plan to tie in as follows: Genset L1 to Master L, Genset L2 Slave L, Neutrals bridged and the ground going to a ground rod and the neutral and ground are bonded in the AC load box which runs to same ground rod.
Connecting generator L1, L2, N, G to them like this sounds correct.
Inside Sunny Island AC1-N is hardwired to AC2-N, AC1-PE is hardwired to AC2-PE.
(I happen to connect just one lug for N and one for PE; I have "Y" connections externally where the wires to Sunny Island, main panel on grid, and protected loads panel are joined together. I did that because conduit was getting too full for more wires.)
Before I tie in the generator, I checked the terminals on AC2 and I read 120V a/c across N & L (gen/grid input) Is this correct and why?
Sounds odd. We don't expect electrical connection from AC1 output of Sunny Island to AC2 input until after it has run for 5 minutes, observed power good on AC2, and synchronized its output to the input. So no voltage should be present.
I have AC2 connected to grid, through 63A 2-pole breakers and a fused disconnect. When I open the disconnect, no voltage is present on the wires leading to AC2. I checked that specifically before touching them to install lightning protection.
Earlier you saw 10V on master AC2 N. What was different about that measurement vs. this one?
10V is a floating, coupled value. I sometimes see small voltage on isolated circuits after turning off a breaker. The wires are adjacent in boxes and conduit. It can't drive any current.
Put a light bulb across that 120V reading (AC2 N & L), see if it lights. Measure voltage. Do same with 10V reading.
That will pull a floating voltage to zero, or show that there is a solid connection.
Check both Master and Slave.
Check Master AC1 L to Slave AC1 L. That should be 240V. The Master and Slave can be isolated, can be stacked in series, can be connected in parallel. They can also be running independently as two masters, not synchronized. Many ways of connecting would support 120V loads on both legs of a panel.
How is Sunny Island configured?
I'm expecting "2Phase2 Split-phase system, 2 Sunny Island"
Which of the following?
"PvOnly Stand-alone grid, no utility grid, no generator
Gen Stand-alone grid with generator
Grid Battery-backup grid
GenGrid Battery-backup grid with generator"
Because you use Midnight SCC not Sunny Boy, less likely it would try to backfeed the generator. But Sunny Island can be configured to backfeed (the grid) and you want to make sure it knows this is a generator.
If Sunny Island is actually feeding AC2, that would indicate relay is closed. I don't think that is supposed to happen unless it sees grid present, or is talking to a Multi-Cluster box.
Earlier you wrote,
"I attached the generator wires L1 to Master, L2 to Slave, Neutral split with equal length wires going to both SI's. Is this wiring from the genset correct?"
Are wires connected to AC2 now? Disconnect them, measure voltages directly at AC2 terminals. Measure voltages directly on wires.
If Sunny Island is working correctly, it would seem the voltage you see has to be coming from the wires. I don't know if you have them going through conduit, out of site where they can be mixed up, or anything.
How about a photo and sketch of the hookup?