Branching this off of my Generator post as I can see the thread getting too overwhelmed with replies. Original https://diysolarforum.com/threads/what-generator-works-with-sma-sunny-island.72963/post-1277033
Basics:
After getting my SI to work with a generator via manual mode it will sometimes not charge the batteries when there is full sun and the battery charge mode is boost or full (but I suspect all modes at this point) ... Changing #222.01 BatChgCurMax to anything other than what it is currently set to (90) will start the SI charging again. Changing back to 90 does not revert the state for that current "session" I am going to call it.
I call it a session as early morning I saw amps going into batter, SOC on SI 60%, I come back mid day and it is on BOOST and 1-2a max going into batteries. I change the parameter above and instantly get 50amps into both batteries for a while.
Likely FIX: 2024 12 21 UPDATE
Adding a 2k resistor to the temp sensor (since I never had one installed and technically VRLA is lead acid and "requires" one) has likely resolved this issue. Worked for 2-3 days, today 2024 12 22 stopped charging in full sun, no errors, no events to point to. Changing the single setting again allowed for charging.
Details
VRLA, 560a, 48v basic battery setup, open system. Have Batrium controlling pre-charge and main contractor, have JK BMS on both packs (another story).
SI has shunt configured as 50mV/500, previously worked this way.
Some settings I currently have, and I can't recall if they were set this way before this issue.
#222.12 AutoEquChrgEn is Disabled
#233 Grid Start section
03 GnSocTm1Str 80% (40% stock)
04 GnSocTm1Stp 95% (80% stock)
05 GnSocTm2Str 80% (40% stock)
06 GnStocTmStp 95% (80 stock)
09 GnPwrEna On (default Off)
10 GnPwrStr 13.0 kW (stock 4)
11 GnPwrStp 5.0 kW (stock 2)
#234 Generator Control section
07 GnStrMod Manual (I have to tell the SI to "start" gen on the SI for it to see it IIRC)
Lots of settings reduced for testing (aka to get faster failure points) but I don't think they are an issue
08 GnOpTmMin 1m
09 GnStpTmMin 1m
10 GnCoolTm 1m
11 GnErrStpTm 0h
12 GnWarmTm 10s
20 GnAiSns Low (stock is normal) Not sure if this was "required" to change to get things working with Gen
#231 section
10 TotPvPwr (is this DC or AC from the sunny boys?) Currently 7.5kW (assuming SB AC, might have previously been 11.5 but can't remember if I changed it)
11 ClstPwrNom 11.5kW (oddly this is my DC PV nominal IIRC)
Basics:
After getting my SI to work with a generator via manual mode it will sometimes not charge the batteries when there is full sun and the battery charge mode is boost or full (but I suspect all modes at this point) ... Changing #222.01 BatChgCurMax to anything other than what it is currently set to (90) will start the SI charging again. Changing back to 90 does not revert the state for that current "session" I am going to call it.
I call it a session as early morning I saw amps going into batter, SOC on SI 60%, I come back mid day and it is on BOOST and 1-2a max going into batteries. I change the parameter above and instantly get 50amps into both batteries for a while.
Likely FIX: 2024 12 21 UPDATE
Adding a 2k resistor to the temp sensor (since I never had one installed and technically VRLA is lead acid and "requires" one) has likely resolved this issue. Worked for 2-3 days, today 2024 12 22 stopped charging in full sun, no errors, no events to point to. Changing the single setting again allowed for charging.
Details
VRLA, 560a, 48v basic battery setup, open system. Have Batrium controlling pre-charge and main contractor, have JK BMS on both packs (another story).
SI has shunt configured as 50mV/500, previously worked this way.
Some settings I currently have, and I can't recall if they were set this way before this issue.
#222.12 AutoEquChrgEn is Disabled
#233 Grid Start section
03 GnSocTm1Str 80% (40% stock)
04 GnSocTm1Stp 95% (80% stock)
05 GnSocTm2Str 80% (40% stock)
06 GnStocTmStp 95% (80 stock)
09 GnPwrEna On (default Off)
10 GnPwrStr 13.0 kW (stock 4)
11 GnPwrStp 5.0 kW (stock 2)
#234 Generator Control section
07 GnStrMod Manual (I have to tell the SI to "start" gen on the SI for it to see it IIRC)
Lots of settings reduced for testing (aka to get faster failure points) but I don't think they are an issue
08 GnOpTmMin 1m
09 GnStpTmMin 1m
10 GnCoolTm 1m
11 GnErrStpTm 0h
12 GnWarmTm 10s
20 GnAiSns Low (stock is normal) Not sure if this was "required" to change to get things working with Gen
#231 section
10 TotPvPwr (is this DC or AC from the sunny boys?) Currently 7.5kW (assuming SB AC, might have previously been 11.5 but can't remember if I changed it)
11 ClstPwrNom 11.5kW (oddly this is my DC PV nominal IIRC)