I am putting together a small portable system and have some questions about wires and fuses. This will be 12 volt only, no inverter. Max load will be well under 15 amps, but want to allow for a little more, maybe up to 25 amps total for all loads.
I want to connect two 100AH LiFePO4 batteries with 100A BMS in parallel.
Questions:
When connecting batteries to each other in parallel, do you size the wires for max load or BMS amps? If I size the wire to the 100A BMS with something like 2 or 4 AWG, then I assume no fuse needed between batteries. If I were to connect the batteries together with something like 10 AWG, I assume I would need to use something like a 30 amp fuse?
Considering small loads, is a 30A DC breaker and fuse box between batteries and loads sufficient using 10 AWG? Or would I still need a battery terminal fuse? (Will be using the DC breaker as a disconnect of system.)
I put together the attached drawing for reference. Feel free to point out anything else to consider. I will have a plug connector between charge controller and solar panel as it is going to be portable.
I want to connect two 100AH LiFePO4 batteries with 100A BMS in parallel.
Questions:
When connecting batteries to each other in parallel, do you size the wires for max load or BMS amps? If I size the wire to the 100A BMS with something like 2 or 4 AWG, then I assume no fuse needed between batteries. If I were to connect the batteries together with something like 10 AWG, I assume I would need to use something like a 30 amp fuse?
Considering small loads, is a 30A DC breaker and fuse box between batteries and loads sufficient using 10 AWG? Or would I still need a battery terminal fuse? (Will be using the DC breaker as a disconnect of system.)
I put together the attached drawing for reference. Feel free to point out anything else to consider. I will have a plug connector between charge controller and solar panel as it is going to be portable.