Either you up the cable massively and not fuse or fuse and evaluate the risks.
Perhaps I should increase all the Alternator to Battery cables to 2/0 AWG and change the
Alternator Lynx fuse to 200a and increase the
LFP Battery fuse to 200a mrbf (this size fuse is just 2a more than the ampacity). I understand that the
T-fuse has an extremely fast short circuit response and is the type of fuse we need on the battery, of course that fast characteristic jeopardizes the Alternator but protects the system.
John Harries suggests sizing the alternator fuse at 120% of the rated capacity and then sizing the wire for that.
160A x 120% = 192A so 200A should be ok.
Most boats have no comprehensive battery low protection, this is not LVE. LVE should be set at the lowest manufacturers cell voltage of SOC. Battery Soc disconnects are separate and if fitted shoud trigger above LVE.
I believe
@svsagres uses a Victron Smart Battery Protect 65 in the bus to the DC Panel Loads with an automatic disconnect at some voltage greater than the LVE disconnect voltage. Is this a device that I should have on the feed from the Lynx to the DC Panel ? I understand this is a system separate from the BMS for "comprehensive battery low voltage protection".
Peter Kennedy wrote:
I have to question how the BMS acts for the other load and charge devices too. Perhaps it can communicate with the Cerbo to achieve this electronically with connected devices using DVCC but you would have to verify that the integration works.
@Goboatingnow wrote:
It can communicate or you can have separate “ battery saver “ disconnects. Your diagram has neither
I thought that @svagres had all Victron devices like Solar MPPT and Phoenix 120vac charger connected to the CerboGX and via VE.direct so that the CerboGX would control them appropriately. I have shown these VE.direct cable connections in the diagram as 1,2 & 3 (inside a small circle). Won't the CerboGX control these devices so that they don't overcharge and shut off, and charge when the LFP is low?
LATER: Refer to
@Goboatingnow Post #280
You can run DVCC on the Cerbo Gx and Control all Mppt and alternator charge sources , allowing central control What would be nice would to add the ability in the Cerbo to instruct the REC to reconnect the battery , this would even allow remote ( via victron VRM ) ability to reengage charge sources etc. I must study the Ve.can integration of the REC to see what it’s possibilities are.
Also by adding a Victron Smart Battery Protect 65 in front of the DC Panel loads we wouldn't we then have a better battery protection?
First see
Post #86
2. Smart disconnect. If u intend to use this as a disconnect device it must be next to the battery. No other devices except the bms must remain connected and provision must be contained within the bms to not discharge the li completely either. Hence as it is the smart switch is not compliant with ABYC or ISO.
In reviewing the past posts in the thread we have had a number of discussions about having a Smart Battery Disconnect 65. I believe that Goboatingnow does not recommend having one of these devices for several reasons.
The remaining device to consider is then the Alternator and Regulator (Wakespeed) which has an Balmar APD (to perhaps help) and the regulator is interlinked via Canbus to the REC Active BMS and VE.canbus to the CerboGX and is then controlled by the CerboGX to shutdown in advance of a BMS HVD or HVE (High voltage event)?
Post #361 svsagres - nice.
Without BMS control, the Wakespeed will set its voltage out to limit to a configured value. On my boat, I have it at the default limp mode at 13.2v, but unless things go really bad, I’ll just run the lfp without the bms.
Also I believe that the Wakespeed has its own high voltage setting which stops the alternator from charging which would be set at a lower voltage than HVDisconnect or HVEvent setting. In addition, I think the CerboGX will control other charge devices like the Solar MPPT?
Post #369 svsagres -nice!
In regards to the solar, it’s all managed by the Cerbo GX. So the MPPTs themselves can be programmed for lead acid. This will be overridden when they’re connected to the cerbo and being remote controlled. (The Cerbo takes in the voltage/current limits and measurements from the BMS, and translates them to the MPPTs. Without the remote control, the MPPTs will revert to their internally measured voltage set points.
Alternator protection when switching
Should the Alternator brown or the field wire be run through the 1-off-2 switch AFD to protect the alternator when switching, or should we just shut the engine down before touching the switch? --NO
LATER: No that isn't going to work,
- When switch is at OFF "Normal LFP" we want the alternator to be able to charge.
- When we switch to "LFP Disconnect & SLA Emergency Feed", if the engine is running, hopefully the alternator/regulator will adjust to the "limp home" setting (13.8-13.2v).
- When we switch to LFP Override, if the engine is running, then we may want the alternator to be charging or may not depending on the state of the battery!
- Does this need further attention? - No, not going to do.
LATER: Regarding PK question about keeping the BMS powered after shutdown.
Post #184
BMS draws its power from the sense leads connected to the (LFP) battery, so it will always be powered.
Additionally, the CerboGX is powered from the SLA battery so it will continue to function with Victron equipment (MPPT, Orion-Tr) and with the Wakespeed, and the BMS since it continues to be powered from the LFP.
Svsagres wrote:
For me, if I’m not aboard, I put the boat into hibernation mode. That drops my load to 20W or so (Cerbo, Instrumentation, AIS, and LTE left on). With my battery that gives me about 20 days to respond to something gone wrong with charging.
If I’m just leaving the boat for an afternoon, I really don’t care, since I’m fully operational mode (refrigeration, devices, laptops, etc…) I still have about 4 or 5 days until I really need a charge.