In the attached, I updated the wiring diagram to include a bank of 6 EG4 batteries (48V, 100ah each) in parallel in the metal EG4 battery rack with the integrated busbars. Each EG4 has a 125A breaker built-in. I plan to run 4/0 wire connecting the busbars to the two parallel stacked Sol-Ark 12Ks (via multi-tap connectors). Each SA 12Ks has a 250A battery breaker.
Your setup is similar to mine except I only have one 12K unit.
Questions:

1) Is a DC disconnect required between the battery rack and the SAs? If so, what size disconnect and type (fuse vs. breaker) would you suggest? Any suggested brands/links would be appreciated.
I use a 250A breaker. I am cant remember the brand but I think it's the same as the Schneider DC breaker.
Link: 250A DC Breaker
2) Does the battery rack need a ground wire? The batteries are screwed into the rack, so I believe they would be considered grounded to the rack.
I would ground it.
Sol-Ark manual says to "install a subpanel for backup loads if you have Arc-Fault / GFI breakers, NOT a multi-circuit transfer switch. Can someone help me understand, why that is so? I do have AFCI breakers in the main breaker panel. Is that a problem if I keep the current design (see attached)?
Call Sol-Ark, I have not used an Arc-Fault breaker.
Are there any issues with the diagram that the permit office might take issue with?
Ask @FilterGuy or @Dzl they might be able to help you there.
 
Are there any issues with the diagram that the permit office might take issue with?
Curious if you had any issues; I know I am late to the party, but here is what I see:
  1. You do not show a DC grounding connection on the 48V negative bus. I think (but not certain) that is required.
  2. Your grid input feeds (tap conductors to disconnect) appear to be undersized; they would need to be #4 here (depending on length).
  3. Your inverter grid input disconnects should be fused or circuit breaker.
  4. Should state how many poles your PV DC disconnect is. I assume they are 4-pole.
  5. If your inverters do not have a built-in DC circuit breakers you would need external.
Where I live, you would need to show additional information, but that is a local issue.

The statement from SolArk about GFI is alluding to the fact that you could end up with circulating neutral current that would trip a main GFI-- typicall only an issue for 480V services 800A and up. GFI is to protect equipment, GFCI is to protect people-- two different things. AFCI doesn't matter in this situation.
 
I updated the wiring diagram - see attached. I got the permit. I'm now in the slow process of DIY installation. Done installing the ground mount in the backyard about 150 feet away from the house. Next phase is to install the equipment on a 3/4" 4' x 8' plywood secured to the basement wall. Last phase will be digging an 18" deep trench between the house and the ground mount and run the 10 AWG wires for the 4 strings in 4 separate 3/4" pvc conduits to the 2 Sol-Arks via two 4-pole IMO 25 amp DC disconnect (each IMO handles 2 strings). The DC disconnects will be near the inverter on the basement wall. I'm not comfortable handling the wiring to the meter panel, so plan is have an electrician wire the AC portion of the project, before requesting AHJ inspection.

About your notes:
  1. You do not show a DC grounding connection on the 48V negative bus. I think (but not certain) that is required. See revised schematic attached.
  2. Your grid input feeds (tap conductors to disconnect) appear to be undersized; they would need to be #4 here (depending on length). 6 AWG wire is the max the Sol-Ark can accept on the AC side. But there is a manual transfer switch between the meter and the inverters. I'm using 4/0 SER wire between the meter and the transfer switch. Then 6 AWG wire between the transfer switch and the inverters.
  3. Your inverter grid input disconnects should be fused or circuit breaker. Using Square D 60 amp AC disconnect (breaker style) for inverter grid inputs ($18 each at Home Depot). Would prefer to use 63 amp AC disconnects (since each inverter can take up to 63 amps), but those seem to all be very expensive. Sure would like to know if there are any UL listed 63 amp AC disconnects under $100.
  4. Should state how many poles your PV DC disconnect is. I assume they are 4-pole. Yes, they're 4-pole and can receive 2 strings each.
  5. If your inverters do not have a built-in DC circuit breakers you would need external. They do - specs attached.
 

Attachments

  • Wiring Diagram Solar Ground Mount - R.pdf
    214 KB · Views: 35
  • 021 Sol-Ark 12K-P Inverter Specification Sheet.pdf
    263.9 KB · Views: 29
Good work. Let us know how this is coming along… I have a similar setup coming on a truck. Mine will be off-grid, backed with a 14kW gen, and inspection-less.
Only way to go. Mine runs as a permanent “backup” without all the inspections.

I’m not saying use Plastic wire nuts and make it “Good enough “ Just a lot easier without someone who doesn’t know the first thing about Solar making mandates to your system.
Our Local inspectors really do not know what to do with Solar.
 
I would use larger 1 inch or 1.5 inch conduit for easier pulls.(you can us the cheaper thinner ducting (DB duct) in 20 footers as long as its schedule 80 or 40 that comes up out of ground. I used 1.5 inch for an 80 foot run. I have the mouse and vac system to suck the string thru as well. Check on wire size with that long run on voltage drops as you will need to size up some.
I would also drop in a spare 3/4 inch conduit as i have to hand dig one in 1 year later when I added optimizers and needed a data cable run back to inverter area. Spare is always good.
 
  1. You do not show a DC grounding connection on the 48V negative bus. I think (but not certain) that is required. See revised schematic attached.
  2. Your grid input feeds (tap conductors to disconnect) appear to be undersized; they would need to be #4 here (depending on length). 6 AWG wire is the max the Sol-Ark can accept on the AC side. But there is a manual transfer switch between the meter and the inverters. I'm using 4/0 SER wire between the meter and the transfer switch. Then 6 AWG wire between the transfer switch and the inverters.
  3. Your inverter grid input disconnects should be fused or circuit breaker. Using Square D 60 amp AC disconnect (breaker style) for inverter grid inputs ($18 each at Home Depot). Would prefer to use 63 amp AC disconnects (since each inverter can take up to 63 amps), but those seem to all be very expensive. Sure would like to know if there are any UL listed 63 amp AC disconnects under $100.
  4. Should state how many poles your PV DC disconnect is. I assume they are 4-pole. Yes, they're 4-pole and can receive 2 strings each.
  5. If your inverters do not have a built-in DC circuit breakers you would need external. They do - specs attached.
The Sol-Ark sheet you attached is a little short on technical information, but I don't see reference to a 48VDC disconnect internal to it. Personally I would want one disconnect for each inverter. If you are using two-pole disconnects then you don't need to ground the -48V bus, but that is outside my expertise.

The $18 disconnect you have is not fused; it is just an air conditioner disconnect. That would be a dangerous device to use on several levels-- first your wiring is only protected at 200A by the service disconnect, and second there can be exposed parts in it that are live. (I remember these being the "pull plug" style device, but maybe they are fancier now-- that was a few decades ago.)
 
Sol Arc has a built in array power disconect on the side-newer version (mine is a almost 1.5 years old and is on bottom)
They out put (50 amp) is on a breaker on unit as well
I have two disconnects on my ground mount array one for each string before heading underground to sol arc.
In my case I'm going from the Sol Arc to a 100 amp subpanel (into a 50 amp breaker ) in a outbuilding which then goes a long ways back to my main 200 amp panel on house. It a bit awkward but does work well.
 
Last edited:
Sol-Ark instruction state not to ground 48V bat neg or pv neg circuits.

150' will give you approx 2.25% voltage drop.
 
run the 10 AWG wires for the 4 strings in 4 separate 3/4" pvc conduits
Hi, I see the question a few times in this thread about putting all PV conductors in the same conduit vs separate conduits but not much discussion on why do to it one way or the other. Why did you decide on 4 separate conduits? I am starting to plan a very similar project that is about a year out and will need to plan running conduit through the slab of a yet to be built addition, so I need to plan what is run through there. Thanks!
 
Hi, I see the question a few times in this thread about putting all PV conductors in the same conduit vs separate conduits but not much discussion on why do to it one way or the other. Why did you decide on 4 separate conduits? I am starting to plan a very similar project that is about a year out and will need to plan running conduit through the slab of a yet to be built addition, so I need to plan what is run through there. Thanks!
Two conduits, one for each inverter, would have likely been a better choice, as would up-sizing the wire to #8 AWG to reduce voltage drop.

Electrical code is you need to de-rate when you get over 3 current carrying conductors in a conduit; 4-6 conductors you only get 80% of the ampacity and 7-8 you get 70%. However, pulling just two conductors in a conduit often results in more binding than 3 or 4, and if your wire sizing is dictated by voltage drop anyway you might as well reduce the number of conduits.
 
I understand NEC requires all DC wiring inside a house to be in metal conduit. My four DC strings from the ground mount array will in 3/4" FMC conduit once they enter the exterior wall. The inverters and battery rack are setup in my basement.

Question: Should the 4 feet of 4/0 battery cables from the battery rack (6 EG4s) to the wire trough under the Sol-Arks be run in 2" FMC? Those of you who have to deal with inspections, what conduit (if any) have you used for your battery cables between inverter and battery rack?
 
I understand NEC requires all DC wiring inside a house to be in metal conduit. My four DC strings from the ground mount array will in 3/4" FMC conduit once they enter the exterior wall. The inverters and battery rack are setup in my basement.

Question: Should the 4 feet of 4/0 battery cables from the battery rack (6 EG4s) to the wire trough under the Sol-Arks be run in 2" FMC? Those of you who have to deal with inspections, what conduit (if any) have you used for your battery cables between inverter and battery rack?
Do you have a fuse between the common battery busbar and the 4' cable? What type of conductor insulation are you using?
 
Each EG4 has it's own 125A breaker (just before the common busbar) and the other end of the 4/0 cable connects to a 250A breaker in the Sol-Ark, so I didn't see the need for further fuses or disconnects since I think the breakers serve as OCPD and disconnect. Do I have that right?

Regardless, do I still need to run the 4/0 cables through metal conduit to meet NEC requirements?
 
Each EG4 has it's own 125A breaker (just before the common busbar) and the other end of the 4/0 cable connects to a 250A breaker in the Sol-Ark, so I didn't see the need for further fuses or disconnects since I think the breakers serve as OCPD and disconnect. Do I have that right?

Regardless, do I still need to run the 4/0 cables through metal conduit to meet NEC requirements?

"What type of conductor insulation are you using?" I'm using what appear to be high quality 4/0 battery cables from Spartan Power:

Cable Features:
  • Made in the USA
  • Polyvinyl-chloride (PVC) insulation
  • 90°C MTW – UL & CSA 105°C
  • Voltage rating: Up to 1000 volts UL 10269
  • VW-1 & moisture resistant
  • ROHS Compliant
  • UL 1232/1284/1338/10269 Approved
 
I found an add for 2 used sol_ark 12k and 2 48v rack batteries.
The 12ks are about 7 to 8 years old. I can't find much on history of the 12 k's they are asking 6k for the 2 inverters and 2 batteries.
1.Is there any issues with the older solark 12 k's?
2. Since they're older units will they meet the requirements for the newer codes nec 2017-18?
3. What should I look for when I go to check out these inverters and batteries?
4. What is the release date of the 12k.

I was told that They were only used 3 to 4 weeks out of the year because they were in a vacation home.

Thanks,
 

Attachments

  • 12155.jpeg
    12155.jpeg
    119.6 KB · Views: 15
  • 12153.jpeg
    12153.jpeg
    116.6 KB · Views: 15
  • 12151.jpeg
    12151.jpeg
    140.7 KB · Views: 15
  • 12150.jpeg
    12150.jpeg
    139.2 KB · Views: 12
  • 12149.jpeg
    12149.jpeg
    81.2 KB · Views: 14
@Chris72 I wouldn't expect much of the batteries if it was only used a few weeks a year. I wasn't aware the 12k was that old, will be curious what others can offer up.
 
@Chris72 I wouldn't expect much of the batteries if it was only used a few weeks a year. I wasn't aware the 12k was that old, will be curious what others can offer up.
Yeah I'm on the fence weather to Buy these or not. The other option is just to buy a 15k new.
 
It isn't. The 12K came out in 2017 or 18.
That's the thing how do you tell? Not a lot of info on when they first came out. The price seems fair for 2 12ks and 2 5.1kwh batteries.
 
Last edited:
So I ended up buying those 12ks and the batteries I dont think they are that old becuse the wireless Module is on the side. Not sure when they changed it to the side.
 