I watched Will's recent 0-100% LiFePO4 battery videos and thought I'd set that up (I've got no issue with the 100% advice (I'm already doing that) -- I've got some misgivings about not keeping any spare capacity in my HomeGrid Stack'd 19.2 kWh (4 module) battery, but that's a different issue). I need help in figuring out where to make changes to implement that 0% level on my Sol-Ark 15k inverter.
There are 3 places in the settings where I think I'd have to change things to go with that 0-100% battery range. The first is the Batt Setup > Discharge tab:

I assume I need to change the Shutdown field to 0% from my existing 10%. But, when the manual says "...the inverter will shut down...," does that mean the DC -> AC conversion (inversion?) from the PV/Battery will cease or that the actual, entire inverter (including the PV -> Battery function) will shut down? Assuming it's just the AC output that shuts down until the battery reaches the Restart number, what's a good number for Restart and Low Batt? I'm thinking I should just leave those at my existing 20% and 15%. (EDIT2: I think I'll go with 0/5/10% for Shutdown/Low Batt/Restart)
The next area is the Batt Setup > Charge tab:

I've got a generator hooked to my GEN input. I think my existing settings mean that if the battery SOC falls between 15% and 20%, the battery will charge from the grid, and if the battery SOC falls below 15%, it'll fire up the generator and charge the battery from there. That should only happen if the grid is down long enough to drain the battery to those levels and then comes back on line.
EDIT1: After posting this, I realized I'll HAVE to change the Start%. Otherwise, I'll just end up charging the battery from Grid/Generator when the battery SOC reaches 20%/15% (which might be routinely). I'll have to think about that some more.
Originally, I just matched those 20% and 15% numbers to what I had on the Discharge tab's Restart and Low Batt numbers. But, I'm not sure what/if I should change them with a new 0% Shutdown setting on the battery. Should I continue to match them to whatever I decide to put in those Discharge tab numbers this time around? (EDIT2: Yes, I think I'll match the settings -- 5/10% for Gen/Grid Start%)
And then there's the Limiter (Time of Use (TOU)) tab:

I'm using TOU solely to change the inverter's energy priority from the default:
1. Solar PV Power | 2. Grid Power | 3. Batteries | 4. Generator
to the TOU priority of:
1. Solar PV Power | 2. Batteries (down to programmed discharge V or %) | 3. Grid Power | 4. Generator.
My existing settings should mean that if my battery SOC falls below 20% (the old Battery Discharge Startup and Grid Start% numbers -- which, again, should only happen if the grid goes away long enough to discharge the battery that far), when the grid is available, charge the battery. I assume I should match that percentage to whatever I put in the Battery Discharge Startup and Grid Start fields. Is that reasonable? (EDIT2: Yes, I think I'll change the TOU Batt field to match the 10% Battery Discharge Startup and Grid Start% fields)
EDIT2: I've decided to change my Batt Setup > Discharge > Shutdown/Low Batt/Startup settings to 0/5/10%. I'll also change the Batt Setup > Charge > Gen/Grid Start% settings to 5/10% and my Limiter > Batt setting to 10%. That means that routinely, my lower battery level will be 10% and will only reach 0% if the grid is down long enough for the generator to run out of propane. I suppose I could reduce the spread of those numbers from 5% between each to maybe 1% between each. But, I don't know how accurate the inverter can see those battery values. A 10% increase in available battery is pretty good, though.
EDIT3: Interesting. I can't get the inverter to save a Gen Start% less than 10% (same as what the Grid Start%, Restart and TOU Battery settings are). I wonder which will start first: Grid charging, Gen charging or both at the same time. I assume it'll be Grid charging if the grid is available (because of the TOU energy priority. Also, since I'd only ever get to that 0% battery level in a zombie apocalypse, I bumped the Shutdown setting up from 0% to 1% (just in case the battery really doesn't like 0%).
There are 3 places in the settings where I think I'd have to change things to go with that 0-100% battery range. The first is the Batt Setup > Discharge tab:

Shutdown: Battery voltage or % at which the inverter will shut down to protect the battery from an over discharge situation (battery
symbol on the home screen will turn red).
Low Batt: Low battery voltage or % (battery symbol on the home screen will turn yellow). Stopping point for TOU.
Restart: Battery voltage or % at which AC output will resume after previously reaching “shutdown”.
I assume I need to change the Shutdown field to 0% from my existing 10%. But, when the manual says "...the inverter will shut down...," does that mean the DC -> AC conversion (inversion?) from the PV/Battery will cease or that the actual, entire inverter (including the PV -> Battery function) will shut down? Assuming it's just the AC output that shuts down until the battery reaches the Restart number, what's a good number for Restart and Low Batt? I'm thinking I should just leave those at my existing 20% and 15%. (EDIT2: I think I'll go with 0/5/10% for Shutdown/Low Batt/Restart)
The next area is the Batt Setup > Charge tab:

Gen Charge: Uses the “GEN” input of the system to charge the battery bank from a generator.
...
b. Start %: Percentage S.O.C (state of charge) at which the system will AutoStart a generator to charge the battery....
Grid Charge: There are two scenarios in which this option is used:
a. Grid connected to “Grid” input: The inverter will limit the charge rate to the set value in “A” and the battery will charge to
100% SOC....
I've got a generator hooked to my GEN input. I think my existing settings mean that if the battery SOC falls between 15% and 20%, the battery will charge from the grid, and if the battery SOC falls below 15%, it'll fire up the generator and charge the battery from there. That should only happen if the grid is down long enough to drain the battery to those levels and then comes back on line.
EDIT1: After posting this, I realized I'll HAVE to change the Start%. Otherwise, I'll just end up charging the battery from Grid/Generator when the battery SOC reaches 20%/15% (which might be routinely). I'll have to think about that some more.
Originally, I just matched those 20% and 15% numbers to what I had on the Discharge tab's Restart and Low Batt numbers. But, I'm not sure what/if I should change them with a new 0% Shutdown setting on the battery. Should I continue to match them to whatever I decide to put in those Discharge tab numbers this time around? (EDIT2: Yes, I think I'll match the settings -- 5/10% for Gen/Grid Start%)
And then there's the Limiter (Time of Use (TOU)) tab:

Batt: V or % used to specify a lower discharge limit or upper charge limit whenever “🗹 Charge” is enabled. Grid-tied systems
will not allow TOU to discharge lower than “Low Batt V/%”. Off-grid systems allow TOU discharge down to “Shutdown V/%”.
🗹 Charge: During the hours selected, it is allowed to charge batteries from an external AC source up to a programmed voltage or
%. If the external AC power source is a generator, the “Start V” or “Start %” condition must be fulfilled first. If available, the solar array
will always charge the batteries at 100% regardless of “🗹 Charge” in TOU.
I'm using TOU solely to change the inverter's energy priority from the default:
1. Solar PV Power | 2. Grid Power | 3. Batteries | 4. Generator
to the TOU priority of:
1. Solar PV Power | 2. Batteries (down to programmed discharge V or %) | 3. Grid Power | 4. Generator.
My existing settings should mean that if my battery SOC falls below 20% (the old Battery Discharge Startup and Grid Start% numbers -- which, again, should only happen if the grid goes away long enough to discharge the battery that far), when the grid is available, charge the battery. I assume I should match that percentage to whatever I put in the Battery Discharge Startup and Grid Start fields. Is that reasonable? (EDIT2: Yes, I think I'll change the TOU Batt field to match the 10% Battery Discharge Startup and Grid Start% fields)
EDIT2: I've decided to change my Batt Setup > Discharge > Shutdown/Low Batt/Startup settings to 0/5/10%. I'll also change the Batt Setup > Charge > Gen/Grid Start% settings to 5/10% and my Limiter > Batt setting to 10%. That means that routinely, my lower battery level will be 10% and will only reach 0% if the grid is down long enough for the generator to run out of propane. I suppose I could reduce the spread of those numbers from 5% between each to maybe 1% between each. But, I don't know how accurate the inverter can see those battery values. A 10% increase in available battery is pretty good, though.
EDIT3: Interesting. I can't get the inverter to save a Gen Start% less than 10% (same as what the Grid Start%, Restart and TOU Battery settings are). I wonder which will start first: Grid charging, Gen charging or both at the same time. I assume it'll be Grid charging if the grid is available (because of the TOU energy priority. Also, since I'd only ever get to that 0% battery level in a zombie apocalypse, I bumped the Shutdown setting up from 0% to 1% (just in case the battery really doesn't like 0%).