I don't know what "CLP" is.
You could test voltage change under moderate load, e.g. 1500W 120V space heater. That would give an idea of how bad the problem is. What you don't want to do is kill your refrigerator or anything else important.
It appears Neutral is overheating worse than the two Line conductors.
120V loads can suffer brownout, e.g. a motor failing to start. Loads on the other phase then get over-voltage.
Looks like about 6V delta (12V spread), multiply by current draw to get watts dissipated in that connection. If 10A, that's 60W. Kind of high in a small space, but I think most of the heat then conducts along wire before spreading to environment. 60W is what 20' of 2/0 (copper) cable is expected to dissipate, for 60C rise, 90C operating temperature. That explains why yours got hot enough to melt plastic.
One of your graphs mentions 5000W or so, which would be 20A at 240V. Not sure how much imbalance at 120V, which causes current through the more poorly connected neutral wire.
At least, minimize power draw until fixed.
You could test voltage change under moderate load, e.g. 1500W 120V space heater. That would give an idea of how bad the problem is. What you don't want to do is kill your refrigerator or anything else important.
It appears Neutral is overheating worse than the two Line conductors.
120V loads can suffer brownout, e.g. a motor failing to start. Loads on the other phase then get over-voltage.
Looks like about 6V delta (12V spread), multiply by current draw to get watts dissipated in that connection. If 10A, that's 60W. Kind of high in a small space, but I think most of the heat then conducts along wire before spreading to environment. 60W is what 20' of 2/0 (copper) cable is expected to dissipate, for 60C rise, 90C operating temperature. That explains why yours got hot enough to melt plastic.
One of your graphs mentions 5000W or so, which would be 20A at 240V. Not sure how much imbalance at 120V, which causes current through the more poorly connected neutral wire.
At least, minimize power draw until fixed.