I have a pair of 15k inverters in parallel + 10kW battery that were operational for 2 months before I had permission to operate (so waiting for "go live" from the utility on the net metering agreement). I wanted to do the same thing - why not use the PV (and even batteries) but with no export?
No go. My config was very straightforward - no grid peak shaving, Grid Sell unchecked, Limited Power to Load checked (100% of my load is on the load terminals), Time Of Use unchecked.
With just the grid, inverters and battery, everything was fine - it would never export. However, if I connected the PV array, it would occasionally export a small amount. The most common time this happened was when there was a sizable load (electric clothes dryer, for example) that was running, then stopped. Right after the large load went away, the inverter could export some then ramp down PV usage.. just not quickly enough to prevent some export. I wondered if this was just incorrect/inaccurate monitoring in the Sol-Ark software - not the case. I have a smart meter and have Emporia View Utility connected so I can see real-time data for what the meter is doing and it was indeed running "backwards", proving that from the grid's point of view, export was happening.
I spent some time searching the web and found lots of comments that it's impossible to have zero export when using PV. Not sure that's 100% true, but it sure seemed to be true in my case.
HTH