I'm trying to figure out how my electric use relates to what the maximum current the Sol-ark 15k will convert from DC (i.e., PV or battery) to AC (i.e., load). The spec sheet for it says:
Max. Output Current: 62.5A
Real Power, max continuous (batteries only, no PV): 12,000W (50A @ 240V)
Max Output Fault Current (5s): 94A with PV, 75A (batteries only, no PV)
Max Output Fault Current (100ms): 120A
Max. Grid Passthrough Current: 200A

My silly question is what counts as current? Looking at the graph on the Equipment tab of solarkcloud.com for the inverter's I-ac-L1 and I-ac-L2, I've got good chunks of time with each of those at upper-30s amps. Are those I-ac-L1 and I-ac-L2 values what's being talked about with the specs, above? If I were off-grid, and if those L1/L2 values are what I should be referencing, would I add the two legs (so roughly >75A) and have to worry about exceeding the current rating? Or, would it be more correct to look at the load's P-Load_L1 and P-Load_L2 and dividing them by Load Voltage L1 and Load Voltage L2, respectively, to get the current?
Max. Output Current: 62.5A
Real Power, max continuous (batteries only, no PV): 12,000W (50A @ 240V)
Max Output Fault Current (5s): 94A with PV, 75A (batteries only, no PV)
Max Output Fault Current (100ms): 120A
Max. Grid Passthrough Current: 200A

My silly question is what counts as current? Looking at the graph on the Equipment tab of solarkcloud.com for the inverter's I-ac-L1 and I-ac-L2, I've got good chunks of time with each of those at upper-30s amps. Are those I-ac-L1 and I-ac-L2 values what's being talked about with the specs, above? If I were off-grid, and if those L1/L2 values are what I should be referencing, would I add the two legs (so roughly >75A) and have to worry about exceeding the current rating? Or, would it be more correct to look at the load's P-Load_L1 and P-Load_L2 and dividing them by Load Voltage L1 and Load Voltage L2, respectively, to get the current?