I’ve been away from the form a little while battling this issue.
15k sol ark, 48v LFE 4k Trophy battery + a little SLA because my battery is so small at low voltage it shuts off
Generator need is only standby.
The biggest challenge for me is that the Sol Ark 15k does not use the generator power input to ONLY charge the battery. It first draws from the generator to power loads using the dirty generator power (compared to grid and Sol Ark created power) and then, on top of those loads it draws from the generator with its 240v battery charger. I saw this is a challenge because a battery charger load can be constant and a big battery and Sol Ark can efficiently handle load spikes. Those same load spikes on a generator cause really dirty power, equipment wear and possibly failure / safety shut off systems to trigger.
Some important notes you may want to scroll to the end for:
- 240V generators only give half power
- Sol Ark can run the generator when grid power is on
This post is not intended to show disrespect to sol ark, generator manufactures, etc. Perhaps the Sol Ark generator input needs to power loads first or it can not deliver the feature of using it’s generator input as an AC Coupled solar power input. The sol ark has a huge number of features and those features come with limits.
120V generator with separate DC chargers.
Total cost: $700 - $900
Started with 120V gas generator with 48V DC 10 AMP chargers. I had lots of problems with this solution. It did not work at all with low SOC (state of charge) the Sol Ark would trigger low state of charge and fault.
With high state of charge sometimes the Sol Ark system would detect the incoming generator DC charging power as a problem and then shut off loads.
There was one time it did work. It was nice, solid consistent load on the generator, solid power output by the chargers, smooth house operation. For me, not dependable enough. Costs: I had the generator ($200 - $500), chargers cost about $300 - $400, custom wiring, I just used spare parts ($100 - $200).
Pros:
- Operation of this system was very smooth. The generator load was constant and efficient.
- Load spikes were handled by the battery / Sol Ark
- Phase imbalanced handled by the battery / Sol Ark (efficient)
- All commodity parts (except the sol ark)
Cons
- Not dependable
- Power scaling problem
- Cost scaling problem
Sol Ark support was very nice trying to help me make this work. I think it could have worked well if my load was smaller. I run a few power-hungry computers all the time and at times (gardening and hunting) can have 6 refrigerators going.
The 120V generator I had maxed out at 2500 Watts, I could only run 2x 10 AMP chargers and 2x 5 AMP chargers before the load was getting too heavy. Perhaps if I had a larger generator with 4x 10 AMP chargers the solution would have squeaked by. However, the price point was about $500 for chargers and with the Sol Ark being so unreliable with this solution I moved in another direction.
240V generator with integrated Sol Ark charger
Total cost: $800 - $1,000
So I switched gears and got a firman Tri-Fuel generator: $800 (shipped with tax)
https://www.google.com/search?q=120...57j33i160l2.3504j0j4&sourceid=chrome&ie=UTF-8
I have it hooked up to the houses natural gas line ($30 - $1,000). You could go gasoline or propane depending on your resources. I used the 240V twist lock 20 AMP receptacle and ran a power wire ($50 - $200) right into my sol ark. I had to adjust the motor governor to get the frequency down from 63 Hz to 60 Hz
My house was a great worst case situation (imbalanced load).
Final working configuration:
Circuit A: 120v, 11 AMP draw
Circuit B: 120v, 2 AMP draw
Sol Ark configured to draw 5 AMPS to charge the battery. (240V load)
I had no 240V loads, that is my next priority project this summer. The generator is supposed to put out 5500 Watts on Natural Gas, 6900 Watts peak. More on all other fuels. That means each 120V output should handle about 2750 Watts, about 22.9 AMPS, 28.75 AMPS Peak. This did not turn out to be the case with the sol ark and my imbalanced loads. I maxed out at about 11 AMPS. Going to 12 caused a fault. I wish I would have metered the power going into the sol ark during the fault. Without having done that I don’t know if the sol ark stopped taking the power, maybe it was too dirty, or the generator stopped delivering power. The video I linked shows the sol ark receiving 240V power during the battery operation cycle so I think the issue is with the sol ark. At the price point I paid for the firman, even if I can only get 11 AMPs per phase with this crazy load imbalance I’m good. After I balance my loads and switch a bunch of 120V devices to 240v I’ll test again with higher charger draw.
I tried to up the charging to 10 AMPs, but it did not work. After about a minute the Sol Ark went back to battery, cycling on and off generator every minute. Same thing with 15 and 25 AMP battery charge.
- The beeping noise is the APC computer battery backups saying the power is too dirty and going to their own battery backup.
APC Battery Backup for Computers: This isn’t “NEEDED” as my present results show that computers on the SOL ARK backup power do not power cycle when the sol ark takes over. I have older units (linked below) but I don’t think newer ones are much different. When on generator backup the power is too dirty for the UPS systems and they go to battery backup. This may not be the case if I had a more balanced 120V set of loads. I may do this in the future by switching to a 240 V UPS system I have on hand. I was able to get it working properly by reducing the power quality setting in the APC systems to it's medium sensitivity.
https://www.apc.com/us/en/product/SUA1500RM2U/apc-smartups-1500va-usb-serial-rm-2u-120v/
So my journey is complete on this front right now. My price, $830 gives me unlimited run time at night, no need to run it at all during a sunny day (PV power), no trips to the gas station and room for lots of improvements in the future:
Improvements planned for me and options this solution gives people considering it:
- Balance 120v loads - A good idea for anyone using 240v AC
- Make all wiring and gas connections permanent – My current wires and natural gas lines are connected in the event of a failure. So no permitting and really low cost.
- Critter proof, noise reducing, cold weather effect limiting box.
- Upon batter failure wire starter into tractor battery / trickle charge system.
- Automate start and stop of the generator
Important notes about 240V generators:
- 240V generators only give half power if you’re only drawing 120V. In fact the number may be lower as my tests showed.
- Sol Ark can run the generator when grid power is on. This is a great feature allowing you to show an inspector that your generator will not be used to run power into the grid ever. And when you want to test / maintenance run your generator, you can start the generator, connect all your wires if needed, and then flip the grid power off with the generator ready to come online when the sol ark switches too it.
48V generator
I wanted to add this topic because it’s so sad. The ideal generator for most off grid folks is:
- 48v DC power output
- Auto start and stop on a set voltage points
- Motor speed governed by voltage level
- Multi fuel capable
https://www.google.com/search?q=48v...AGFBZIBAzcuMZgBAKABAcABAQ&sclient=products-cc
As you can see by the above link, options are extremely limited and far more expensive.
That’s why I went with what I did, value.
Hope this helps, good luck with your projects!