Agreed. I was just doing this today on my iPhone and iPad and a small Pi 4 touch screen running Ubuntu. The all looked perfect.
ill have to set up that automation for the grid Loss!
I was shocked yesterday to find out that if both the LV6548or LV6048 loose power (no battery or pv) they do NOT go into Grid bypass mode. It was 105 here and the inverters were at 63 degrees C Which is over their 50C operating max temp. So I called my wife to shut off the batteries and PV so the inverters wouldn't go into thermal shutdown. But instead of going into Grid bypass mode, They just shut down and you're S.O.L. - no power at all... So I'm installing a couple of DPDT 80amp relays for an automatic transfer switch function on the loss of the inverters. They'll be here Tue. I'll set up that automation then as well.
So the lesson here is that if it's night time and your batteries unexpectedly die or go into error mode (and SA is crashed), and you don't have a grid tx switch, you go down with no power... glad I figured this out now vs when it matters.
Jeff