These voltages sound way to high for a happy MPPT. Did you do cold weather calculations on VOC?

I did. I will admit I didn't understand as much about solar panels when I originally did the calculations months ago, so I just did it again using the Midnight solar tool.

The coldest it gets here is -10. For the FB21, max MPPT voltage is 600v. At -15 degrees the VOC would be 596v.

If 26.64a is not pushing the limits of the FB21, I could do series parallel and only use 2 MPPT's.

Input values based on the panels spec sheet (SEG-415-BMD-HV) :

1741837566653.png
 
I did. I will admit I didn't understand as much about solar panels when I originally did the calculations months ago, so I just did it again using the Midnight solar tool.

The coldest it gets here is -10. For the FB21, max MPPT voltage is 600v. At -15 degrees the VOC would be 596v.

If 26.64a is not pushing the limits of the FB21, I could do series parallel and only use 2 MPPT's.

Input values based on the panels spec sheet (SEG-415-BMD-HV) :

View attachment 284557
Use the midnight Barcelona calculator, not the classic calculator.

15 in series will be too much for -10

I have similar panels and I did 14 in series.

You might want to do fewer so you are not locked into a 600v inverter forever.
 
I did. I will admit I didn't understand as much about solar panels when I originally did the calculations months ago, so I just did it again using the Midnight solar tool.

The coldest it gets here is -10. For the FB21, max MPPT voltage is 600v. At -15 degrees the VOC would be 596v.

If 26.64a is not pushing the limits of the FB21, I could do series parallel and only use 2 MPPT's.

Input values based on the panels spec sheet (SEG-415-BMD-HV) :

View attachment 284557
Look at the working range for the MPPT not the specs....
 
Look at the working range for the MPPT not the specs....

Understood. The working range is much lower, 440v. At that voltage, it's ~11 panels per series string.

If I series parallel array1: that's 22 panels, then do the same for array2, another 22 panels. that gets me to 44 without needing the third MPPT. If the inverter does end up in the shed, I can hook the 5 existing panels connected to the EG4-3K to the third MPPT. Not a lot, but another 2000Watts.

Now I just need to research the type/specs of MC4 inline fusing required for series parallel...

Thanks for the info gents!
 
Now I just need to research the type/specs of MC4 inline fusing required for series parallel...
None needed. More than 2 strings in parallel you need proper protection.
Personally I use disconnects on every string I run.
I wouldn't use anything inline. A combiner box is the route I would take.
 