The panels have a Voc of 22.3V. The SCC can handle 150V. The 6 current panels in series is 133.8V and will get to 150V at -13ºC/9ºF.8 panels in series should have fried the controller. Need to drop a panel or twp or wire for 4S2P or 2S4P.
I have 8 x 100 SP's. I want to wire them in parallel, what size wire, and what size fuse do I need.
If your 6 current panels are in series why do you want to put them all in parallel when you add 2 more? 4S2P would be a much simpler solution. That would allow you keep the existing 10AWG wires and you wouldn't need a combiner box or fuses. Just a pair of MC4 Y connectors to connect the two series strings together.I have 6 panels or 600w now with 10AWG wires in series.
I currently have a total of 6 100w panels wired in series to a 60a controller with a max of 150v. I want 8 panels, 8 panels in parallel will keep me under 150v. what I am asking is what size fuse do I need inline from the panels to the controller?The panels have a Voc of 22.3V. The SCC can handle 150V. The 6 current panels in series is 133.8V and will get to 150V at -13ºC/9ºF.
So the current 6 panels in series is OK as long as they don't get any colder than -13ºC/9ºF. 8 of these panels can't be put in series on that one controller.
If your 6 current panels are in series why do you want to put them all in parallel when you add 2 more? 4S2P would be a much simpler solution. That would allow you keep the existing 10AWG wires and you wouldn't need a combiner box or fuses. Just a pair of MC4 Y connectors to connect the two series strings together.
That would imply 2S4P. You can do that. And you would need 6AWG to the controller and the fuse as you state. But in post #3 you stated you didn't want new wires. You wanted to use the existing 10AWG.why can't I use 10AWG from the 4 pair of panels, then 6AWG from the 4 branch connector to the controller, with a 50a inline fuse.
I don't need fancy, I need basic and useful.
that is what I am going with. 4 panels in series x 2 sets of 4 panels in series, 2 sets of 4 in parallel.That would imply 2S4P. You can do that. And you would need 6AWG to the controller and the fuse as you state. But in post #3 you stated you didn't want new wires. You wanted to use the existing 10AWG.
I'm suggesting 4S2P. Wire 4 panels in series. Wire another 4 in series. Put those two strings in parallel. Join with Y connectors. Keep the 10AWG all the way to the controller and avoid the need for the extra fuse.
It just seems strange to go from 6 panels all in series to 8 panels mostly in parallel. But either approach works.