Over9000
3rd Shift Ass. Manager @ 2nd-Hand Adult Toy Store
Insulation my friend.
that only goes so far.
Insulation my friend.
It does, inverters make heat in operation too.that only goes so far.
It does, inverters make heat in operation too.
Insulation is an amazing thing.That's true, but this year was cold as shit and hit -10 several times. We're talking a 40 degree swing to compensate for if I wanted to use one of the other choices.
Insulation is an amazing thing.
I camped in a hammock in single digit temperatures... It's amazing. LolIt ain't that amazing! But it's helpful.
I camped in a hammock in single digit temperatures... It's amazing. Lol
Similar to the inverter / AIO efficiency losses keeping themselves warm in a well insulated shed.Your gas was keeping you warm, and I'm not talking propane.
Similar to the inverter / AIO efficiency losses keeping themselves warm in a well insulated shed.
For my 5s3p config on my 250/100 I use Staubli branch connectors for the paralleling and 15A mc4 inline fuses prior to each branch to protect each string.Hey folks,
Each of my panels is 41.75VoC @ 14.13A. I have (9) of them and want to run (3) strings of (3) = 3s3p configuration.
I checked my new inverter (SGN7.6K1HB-48) and it doesn't have built-in PV breakers for its (3) MPPTs. However the unit does have a "PV Switch" on the side of it.
Do I need a PV String Combiner in this case? If so, is there a good one that I should use where I can have breakers instead of fuses?
- If I need one, this product (link) is seemingly a good option and then I'd just need (3) 20A breakers to go with it.
Please let me know your thoughts. Thanks!
For my 5s3p config on my 250/100 I use Staubli branch connectors for the paralleling and 15A mc4 inline fuses prior to each branch to protect each string.
![]()
Staubli 32.0196 MC4 Branch Connector MC4-Evo 2 Female
Shop now for Staubli 32.0196 Branch Socket MC4-Evo 2 Female PV-AZB4-EVO 2-UR.www.stellavolta.com
![]()
Stäubli 32.0197 MC4 Branch Connector MC4-Evo 2 Male
Shop now for Stäubli 32.0197 MC4 Branch Connector MC4-Evo 2 Male PV-AZS4-EVO 2-UR.www.stellavolta.com
Regardless what the spec sheet says, I don't think that inverter for perform optimally with the panels in a 3S config.Hey folks,
Each of my panels is 41.75VoC @ 14.13A. I have (9) of them and want to run (3) strings of (3) = 3s3p configuration.
I checked my new inverter (SGN7.6K1HB-48) and it doesn't have built-in PV breakers for its (3) MPPTs. However the unit does have a "PV Switch" on the side of it.
Yes, you need one.Do I need a PV String Combiner in this case? If so, is there a good one that I should use where I can have breakers instead of fuses?
- If I need one, this product (link) is seemingly a good option and then I'd just need (3) 20A breakers to go with it.
Please let me know your thoughts. Thanks!
I'm sorry I thought you were trying to connect three parallel strings of three to a single mppt . When you say things like 3s3p we think you are connecting that to a single mppt, and then you need fuses or breakers. Combiner box etc.I'm a bit confused. I have (3+) and (3-) strings which I can run directly to my AIO unit which has a PV Switch on it.
Do I need to fuse / add breakers in between? If so, what's the best way to do it?
I'm sorry I thought you were trying to connect three parallel strings of three to a single mppt . When you say things like 3s3p we think you are connecting that to a single mppt, and then you need fuses or breakers. Combiner box etc.
If you only have 9 panels yes just have three strings of three going to the three mppts. No combiner box needed. But that inverter needs 90V minimum to start its mppts. You could potentially have issues getting to that level with only three panels per string (use Vmp figure for that calculation), especially in the heat of summer.
Given you have a 540V top end limit then I would suggest 5 panels on one mppt and 4 on the second, leave third one free.
View attachment 286518
From my understanding, until your SCC starts up, it will see 3x Voc for voltage. Once it starts, the voltage will be pulled down to Vmp. And then once started, the MPPT range is down at 70V-540v. Sounds a little unusual but as spec'd, it sounds like 103.5Vmp will work.Do you think it would really have issues clearing 90V? 10V at that point is a pretty big swing.
3 panels in series won't work, vmp listed is when the PANEL is at 25C ( typically they can run +25-40C on top of ambient in hot weather )
Just as you need to calculate maximum voltage in record cold weather for winter, in the summer heat the reverse is true, voltage will drop. Now that's usually not a concern however when running smaller strings you can run into the minimum startup voltage.Can you explain this more? The math ain't mathing for me.
Just as you need to calculate maximum voltage in record cold weather for winter, in the summer heat the reverse is true, voltage will drop. Now that's usually not a concern however when running smaller strings you can run into the minimum startup voltage.
I guess no harm going with 3s strings and if it turns out thats not enough in the summer change them around to 5s and 4s.
You dont need additional fusing for your planned config of 3 in series to separate mppts.
Yes but you don't need the inline fuse. A switch or breaker for PV shutoff is always a must.Okay. Previously I had all (9) panels in series and ran them through an inline fuse before going into a single MPPT. Was that the right thing to do?
There's no need for a fuse or breaker for a single string or two strings in parallel. They serve no purpose. Once you parallel three strings or more thats when you need ocp.Okay. Previously I had all (9) panels in series and ran them through an inline fuse before going into a single MPPT. Was that the right thing to do?