Hi,

after spending a lot of time to get my IGRID VE II to do what I want by controlling it via the RS232 interface I'm now experiencing a new issue: About all 10 days the inverter goes to fault state with error "01" = "Bus voltage is to high" mostly short after sunrise (Battery mode, On Grid, EnPV/AC, 0A AC Charging). This causes the load to be disconnected :-( If I toggle the inverter On/Off switch, the inverter starts running fine again. Since I didn't find any solution so far, I'm checking the fault state of the inverter using the RS232 connection again and toggling the power switch with a relay. A workaround but not really satisfying...

Does anyone experience similar issues and how did you solve them? Maybe there is a setting (using the calibration program or RS232 command set) to increase the bus voltage tolerance etc.

Regards, Itschi
 
Hi, I have the same issue on one of the 2 inverters I have....
Could you solve it?
Also I don't have same software version on my 2 inverters and would like to flash....
I need to find explanations how to flash inverters REVO2
 
Hi, I have the same issue on one of the 2 inverters I have....
Could you solve it?
Also I don't have same software version on my 2 inverters and would like to flash....
I need to find explanations how to flash inverters REVO2
No, not yet. The EASun-Support is practically not existing (I'll never ever buy from EASun again). The Sorotec engineers told me hat I need a firmware update of the control board. There are some posts in this forum how to do that but you need programmer and the firmware.... Too bad that there is no easy way to update.
 
Hi, I have the same issue on one of the 2 inverters I have....
Could you solve it?
Also I don't have same software version on my 2 inverters and would like to flash....
I need to find explanations how to flash inverters REVO2
Indeed, you need a programmer.
Jlink any version will do, to update the display module.
This one controls just about all the settings.

There are other parts that can be flashed/ updated, bit they require "special version".
Your standard aliX and Amazon crap won't work on that one ( flash MPPT)

Controller board, sorotec didn't release new firmware for "security reasons".

Communication board there is some updates available on this forum :)

For most situations, similar display firmware is enough to be able to run in paralel and/or 3 phase.

Its not difficult to update.
Takes about 3 seconds.

Setting up the software, takes about 5 minutes.

Cheapo china Jlink.. 7 bucks or so (including transport)

Not too bad.

Via wifi or cable would be better.
Sadly, not (yet) available.

Price/quality, the Revo II is a nice unit.
It absolutely has its drawbacks, those are mostly based on wrong sales information.
(Something absolutely normal for China. According to marketing Chinese flashlight have more lumens then the sun)

I don't get 5500 watt via MPPT, max 4200.
I don't get the efficiency..
Nor the low self power consumption.
Probably not longer loads at 5500 watt.
10 minutes go OK :)

The shunts are inaccurate at higher loads, and what is that crazy stuff that it needs to eat 140 watt for being connected to the grid???
(As I use off grid, i don't have this problem)

But....
Compared to the competition that provides real quality (Victron/Outback)..
Who also don't have the advertised low self power consumption, nor the efficiency...
Yes, they do reach the MPPT numbers l, are spot on with the readings and don't have a crazy "connect to grid" drain..

Price wice ...
If I could afford.. perhaps i would buy.
It's more stable.
Getting the same setup for solar and inverter, you can buy 4 Revo units for the price of one comparible Victron.

In 5 to 10 years that the Revo has its end of life...
Development will make the new generation probably to the level the Victron is now :)

We are just getting started, solar panels and lifepo4 getting more affordable, more mainstream.

More Customers, more development, lower prices and overall better quality:)

For now it's a good trade-off.
And for the money saved, the few panels extra to compensate the higher energy use of the unit and a bit lower efficiency, are a steal..

345w poly panels are here $90, including delivery.
If i would need to be connected to the grid...
2 panels and the 140 watt drain is compensated:)
(Plus they last 25 years, probably 3 times the cycle of a Revo II unit)
 
Controller board, sorotec didn't release new firmware for "security reasons".

Unfortunately the Error 01 issue seems to be a problem of the controller board firmware.

Price/quality, the Revo II is a nice unit.
It absolutely has its drawbacks, those are mostly based on wrong sales information.
(Something absolutely normal for China. According to marketing Chinese flashlight have more lumens then the sun)

You are right and I don't complain about the quality trade offs. You get what you pay for and for the price it's quite good. However it's definitely not usable for a normal consumer. Perhaps the biggest issue is with the bad manual and accordingly with the advertising. The different modes and settings with their inter-dependencies are just not well described if at all. This is something that could be solved easy.

 
Error 01 i had in the beginning (January 2020) ...
Some configuration mistakes and a lot of magic smoke...

They made enormous steps compared to 2020 hahaha....
Really.

For series.....
It didn't set master or slave automatically..

So if you had a master slave setting and wanted to change...

Apparently you needed to disconnect all cables (Except battery) and change the setting..
Otherwise 2 masters or 2 slaves...
Magic smoke.

And a few other "surprises"...

Sorotec gave amazing support, shipped me many replacement parts for free.
Thailand Customs was less flexible..
I paid several hundreds of dollars to get the replacement parts... Duties and tax.

Nothing but praise how Sorotec helped out at the start!!!

Now things are different, a LOT more customers, and indeed...
Manuals can be better.
With it, many support calls.
Lots are ignored ?

Pricing doesn't include end user support.
It also normally should not be installed by end user but by electrician / solar specialist.

450v internal isn't a joke, and from experience i can tell you... That hurts like @&#$ to get a bite from it!

2019 the lifepo4 that was used for the testing was S15 setup, 48v...
So standard lithium setting is... S15..
Not so bad, when you like to charge to 85-90%, works perfectly:)
Otherwise first lithium, save, exit. Then user and set the voltage you like.
 
I can confirm Sorotec to be very supportive! It's the opposite with EASun. If they answer at all they continue asking for images etc. Unfortunately I din't find an Sorotec EU reseller yet.
 
I can confirm Sorotec to be very supportive! It's the opposite with EASun. If they answer at all they continue asking for images etc. Unfortunately I din't find an Sorotec EU reseller yet.
Business opertunity hahaha
 
Hi, I have issues connecting 2 Pylontech US3000C in parallel to the inverter. Both batteries work separately, but they won't charge once connected in parallel (but discharge is ok) - inverter shows something like random 50-90W but green SOC is not flashing. Tried at SOC 50% on both, then charged to 80% on both and no changes. If I disconnect the link port cable from one battery, the inverter starts putting current but then the master battery goes into ALM. What is the possible reason for this issue? See attached, the last one shows that charging is ok for a single battery.
 

Attachments

  • Screenshot 2022-12-10 at 23.11.19.png
    Screenshot 2022-12-10 at 23.11.19.png
    1.2 MB · Views: 30
  • Screenshot 2022-12-10 at 23.11.32.png
    Screenshot 2022-12-10 at 23.11.32.png
    1.3 MB · Views: 33
  • Screenshot 2022-12-10 at 23.11.51.png
    Screenshot 2022-12-10 at 23.11.51.png
    1.6 MB · Views: 37
  • Screenshot 2022-12-10 at 23.12.09.png
    Screenshot 2022-12-10 at 23.12.09.png
    1.2 MB · Views: 32
Hi, I have issues connecting 2 Pylontech US3000C in parallel to the inverter. Both batteries work separately, but they won't charge once connected in parallel (but discharge is ok) - inverter shows something like random 50-90W but green SOC is not flashing. Tried at SOC 50% on both, then charged to 80% on both and no changes. If I disconnect the link port cable from one battery, the inverter starts putting current but then the master battery goes into ALM. What is the possible reason for this issue? See attached, the last one shows that charging is ok for a single battery.
Sadly I have no knowledge of "Pylontech US3000C".

Basically what it sounds like is that the BMS of the battery doesn't allow you to use on paralel.

This can be a protective measure due to different SOC, or some other setting that needs to be done on the BMS.

The Revo units have no problem with batteries parallel or series, it doesn't see or feel any difference.

It just sees one big place to dump electricity ?

Some Googling show that more people have the same problem.
This is just one of the results:


Manual doesn't specify to balance the sets, but this is the most important step to do.

My advice:
Charge both sets to 100%.
Nominal voltage is 48v, aka S15.
15* 3.65= 54.75v

What many people seem to forget that reaching this isn't 100% SOC
There is an absorption phase.
Keep the charge on for several hours after reaching the 54.75.

During this stage the BMS will balance the individual cells.
Depending on the imbalance and the power of the BMS to be able to correct, this can take a few hours to a few days.(!)
(Daly BMS can balance 0.08A.
1Ah difference would take 12 hours to balance, that is keeping the pack at 54.75 for 12 hours.
And... To make you more unhappy... That is per cell.

So if 4 cells have 1Ah SOC difference, it will take a Daly BMS 2 days at 54.75 to balance this.

Jikong active balancer BMS would do the same in 4 hours.

If you can spare the time, just keep the units at 54.75 for a few days, then disconnect from the charger.

(Both "stand alone")

After at least 24 hours, measure the voltage of both units.
They should be identical (like 53.78v or so)
53.78 and 53 82 is acceptable.
53.78 and 53.73 is acceptable
53.78 and 53 70...
To large difference in SOC.

You can charge both units again, and keep at 54.75 for an other 2 days:)

If problem isn't SOC related, then most likely the cominication cable between the 2 units is.
This seems to be happening more often then it should.

Good luck and keep us posted on how it goes!!!
 

Attachments

  • US3000C-MANUAL.pdf
    1.6 MB · Views: 28
I’m continuing to see a weird behavior - now my inverter is unable to charge a single battery to over 95% (setting is 6 to 100), is stops at 95% and constantly uses some low wattage like 80w, and bat voltage slowly drops, sometimes percentage also drops to 94 and charges again to 95.

Tried to set battery as “user” - bulk/float 52.4 - it charges to 52.4 and then i see that battery is not charging anymore - SOC leds are all off (was not the case for “lithium” with bms connected via CAN - they were on but not blinking at 80-90w). If at this time I connect CAN - it shows 100%, but voltage slowly drops as well as percentage
 
I’m continuing to see a weird behavior - now my inverter is unable to charge a single battery to over 95% (setting is 6 to 100), is stops at 95% and constantly uses some low wattage like 80w, and bat voltage slowly drops, sometimes percentage also drops to 94 and charges again to 95.

Tried to set battery as “user” - bulk/float 52.4 - it charges to 52.4 and then i see that battery is not charging anymore - SOC leds are all off (was not the case for “lithium” with bms connected via CAN - they were on but not blinking at 80-90w). If at this time I connect CAN - it shows 100%, but voltage slowly drops as well as percentage

Some of the behaviour sounds perfectly normal.

The 80 watt power consumption is normal, for just being turned on, not even providing AC output.

Discharge to from 95 to 94% due this power usage is expected also, just as it is that it will recharge to 95% again.

S15. 15 x 3.65v = 54.75v
With a user setting of 52.4v, the battery won't ever reach 100%.

What ever the inverter or the BMS will tell you about SOC, that information isn't accurate not exact.

Please visit battery University website (google is your friend) and study about lifepo4.

There are just 2 things for sure.
3.65 volt is considered 100% SOC
2.0v is concerned 0% SOC

Considered.. Not in reality.

Charge to 3.65, let it rest for a few hours... It's under 3.65, and can be topped up to 100%.
In other words, it wasn't fully charged.

Discharge to 2.0v, and let it rest for a few hours. It will "bounce back" to something like 2.5v, and can be discharged to 2.0v again..
In other words, it wasn't fully discharged.

To make it more inaccurate:
You can charge above 3.65, even to 4.2v without damaging the battery.
You can discharge below 2.0v (with some damage)
How?
It was 100%, aka full and 0% , aka empty!

And I'm not even starting with the BMS, the device that controls your cells.
Not only won't it have a perfect accurate reading of the voltage, it might be set to stop at 95% charge.

Lead acid was simple
You charge it to 14.4v, and it stabilized at 12.7v, 100% charge.
10.5v "empty"
DOD (depth of discharge) 40% of you wanted many cycles (hundreds)
Oh.. and temperature.. at 30c.. you lose 75% of cycle life..
Simpel because it s*cked.
No matter what you want, they won't last long, and give a terrible efficiency.
And they last longest / are most happy at 100% charge.
Unhappy below 60%

Lifepo4 is different.
It doesn't care that much about temperature, it does NOT like 100% charge, and doesn't mind discharge to even 5%.

Where lead acid a voltage would give a reasonable estimate of the state of charge, lifepo4 doesn't..
At 3.65 and 2.0v, those are "known"
(And at start not correct 100 and 0%)
All measurements between 2.8 and 3.4 volt are a really rough indication of the SOC.
Expect 20-30% error margins (!!)

And then there is the nice part ..
Was the battery in use?
Charge or discharge?
As being charged will give higher voltage reading, discharged a lower reading.

It S*cks.
Not accurate at all.

For the people who need to know exact SOC, within 5% error margins, shunts and special AM meters are needed.

They count the amount of kWh entering and being drawn out the battery.

5% error margins is probably too optimistic.
Not only does the battery not give 100% back of the energy put into it (and this slightly different per pack / installation / environment temperature and number of cycles), the shunt isn't really accurate

In time this 5% error will increase
And needs to be recalibrated.

For a few thousand dollars you can get accurate equipment to measure.
It is smart enough to compensate for the variables and the measurement is within 0.0x% margin.

And this is with DIY, all parts under your own control.

Many pre-build sets undercharge the set.
They pack 280Ah cells and sell it as a 260Ah battery.

Lifepo4 doesn't like being kept at 100%.
While 4.2 should not damage a perfect Cell, most affordable are "B choice", not perfect.
Easy solution, don't top charge!
Why try to find the absolute maximal performance when that increases the risk of failure significant?

Heck, even a Tesla car doesn't top charge, or fully discharge.
Or does an software update suddenly change the hardware battery installed??

Lead acid: if you like them to last as long as possible, DOD 40% and keep as much as possible at 100% charge.

Lifepo4: if you like them to last as long as possible, DOD 80%, and keep them as much as possible at 90% charge.
(So keep between 10 and 90% SOC)

Roughly between 2.7-2.8 and 3.4v
Roughly.

And depending on the factory that made the cells, the age, the temperature, matched internal resistance etc etc etc.

This 2.7/2.8 and 3.4 is not exactly 10 and 90%

It can be 5 or 15% at 2.7/2.8v
It can be 85 to 95% at 3.4v

Expecting that you are able to set between 6 and 100% SOC...
Yes, possible.
With a few thousand dollars on Investment on the right equipment that is calibrated.

Simple volt meter?
While being discharged? (Even slightly)
Ballpark estimate of roughly xx% of SOC..
Crystal Ball, fortune teller,
Like the weather forecast :)

Or perhaps the fuel meter in your car.

You know it's full when you can not fit an other drop of gasoline in the tank.
You know it's empty when the meter is at 0 (probably for the last 50km or so) and the engine stops (note, no other technical problems, only run out of fuel)

Between this, you hava a rough estimation of the amount of fuel left.

You can make an estimation on how much km more you can drive.

You don't know exactly.
And even with a dipstick...
Is the car horizontal?
What is the temperature? As gasoline has expansion and contraction with different temperatures.
And then the road, trafic, and the way you drive. Humidity....
The list is long to be able to accurately estimate the about of liters in the gasoline tank, and even harder how much you can drive!!

A slow discharge of lifepo4 will provide more kWh from a single charge then C0.5 or higher discharge.

The Ammeter and shunts mentioned before... They measure the kWh (ampere and voltage)

Even those "suck", for that simple reason, how fast do you discharge?
How fast do you charge?
Always the same?
Or fluctuations?

You get the idea...
Knowing SOC on a percentage, that's expensive.
Estimation with 10% error margin is normal.
To prevent damage to cells the rule of thumb is not to charge beyond 3.65, not discharge below 2.5v

Also, to stop the charge at 3.65.
No absorption (what would take many hours)
In 20% of the time, 80% of the battery is charged
Result, to get the last 20% it takes 80% of the time, or 5 times as long as the first part.


Realistic, solar, "Fully charged" from 07.00 to 15.00 (or so)
Say 5 to 6 hours.

To really fully charge, you would need an additional 25 hours of sunlight.

Reaching 3.65v isn't fully charged, not 100% SOC, not maximal capacity.

And that is OK.
Having 280Ah, being able to on normal use, use 230-240Ah is a LOT better then lead acid, were one would be able to use 110Ah.

Besides, staying in this 80% will increase the number of cycles significantly.

In other words, if you need to use more then the 80% on a day to day basis (or probably even when you reach this number) you don't have enough storage capacity, and need to extend your battery array.

94-95% is perfect.
Already kinda high.

Don't try to reach the 100%
You probably won't even be able to, due Factory protections and time restraints.
And even if you are able..
The cells that are a little less perfect can get you into trouble.
 
Thank you for such a detailed explanation! My description was a bit inaccurate: at 95% inverter still puts 80w into the battery but voltage/soc is dropping, then it puts say 400-500w for a short period, and we are again at 95%. Sounds interesting why bms is blocking charge by talking via CAN bus, but still accepts more as a user defined. When all components are “smart”, it becomes harder to debug:)
Maybe I can’t override what is in SOC setting of inverter (was 006%-095%), it is not listed in my IGrid manual.
 
You're welcome ?

Tickle. Charge is also "normal".
As Stated, the last absorption phase takes ages.
Feeding 80 watt apparently isn't enough to compensate for the absorption of the set 95%, so from time to time it bursts 500 watt, and then "tickle" with 80 watts.

80 watts on a 10 kWh (?) Battery is peanuts.

Indeed, more "smart" stuff, harder to troubleshoot.

Who listens to who? And to what extent?
The inverter is happy to display the information from the BMS, but is also its own captain.
It doesn't NEED BMS information.
And.... If i would build anything, i would not let third-party decide.

Who is to claim if things go wrong?
I would program hard limits that can't be overruled.

That goes for the BMS and the inverter. (And MPPT)

If your battery is charged to 51v (3.4) and kept at that level (the 80 watt - 500 watt)
You're good to go.

Don't over complicate things, and don't try to fix what isn't broken.

I know that's hard at start.
My BYD setup is working for about 18 months now, and at discharge beyond 50% there is some imbalance between the 6 units.

Nothing that my Jikong active balancer BMS can't handle in the times it's "fully recharged" again.

In between quotes, as I charge to 3.4v
That's enough.
Absolutely not 100%
Probably 95%, and that is perfect.
I usually don't have cells running beyond 3.65v, last time was 2 months ago.

BMS and inverter together work it out just fine.

It takes time.
Even with all batteries top charged as balance between the sets, when you start using them, some will charge / discharge a bit faster then the others.

Just go with the flow and. don't try to control it to strict.

Your BMS should protect from danger.
The inverter (MPPT) should stop charging before danger zone.
The inverter doesn't see individual cells, so one can be too high and an other cell too low.
That's when your BMS should step in for protection.

And the rest?
Let it be.

If you need on regular basis that last few amp hours, you are underpowered.
Tweaking to squeeze as much out of it, trying to find the limits...
Usually bites in the ass.

Especially with China stuff...
As they don't keep safety margins.

I'm curious, did the 2 units now work OK?
After both being top balanced before combining them?
 
No, still can’t get 2x us3000c to charge together, they are stuck at constant 80w charging at whatever level I connect them together (50% both, 80% both, 95% both). Waiting for cables to debug individual cells statuses.
 
You will not believe this, but today is a sunny day and now both batteries in parallel started charging as they should. However, I don't understand why I can't tell my inverter to use the grid for charging when no PV is available. SOC is set to [009 - 100] and it only charged 95% and stopped
 

Attachments

  • IMG_0241.JPG
    IMG_0241.JPG
    139.1 KB · Views: 26
  • IMG_0242.JPG
    IMG_0242.JPG
    98.5 KB · Views: 25
Last edited:
I'm happy for you it works!!

The 95%, we talked about.
That is good, you don't wat to reach 100%.

If you disconnect the connection between the Revo and the BMS, it might be able to pass the "95%".
In my idea that's a limitation opposed by the BMS.

Looking at the battery temperature, you must live somewhere North :) cool .... ??

AC charging, feeding to the grid and those kinds of stuff, i can't help you with.
We don't have grid.

There are a few threads about this, and it seems to be a royal pain in the @ss to het it right, if even possible at all.

I recall something with total MPPT voltage, and obviously the operation mode and the charge settings.

But good that it works, you now know that the batteries are OK.

Why do you want to connect the BMS to the Revo?
It doesn't need to be and 2 captains in a ship seldom works.
Especially when they are from 2 different companies.

Both the battery and the inverter don't need to talk to eachother.

BMS works perfectly without talking to the inverter

The inverter works perfectly without receiving information from BMS

It looks nice, to have the information on the display but that probably gives more issues then that it solves.

When things don't work as they should, minimize the bells and whistles.

Fist make the damn Christmas tree stand, then the decorations.

You probably know it's not so easy to make a tree stand with all decoration in place... Hahaha.

(Sorry, tine of the year)
 
Yeah, I'm from Ukraine, it's -3C outside now, perhaps a bit colder than at your location :)
From my understanding, the inverter is just passively listening on a CAN bus for the data that BMS is providing. I found that potentially helpful for reducing the max charge current, but if those bells and whistles will disrupt normal operations, I'll just remove the inverter-BMS CAN wiring.
 
Sorry to hear about the trouble in your country.

I now understand a bit better the importance to have it operational.

A "quick fix" is an automatic transfer switch (or simple breaker)

If it doesn't work the way it should when connected to the grid.
Disconnect it.
And reconnect when needed.

Its not the first time that i give this advice.
I haven't heard of a better (quick and working) solution.
 
Sorry to hear about the trouble in your country.

I now understand a bit better the importance to have it operational.

A "quick fix" is an automatic transfer switch (or simple breaker)

If it doesn't work the way it should when connected to the grid.
Disconnect it.
And reconnect when needed.

Its not the first time that i give this advice.
I haven't heard of a better (quick and working) solution.
Yeah, this should work. My only concern now is that I don't know what is the expected behavior of this inverter in every case :) Next time I'll probably go with Victron. More expensive, but saves tons of time.
 