Hi Everyone,
I'm new to the Solar Forum, but I am staff on an electronic countermeasure forum so forum life isn't new to me
After years of fending off the solar salesman doorknockers, the ever rising energy cost coupled with the state or the world around us, I decided gaining some energy independence for cost savings and self sustainability was a good idea. Originally I was going to DIY a system, however trying to build a DIY system that meets all the codes/pass inspections and manage that whole install process myself, while not beyond my abilities, it was beyond the amount of time and effort I could afford. I also needed to replace my roof as it was approaching 17 years and was starting to reach end of life. I researched and selected a FL based company to do the roof and solar install after getting several quotes. Ultimately I settled on a full size tier 1 system which based on my energy consumption covers 96% of my yearly use. FL has two tier's based on size of the residential PV system, the larger tier has more requirements and some extra costs involved, it made no sense to add a few more panels to cover that last 4% as that would bump me into tier 2. Going to the max tier 1 size allowed gave me ~11.5KW worth of panels on the roof
I liked the option of microinverters from the standpoint of redundancy (one inverter/panel hasa problem won't impact the other panels). I wanted battery backup too... even though power failures aren't super frequent in my area, if you do have an extended one it can be problematic. When a hurricane threatens FL chaos and food/fuel shortages are plentiful, with the influx of people moving here I can't imagine that situation will improve. I couldn’t comprehend spending the money to install the solar panels knowing that if the grid went down my solar panels would not provide me any power, so batteries were a must. I also wanted a system that would automatically transfer to backup/solar when the grid goes down. We have a small quail farm running here and the incubating eggs and very young quail require strict temperature control, so even a few minutes being without power could be lethal to them. After weighing the options from the various companies Enphase seemed to be the closest match for system for my needs. While their batteries are expensive and the lifespan isn't the best I did really like the fact that the batteries are modular and each contain multiple micro inverters, even if part of a battery unit fails the remainder of it can keep working.
I ended up with 32 365w QCells Q.Peak Duo panels on the south side of my roof on a Iron Ridge rack (I have zero shading over there too) with Enphase IQ7+ microinverters and ~13Kwh of Enphase batteries (10+3). If I have good conditions and my microinverters are producing their max continuous output then it would be about 9500 watts, obviously hitting those numbers consistently may not happen in the real world but the setup is decent so I expect good output.
The install was just completed on friday of last week, but I'm still waiting on FPL to get the new meter installed and grant us permission to produce so I'm not online yet.
Now the way Enphase wants a system like this (partial home backup) installed (and the way the installer installed it) is with a subpanel with a few circuits you want to have run on backup when the grid is down. I do get why, as most folks aren't going to be careful about what they are turning on and when, and having the system overload and shut off frequently would be a bad customer experience... I tried to get them to at least do "cheater" or double breakers to get more circuits but they installed it with singles leaving me only 8 circuits (two of which are the 240volt wastewater grinder) meaning I have 6 circuits running in the house which isn't going to cut it. My house has a lot of circuits (19 of them for lighting and outlets), and with the advent of LED bulbs and energy efficient appliances, many circuits have only a couple hundred watts at max on them so there is plenty of capacity on the Enphase backup power side especially during daylight hours to power significantly more and still recharge the batteries as long as one is conscious of what larger loads are running concurrently.
So once the inspection is complete I intend to embark on the rewire of the system to work the way I want it.
My plan is to install a 200 amp breaker into the Empower on the backup loads circuit (yes this is supported, and whats done when you have more batteries for the "whole home" option) and wire that into my main panel. I will take the 100 amp breaker thats currently connected to the backup side of the empower and switch that to the grid throughput section and connect that to the current 8 circuit "backup loads" panel which is a 125amp max panel. This will effectively swap the function of both circuit breaker panels, the backup loads panel will now be the "unbacked up" loads and the main panel will be backed up. I will simply move the loads back from the current backup loads panel back into the main panel and all circuits will be available, albeit with limited quantities of power due to only having 13KWH of batteries.
The challenge is what to do with the large loads in the main panel. While during good sunlight I can probably run at least one of them at a time, but I don't want them all immediately trying to power up after the system switches to backup as that would overload it and cause a shutdown. My thought is to automate the large loads to automatically disconnect when the system switches to backup, then I can override them manually to use them if I have enough sunlight power. I'm curious if anyone has tried anything like what I'm about to describe before and if it switches fast enough to keep the backup system from seeing the large loads when the system switches from grid to backup.
The thought would be to install contactors between the circuit breakers and the large loads and use those to open the circuits for the large loads automatically on grid failure. I would install a small breaker into the small now non backed up load panel which would supply power for the coil voltage on the contactor, when the grid is live the contactors will be pulled in and the loads will be live, when the grid goes down the coil voltage will go out and the contactors open "instantly" cutting the large loads. The question is do the contactors open quick enough to keep the enphase backup system from seeing any large loads? This setup however only solves part of the problem, cutting the large loads automatically on power grid failure. I would need to install a small manual transfer switch on the circuit that provides the contactor coil voltage to allow me to switch contactor coil voltage supply from grid to backup power so I can manually power up large loads when needed (and I can select which loads by turning off the breakers in the panel, when the contactors pull in only the breakers that are on will actually come alive). This accomplishes the basic need of automatically killing large loads on grid loss and allowing a manual override to run selected large loads on backup if power available allows, however this will still leave one issue that is significant: when grid power returns.
The issues with what I have described above is what happens when the grid comes back. The enphase system instantly switches to backup on grid loss, however it takes several minutes (5 if I recall) after the grid comes back to switch back to grid power. The setup I described above would instantly re-power the contactor coils for the large loads (if the coil voltage transfer switch is still set to grid) when the grid comes up and bring the large loads online before the enphase system transfers back to grid power, likely causing a overload and shutdown. Most of the time when we have a power failure it's a short little blip, so the system will go to backup but then the grid is back up a second later meaning the large loads would get cutout but then come right back before enphase is back to grid power. The solution I have in mind would be to install a time delay relay between the grid power that's feeding the contactor coil voltage and the coil voltage transfer switch, and set that time delay to greater than 5 minutes, say 10 minutes. This means that when grid power returns, if the contactor coil voltage transfer switch is still set to grid the time delay relay will start a 10 minute timer, the enphase system will transfer back to grid in 5 minutes and then when the relay hits 10 minutes it will energize the contactor coils and restart the large loads on grid power. This will also solve the power "blip" where the grid drops and comes right back. If the grid is cutting in and out, each time it drops and returns the relay would start the 10 minute delay again so there won't be a situation where the large loads would be powered up automatically again until after the enphase transfer to grid is complete. If the manual contactor coil voltage trasnfer switch is set to backup, then when the grid returns the large loads won't power back up automatically, but thats not a big deal.
Now I'm a mechanical engineer by trade, so while I have some understanding of electrical stuffs I'm not an expert. So anyone with any experience on the automatic large load transferring process I described above, I'd love to hear your thoughts on my plan, or alternatives if there is a better solution out there. I might look for some support for the relay selection as well making sure I get the right type and configure it correctly so it works they way I need it to.
I have read through @svetz 's Enphase install as he's just a little south of me here in FL and has a very similar setup. He's done some cool things with his system so I'm hoping to do some cool stuff with mine too once it's up and running
-thebravo
I'm new to the Solar Forum, but I am staff on an electronic countermeasure forum so forum life isn't new to me

After years of fending off the solar salesman doorknockers, the ever rising energy cost coupled with the state or the world around us, I decided gaining some energy independence for cost savings and self sustainability was a good idea. Originally I was going to DIY a system, however trying to build a DIY system that meets all the codes/pass inspections and manage that whole install process myself, while not beyond my abilities, it was beyond the amount of time and effort I could afford. I also needed to replace my roof as it was approaching 17 years and was starting to reach end of life. I researched and selected a FL based company to do the roof and solar install after getting several quotes. Ultimately I settled on a full size tier 1 system which based on my energy consumption covers 96% of my yearly use. FL has two tier's based on size of the residential PV system, the larger tier has more requirements and some extra costs involved, it made no sense to add a few more panels to cover that last 4% as that would bump me into tier 2. Going to the max tier 1 size allowed gave me ~11.5KW worth of panels on the roof
I liked the option of microinverters from the standpoint of redundancy (one inverter/panel hasa problem won't impact the other panels). I wanted battery backup too... even though power failures aren't super frequent in my area, if you do have an extended one it can be problematic. When a hurricane threatens FL chaos and food/fuel shortages are plentiful, with the influx of people moving here I can't imagine that situation will improve. I couldn’t comprehend spending the money to install the solar panels knowing that if the grid went down my solar panels would not provide me any power, so batteries were a must. I also wanted a system that would automatically transfer to backup/solar when the grid goes down. We have a small quail farm running here and the incubating eggs and very young quail require strict temperature control, so even a few minutes being without power could be lethal to them. After weighing the options from the various companies Enphase seemed to be the closest match for system for my needs. While their batteries are expensive and the lifespan isn't the best I did really like the fact that the batteries are modular and each contain multiple micro inverters, even if part of a battery unit fails the remainder of it can keep working.
I ended up with 32 365w QCells Q.Peak Duo panels on the south side of my roof on a Iron Ridge rack (I have zero shading over there too) with Enphase IQ7+ microinverters and ~13Kwh of Enphase batteries (10+3). If I have good conditions and my microinverters are producing their max continuous output then it would be about 9500 watts, obviously hitting those numbers consistently may not happen in the real world but the setup is decent so I expect good output.
The install was just completed on friday of last week, but I'm still waiting on FPL to get the new meter installed and grant us permission to produce so I'm not online yet.
Now the way Enphase wants a system like this (partial home backup) installed (and the way the installer installed it) is with a subpanel with a few circuits you want to have run on backup when the grid is down. I do get why, as most folks aren't going to be careful about what they are turning on and when, and having the system overload and shut off frequently would be a bad customer experience... I tried to get them to at least do "cheater" or double breakers to get more circuits but they installed it with singles leaving me only 8 circuits (two of which are the 240volt wastewater grinder) meaning I have 6 circuits running in the house which isn't going to cut it. My house has a lot of circuits (19 of them for lighting and outlets), and with the advent of LED bulbs and energy efficient appliances, many circuits have only a couple hundred watts at max on them so there is plenty of capacity on the Enphase backup power side especially during daylight hours to power significantly more and still recharge the batteries as long as one is conscious of what larger loads are running concurrently.
So once the inspection is complete I intend to embark on the rewire of the system to work the way I want it.
My plan is to install a 200 amp breaker into the Empower on the backup loads circuit (yes this is supported, and whats done when you have more batteries for the "whole home" option) and wire that into my main panel. I will take the 100 amp breaker thats currently connected to the backup side of the empower and switch that to the grid throughput section and connect that to the current 8 circuit "backup loads" panel which is a 125amp max panel. This will effectively swap the function of both circuit breaker panels, the backup loads panel will now be the "unbacked up" loads and the main panel will be backed up. I will simply move the loads back from the current backup loads panel back into the main panel and all circuits will be available, albeit with limited quantities of power due to only having 13KWH of batteries.
The challenge is what to do with the large loads in the main panel. While during good sunlight I can probably run at least one of them at a time, but I don't want them all immediately trying to power up after the system switches to backup as that would overload it and cause a shutdown. My thought is to automate the large loads to automatically disconnect when the system switches to backup, then I can override them manually to use them if I have enough sunlight power. I'm curious if anyone has tried anything like what I'm about to describe before and if it switches fast enough to keep the backup system from seeing the large loads when the system switches from grid to backup.
The thought would be to install contactors between the circuit breakers and the large loads and use those to open the circuits for the large loads automatically on grid failure. I would install a small breaker into the small now non backed up load panel which would supply power for the coil voltage on the contactor, when the grid is live the contactors will be pulled in and the loads will be live, when the grid goes down the coil voltage will go out and the contactors open "instantly" cutting the large loads. The question is do the contactors open quick enough to keep the enphase backup system from seeing any large loads? This setup however only solves part of the problem, cutting the large loads automatically on power grid failure. I would need to install a small manual transfer switch on the circuit that provides the contactor coil voltage to allow me to switch contactor coil voltage supply from grid to backup power so I can manually power up large loads when needed (and I can select which loads by turning off the breakers in the panel, when the contactors pull in only the breakers that are on will actually come alive). This accomplishes the basic need of automatically killing large loads on grid loss and allowing a manual override to run selected large loads on backup if power available allows, however this will still leave one issue that is significant: when grid power returns.
The issues with what I have described above is what happens when the grid comes back. The enphase system instantly switches to backup on grid loss, however it takes several minutes (5 if I recall) after the grid comes back to switch back to grid power. The setup I described above would instantly re-power the contactor coils for the large loads (if the coil voltage transfer switch is still set to grid) when the grid comes up and bring the large loads online before the enphase system transfers back to grid power, likely causing a overload and shutdown. Most of the time when we have a power failure it's a short little blip, so the system will go to backup but then the grid is back up a second later meaning the large loads would get cutout but then come right back before enphase is back to grid power. The solution I have in mind would be to install a time delay relay between the grid power that's feeding the contactor coil voltage and the coil voltage transfer switch, and set that time delay to greater than 5 minutes, say 10 minutes. This means that when grid power returns, if the contactor coil voltage transfer switch is still set to grid the time delay relay will start a 10 minute timer, the enphase system will transfer back to grid in 5 minutes and then when the relay hits 10 minutes it will energize the contactor coils and restart the large loads on grid power. This will also solve the power "blip" where the grid drops and comes right back. If the grid is cutting in and out, each time it drops and returns the relay would start the 10 minute delay again so there won't be a situation where the large loads would be powered up automatically again until after the enphase transfer to grid is complete. If the manual contactor coil voltage trasnfer switch is set to backup, then when the grid returns the large loads won't power back up automatically, but thats not a big deal.
Now I'm a mechanical engineer by trade, so while I have some understanding of electrical stuffs I'm not an expert. So anyone with any experience on the automatic large load transferring process I described above, I'd love to hear your thoughts on my plan, or alternatives if there is a better solution out there. I might look for some support for the relay selection as well making sure I get the right type and configure it correctly so it works they way I need it to.
I have read through @svetz 's Enphase install as he's just a little south of me here in FL and has a very similar setup. He's done some cool things with his system so I'm hoping to do some cool stuff with mine too once it's up and running
-thebravo