Hello! With lots of help I think I have the DC side of my system nailed down. Now I'm stressing over the AC side and could use some advice. I've searched here and on YouTube to no avail.
I have dual Victron Quattro 10k units, dual Victron 450/100 mppts, 1120ah of 48v batteries, 15.3kw of panels (only half will be hooked up for maybe this year). Currently on grid and moving off grid. My plan is to put in a new breaker panel and in the short-term put about 1/2 of the house running on the solar. Once everything is moved over I am right on the border of a 10k unit being enough, but since I live at 9400' in CO and units are derated I decided to double up for redundancy. I have some questions:
1. I understand that I "double my power" if I hook the units in parallel, but it would still be 120v. Wouldn't the same "technically" apply if I hook them up in split phase since each unit is running half of the panel? I can't find anything on how to wire the panel differently for each scenario. Split phase makes sense since that is how panels are normally wired. Is it as simple as the panel gets wired the same and the change occurs in the Quattro unit settings or is the panel wiring different? We currently don't use any 240v electronics, but we do have a backup compressor and dryer that are both 240v so I'd like to easily be able to convert to 240 down the road w/o too much effort.
2. Victron specs 1/0 wire from the inverters (136 amp). 136 x 1.25 = 170 amp breaker right? So I will go with a 200 amp panel. Can the main disconnect just be 200 amp or do I need the less common, more expensive 175 main? BTW the continuous load per inverter is 8000w. So if I divide that by 120 that is 67 amps continuous per inverter. Does any of this change if I choose parallel vs split phase?
I have dual Victron Quattro 10k units, dual Victron 450/100 mppts, 1120ah of 48v batteries, 15.3kw of panels (only half will be hooked up for maybe this year). Currently on grid and moving off grid. My plan is to put in a new breaker panel and in the short-term put about 1/2 of the house running on the solar. Once everything is moved over I am right on the border of a 10k unit being enough, but since I live at 9400' in CO and units are derated I decided to double up for redundancy. I have some questions:
1. I understand that I "double my power" if I hook the units in parallel, but it would still be 120v. Wouldn't the same "technically" apply if I hook them up in split phase since each unit is running half of the panel? I can't find anything on how to wire the panel differently for each scenario. Split phase makes sense since that is how panels are normally wired. Is it as simple as the panel gets wired the same and the change occurs in the Quattro unit settings or is the panel wiring different? We currently don't use any 240v electronics, but we do have a backup compressor and dryer that are both 240v so I'd like to easily be able to convert to 240 down the road w/o too much effort.
2. Victron specs 1/0 wire from the inverters (136 amp). 136 x 1.25 = 170 amp breaker right? So I will go with a 200 amp panel. Can the main disconnect just be 200 amp or do I need the less common, more expensive 175 main? BTW the continuous load per inverter is 8000w. So if I divide that by 120 that is 67 amps continuous per inverter. Does any of this change if I choose parallel vs split phase?