Hi we have a 6KW Growatt hybrid inverter and 4 x 2000c Pylontech batteries, we want to add 2 X 5000c Pylontech batteries as we are exporting a lot to the grid. So the question what is the best way to connect these?
So after much toing and throwing from Voltacon who sold us the cable and the folks who put the panels, and Pylontech, here is where we are at:
Pylontech cables are 4AWG, (peak current capacity 120A, constant 100A) so we understand the need to have the cables doubled up. Pylontech are clear from their point of view all the 6 batteries can be in one stack (UC5000 as master) and can double up their cables from first battery and from last battery and take these to a busbar.
Voltacon are suggesting the need to have the 2000s in one stack and 5000s in another... Either way the doubled up Pylontech cables will be going to a busbar and DC breaker then to the inverter. Can you someone tell me what size/rating cable is needed go from the busbar to DC breaker and DC breaker to inverter? Pylontech saying "you will need to do the calculation". Voltacon saying the 70mm2 cable they sent is needed and will need to be adapted to make the connections, but Voltacon not saying why it needs to be so large, just "that's what is needed"! Someone has kindly sent us a online calculator but we don’t understand enough to use it!
So after much toing and throwing from Voltacon who sold us the cable and the folks who put the panels, and Pylontech, here is where we are at:
Pylontech cables are 4AWG, (peak current capacity 120A, constant 100A) so we understand the need to have the cables doubled up. Pylontech are clear from their point of view all the 6 batteries can be in one stack (UC5000 as master) and can double up their cables from first battery and from last battery and take these to a busbar.
Voltacon are suggesting the need to have the 2000s in one stack and 5000s in another... Either way the doubled up Pylontech cables will be going to a busbar and DC breaker then to the inverter. Can you someone tell me what size/rating cable is needed go from the busbar to DC breaker and DC breaker to inverter? Pylontech saying "you will need to do the calculation". Voltacon saying the 70mm2 cable they sent is needed and will need to be adapted to make the connections, but Voltacon not saying why it needs to be so large, just "that's what is needed"! Someone has kindly sent us a online calculator but we don’t understand enough to use it!