BMEP
New Member
I have a new Sol-Ark whole home backup setup and a really strange problem that, so far, neither myself nor Sol-Ark has not been able to figure out.
Problem: Charge the battery to 100%, once reached, the inverters immediately start using battery power. The inverters will discharge the battery to 96% and then immediately begin charging back to 100%. This cycle continues all day, as long as there's a source to charge. If there is no source (e.g. no PV after sunset), the battery sits at whatever percentage (like 96% for example) it was when charging stopped. I've never seen it below 96% and it's never stayed at 100%
I just got permission to operate from my utility this week so I've had the PV on for a few days and this cycle happens throughout the day. I've had the system operational for 2 months and noticed that the battery would always stay at 96%. I didn't think anything of it because without PV, there was no source of charging (unless I explicitly turned on "grid charge" or forced Gen Charge, both of which I tested but did not leave on). So I believe this behavior has been present all along but because I didn't have a charging source in use, I never noticed it until I finally turned my PV on.
The BMS display agrees with the displays in the inverters as far as state of charge and charge or discharge. i.e. When the BMS display says "97% SOC" so do the Sol-Arks. When the BMS display says "charging 2,000W", so do the Sol-Ark displays.
I reviewed all config settings with Sol-Ark and they see nothing wrong, yet they can't explain why this is happening or how to stop it. There has to either be something I'm missing or a problem with the inverters.
Here's an example of the charge/discharge cycle

One really odd thing I noticed... when the inverters are discharging, one of them discharges at various rates, like you'd expect but the other seems to limit itself to about -3A. In the graph below, blue is one inverter, yellow is the other.

Anybody experienced anything like this before?
Setup details
Problem: Charge the battery to 100%, once reached, the inverters immediately start using battery power. The inverters will discharge the battery to 96% and then immediately begin charging back to 100%. This cycle continues all day, as long as there's a source to charge. If there is no source (e.g. no PV after sunset), the battery sits at whatever percentage (like 96% for example) it was when charging stopped. I've never seen it below 96% and it's never stayed at 100%
I just got permission to operate from my utility this week so I've had the PV on for a few days and this cycle happens throughout the day. I've had the system operational for 2 months and noticed that the battery would always stay at 96%. I didn't think anything of it because without PV, there was no source of charging (unless I explicitly turned on "grid charge" or forced Gen Charge, both of which I tested but did not leave on). So I believe this behavior has been present all along but because I didn't have a charging source in use, I never noticed it until I finally turned my PV on.
The BMS display agrees with the displays in the inverters as far as state of charge and charge or discharge. i.e. When the BMS display says "97% SOC" so do the Sol-Arks. When the BMS display says "charging 2,000W", so do the Sol-Ark displays.
I reviewed all config settings with Sol-Ark and they see nothing wrong, yet they can't explain why this is happening or how to stop it. There has to either be something I'm missing or a problem with the inverters.
Here's an example of the charge/discharge cycle

One really odd thing I noticed... when the inverters are discharging, one of them discharges at various rates, like you'd expect but the other seems to limit itself to about -3A. In the graph below, blue is one inverter, yellow is the other.

Anybody experienced anything like this before?
Setup details
- New install - been in service w/o NEM for 2 months, just got NEM permission to operate this week.
- 400A service
- 2x 15k-2p in parallel - install is just like Page 54 in the current 15k-2P manual
- 17.5kW PV, 5 strings (inv1 has 3 strings, inv2 has 2)
- 10kW HomeGrid Stack'd battery. All settings in Sol-Ark setup reflect the recommended settings from HomeGrid The batter is wired in parallel to both inverters with 4/0 (i.e. oversized) cable. Also, the connections to the inverter "batt" terminals are using bus-bars so both +/- inputs on each inverter are utilized.
- 100% of load on "load" terminals (i.e. no "critical loads panel/setup)
- 26kW generator, on "Gen" terminals, setup for 2 wire start from master inverter
- Battery: All settings match HomeGrid's recommendations. Nothing checked on Smart Load tab.
- Limiter
- Grid Sell checked - limit set to 9,000 (on each inverter)
- Limited Power to Home - unchecked
- Limited Power to Load - checked
- Time of Use - unchecked
- Limiter/Other
- Gen connected to Grid input - unchecked
- Zero Export power 20W
- Batt First - checked
- Load First - unchecked