Warning: Wall of text. Tried to answer as many questions that I myself would probably ask.
I put this in AIO, but could have easily been Offgrid. Moderators feel free.
Shiny Blackface [see attached pic]
$265.68 AliExpress, shipped from Georgia USA
This unit has no control for Grid Tie
Hybrid in that it can charge with AC & PV
There seem to be several flavors of this unit with the same Model Number.
Some have only 1 GND connection on the AC Output side.
I have seen others with a GND on both Input & Output sides.
Manual does not give specs for MPPT input, I estimate 15 - 20 amps
No PV at this moment, but will ramp voltage with a few amps to see when Inverter starts
User Manual is common for SUMRY 3.0KW / 4.0KW
Version number on back cover: 614-02403-00
Planned use:
Hand Truck Build
Limited output: ~3000W
Double pole DC Input Breaker with External Pre-Charge Circuit
Four 12V 100ah LiFePO4 batteries. 2S2P 24V 200ah (with Balancer)
Battery Type Setting: USER, open loop
[I will provide all settings at a later time, if requested]
MUCH TESTING BELOW, may be boring or a chance to learn. YMMV
Measure:
UNPOWERED
Capacitance of DC Input 2200 uf x 8 Electrolytic Caps, 35V = 17,600 uF (Estimated)
Input
L - N Hi Z [Open, for you non Impedance guys/gals]
L - G Hi Z
N - G Hi Z
Output
L - N Hi Z
L - G Hi Z
N - G Hi Z
Input to Output
L - L Hi Z
N - N Short [Common Neutral]
Gnd to Chassis Short
Inside wiring on Terminal block is 10 AWG, with GND 12 AWG
Measure:
POWERED
Power up with 28.5V supply @ 3 amps to change settings.
AC Output 119.9VAC (no load)
When powered Check Output AC with Receptacle tester
Without Input AC Connected: Outlet Tester Shows "Open Ground"
Measured 120VAC from L to N
Measured 43.5VAC L to G
Measured 91.5VAC N to G
No N-G bond on AC Output - NO Utility Input connected.
Removed 28.5V Supply
Connect AC Input cord, wired Ground to G on AC Output connection
With Input AC Connected: Outlet Tester Shows "Correct"
Measured 120VAC from L to N
Measured 120VAC L to G
Measured <1VAC N to G
When AC Input applied, N-G Bond passes to the Output.
Common Neutral, Common Grounds.
Added Space Heater on Medium setting as a LOAD.
715 Watt [Killawatt] / Input & Output Voltage = 115VAC
No battery connected, so AC Pass through.
I was using a crappy long extension cord, probably 16AWG.
Still need to verify Voltage Regulation at higher power. [To Do List]
EDIT: load tested to around ~3KW, with 10AWG wire to AC Output.
Measured voltage was 120.4VAC with a fluke meter at the Output Panel.
Very happy the regulation loaded is spot on.
Supply PV voltage (@ 3 amps) to check Inverter Startup on PV alone.
Expected: 55V
Actual: 56V (drawing 0.250 amps)
All of the above benchtop testing with the following test equipment:
30V, 10A Switching Power Supply
0 - 60V Variable 5A Switching Power Supply
Southwire 120V Outlet Tester
Fluke 177 TrueRMS Multimeter
Killawatt P3
Been a fun morning, more parts arrive tomorrow for Pre-Charge toys
I put this in AIO, but could have easily been Offgrid. Moderators feel free.
Shiny Blackface [see attached pic]
$265.68 AliExpress, shipped from Georgia USA
This unit has no control for Grid Tie
Hybrid in that it can charge with AC & PV
There seem to be several flavors of this unit with the same Model Number.
Some have only 1 GND connection on the AC Output side.
I have seen others with a GND on both Input & Output sides.
Manual does not give specs for MPPT input, I estimate 15 - 20 amps
No PV at this moment, but will ramp voltage with a few amps to see when Inverter starts
User Manual is common for SUMRY 3.0KW / 4.0KW
Version number on back cover: 614-02403-00
Planned use:
Hand Truck Build
Limited output: ~3000W
Double pole DC Input Breaker with External Pre-Charge Circuit
Four 12V 100ah LiFePO4 batteries. 2S2P 24V 200ah (with Balancer)
Battery Type Setting: USER, open loop
[I will provide all settings at a later time, if requested]
MUCH TESTING BELOW, may be boring or a chance to learn. YMMV
Measure:
UNPOWERED
Capacitance of DC Input 2200 uf x 8 Electrolytic Caps, 35V = 17,600 uF (Estimated)
Input
L - N Hi Z [Open, for you non Impedance guys/gals]
L - G Hi Z
N - G Hi Z
Output
L - N Hi Z
L - G Hi Z
N - G Hi Z
Input to Output
L - L Hi Z
N - N Short [Common Neutral]
Gnd to Chassis Short
Inside wiring on Terminal block is 10 AWG, with GND 12 AWG
Measure:
POWERED
Power up with 28.5V supply @ 3 amps to change settings.
AC Output 119.9VAC (no load)
When powered Check Output AC with Receptacle tester
Without Input AC Connected: Outlet Tester Shows "Open Ground"
Measured 120VAC from L to N
Measured 43.5VAC L to G
Measured 91.5VAC N to G
No N-G bond on AC Output - NO Utility Input connected.
Removed 28.5V Supply
Connect AC Input cord, wired Ground to G on AC Output connection
With Input AC Connected: Outlet Tester Shows "Correct"
Measured 120VAC from L to N
Measured 120VAC L to G
Measured <1VAC N to G
When AC Input applied, N-G Bond passes to the Output.
Common Neutral, Common Grounds.
Added Space Heater on Medium setting as a LOAD.
715 Watt [Killawatt] / Input & Output Voltage = 115VAC
No battery connected, so AC Pass through.
I was using a crappy long extension cord, probably 16AWG.
Still need to verify Voltage Regulation at higher power. [To Do List]
EDIT: load tested to around ~3KW, with 10AWG wire to AC Output.
Measured voltage was 120.4VAC with a fluke meter at the Output Panel.
Very happy the regulation loaded is spot on.
Supply PV voltage (@ 3 amps) to check Inverter Startup on PV alone.
Expected: 55V
Actual: 56V (drawing 0.250 amps)
All of the above benchtop testing with the following test equipment:
30V, 10A Switching Power Supply
0 - 60V Variable 5A Switching Power Supply
Southwire 120V Outlet Tester
Fluke 177 TrueRMS Multimeter
Killawatt P3
Been a fun morning, more parts arrive tomorrow for Pre-Charge toys