jbatx
I make stuff with things
..also, I use heltec 16s active balancers on two of my three batteries.
I'll keep playing with it. I haven't had enough panels out or good enough sun to really experiment before I run out of time. Yesterday I added 4 more 435 watt panels for a total of 8 (4s2p). It has been rainy and cloudy most of today until about 3pm when the sun suddenly popped out. I was in the garage and heard the unit taking off. I thought something was going wrong, but it was just taking in over 3400 watts and charging at 53 amps. I was pretty excited. The panels are just tipped up on 5 gallon buckets in my yard. I'm pretty impressed with the setup, I just hope we get some kinks worked out with the firmware eventually. It would be nice to have an on/off/restart switch in the app too.Yes, mine will charge to bulk voltage and the go to float. Issue with that is the lifepo4 batteries need to charge at or close to bulk until there is little to no current flowing. This because they have a pretty flat voltage curve as the reach 90ish % soc. ...so, what I did was set my bulk to 56.7 and my float to 56.
This way float is still charging in that 90% range but it's slower.
This is to avoid run away cells at higher soc. ...I mean, I'm not ever trying to reach 3.65. Even with my top balanced cells I'll start seeing 100ma diff about 3.55 where as normally, I have 10ma diff. So, with float at 3.55 and a 100ma jump in voltage diff, I'm not likely to hit 3.65 for long, if at all.
My array produced about 4kw in good sun. It got to about 80% charge yesterday and then stopped at about 54.1v. Then nothing but draw on the batteries with 3ish hours of sun left. I emailed the company and they're asking for more troubleshooting infoI'll keep playing with it. I haven't had enough panels out or good enough sun to really experiment before I run out of time. Yesterday I added 4 more 435 watt panels for a total of 8 (4s2p). It has been rainy and cloudy most of today until about 3pm when the sun suddenly popped out. I was in the garage and heard the unit taking off. I thought something was going wrong, but it was just taking in over 3400 watts and charging at 53 amps. I was pretty excited. The panels are just tipped up on 5 gallon buckets in my yard. I'm pretty impressed with the setup, I just hope we get some kinks worked out with the firmware eventually. It would be nice to have an on/off/restart switch in the app too.
I have the same question about this unit and deep well pumps. Not much use in an emergency if it cannot handle a deep well pump, 1hp @ 600 ft deep.Thanks for all the info so far, this model has had my attention for awhile.
Can you comment on the surge capacity / capability for motors? I'm uncertain if 1 will handle my well pump...
They have an 18k surge spec for there other LF 6k models; however I have yet to find a surge spec for this model.
I know my 5.5K running 6.5k peak generac handles the pump, while bogging significantly, so this should handle it as well in theory. (waiting for my inrush clamp meter to deliver so I can have some real data)
They answered the question I posted on amazon about surge capacity, I was ready to order .... "Dear customer, the overload capacity of TP6048 is 5sec, @>150% Load ; 10sec, @110%~150%, according to these data, it will certainly handle a 1HP 230V split phase well pump."I have the same question about this unit and deep well pumps. Not much use in an emergency if it cannot handle a deep well pump, 1hp @ 600 ft deep.
135 watts is high, what unit did you end up with?.They answered the question I posted on amazon about surge capacity, I was ready to order .... "Dear customer, the overload capacity of TP6048 is 5sec, @>150% Load ; 10sec, @110%~150%, according to these data, it will certainly handle a 1HP 230V split phase well pump."
Then I saw there reply to my question about idle consumption , 135 watts! I'm almost certain I've ruled this model out. Https://www.amazon.com/dp/B09R42K57J/ref=cm_sw_r_apan_i_SAQC91SBYA9K7GHMYZ4B?_encoding=UTF8&psc=1
Looking back on this old thread I realized I missed your question. I still haven't decided. I was leaning towards the new eg4 now I'm back to this sungold. Going to order real soon.135 watts is high, what unit did you end up with?.
Thank you for the follow up. Would you happen to have a wiring diagram or photo you could share? I'm ready to order this week and want to make sure I'm not missing anything. I plan to use this with grid as backup only, no export.Instead of rehashing all the weird stuff I've experienced with this inverter (lvx6048), here's my final message back to sun gold support.
-----
MY LAST QUESTION TO SUNGOLD:
How should someone set up n-g bonding on this unit?
My grid connection is 240v split phase and has an n-g bond at the breaker on the power pole.
Please be comprehensive in your explanation.
-----
FROM sungold:
Thank you for your inquiry.
In mains mode, the neutral and ground from the input/output are separated. Only in battery inverter mode, the neutral and ground from the output are bonded.
Hope you can understand.
Best Regards
Cindy
---------
MY REPLY:
Yes, thank you. That [incorrect n-g bond] appears to be the root cause of the issues I have experienced. Previously it was n-g bonded on the AC output and also the AC input for the occasions when I had a generator connected. That was not entirely stable but it worked alright. Now I have a permanent mains connection and I did not know to remove the AC output n-g bond. I decided to remove it after considering the symptoms...
symptoms:
1. Erratic and random charge current from AC mains into the battery while "solar only" is selected.
2. Frequent and random fault code 8 shutdowns when PV, AC mains input and batteries are connected. This was not related to a voltage spike as suspected - there was no measured spike during an observed fault and shut down.
After removing the n-g bond on the AC output side both symptoms have stopped.
I suggest that you all start the troubleshooting process with establishing the current n-g bond set up of the system. Maybe you do this already with some customers. This could have saved so much of your time and mine. Additionally, there are numerous threads on solar forums where people are having similar issues and confusions because there is no good documentation on n-g bonding for the LVX6048 inverters. ...not that I can find, anyhow.
Thank you for helping!
----
all the n-g bonds that I'm referring to are external to the unit. They're in breaker boxes. I didn't touch anything in the unit. I don't think I'll have time to do a diagram and I've already left the ranch (where the system is). if I do get time, I'll post it here.Thank you for the follow up. Would you happen to have a wiring diagram or photo you could share? I'm ready to order this week and want to make sure I'm not missing anything. I plan to use this with grid as backup only, no export.
When you say you removed the N-G bond on the AC output, did you open it up and remove the screw?
What are they planning to do special? I'd like to support a US business even its a beefed up clone, I'm still helping US workers.EG4 is about to jump in the pool...
Everything external cleared it up enough for me. Thank you.all the n-g bonds that I'm referring to are external to the unit. They're in breaker boxes. I didn't touch anything in the unit. I don't think I'll have time to do a diagram and I've already left the ranch (where the system is). if I do get time, I'll post it here.
yes it would! When I get some time maybe I will do a dump of it just running and then another with a connection to it. I did NOT check the port it was using so it may be encrypted. I will have to look next time.Nice. It'd be really cool to reverse engineer the communication it's doing and create an open source project for the server...