I'm having a very strange situation and hoping for some insights. I have a Sungrow SH25T 3-Phase inverter, PV and battery, installed as per the manual with a separate 3-Phase meter on the main DB feed - at the moment I'm not exporting to the grid (Export Limitation is enabled and set to export 0%).
When a particular phase is running a higher backup load at any point in time then it seems to be importing from the grid for that specific phase, and at the same time exporting the proportional amount back to the grid on the other two phases. See attached screenshot from the meter on the main DB feed - this shows:
Phase A - importing 1.6kW
Phase B - exporting 1.2kW
Phase C - exporting 0.4kW
Cumulatively the three numbers combined = 0, so the inverter doesn't think it's importing anything (in fact it reports 0 import and export as I would expect) since the numbers balance out to 0. The real net effect though is I'm unnecessarily pulling 1.6kW from the grid on Phase A.
At the time of these values I had a high load on Phase A, low load on Phase B, and medium load on Phase C. If I turn on other appliances to move the high load to a different phase then I see the same thing on that phase - power imported from the grid on the highly loaded phase, and a proportional amount exported back to the grid for the other two phases, again always balancing out to 0.
This is costing me unnecessary grid consumption (backed up by the utility bill). There are a bunch of settings on this inverter but I can't identify any which might influence this behavior. I've made 100% sure there is no phase mismatch anywhere and the meter at the main DB feed is measuring the correct phases too.
Interestingly, if I enable grid export then it masks the problem as long as PV is available (it manages to export enough to not try importing anything), however as soon as PV is unavailable then it's back to the same behavior again.
Any ideas would be welcome!
When a particular phase is running a higher backup load at any point in time then it seems to be importing from the grid for that specific phase, and at the same time exporting the proportional amount back to the grid on the other two phases. See attached screenshot from the meter on the main DB feed - this shows:
Phase A - importing 1.6kW
Phase B - exporting 1.2kW
Phase C - exporting 0.4kW
Cumulatively the three numbers combined = 0, so the inverter doesn't think it's importing anything (in fact it reports 0 import and export as I would expect) since the numbers balance out to 0. The real net effect though is I'm unnecessarily pulling 1.6kW from the grid on Phase A.
At the time of these values I had a high load on Phase A, low load on Phase B, and medium load on Phase C. If I turn on other appliances to move the high load to a different phase then I see the same thing on that phase - power imported from the grid on the highly loaded phase, and a proportional amount exported back to the grid for the other two phases, again always balancing out to 0.
This is costing me unnecessary grid consumption (backed up by the utility bill). There are a bunch of settings on this inverter but I can't identify any which might influence this behavior. I've made 100% sure there is no phase mismatch anywhere and the meter at the main DB feed is measuring the correct phases too.
Interestingly, if I enable grid export then it masks the problem as long as PV is available (it manages to export enough to not try importing anything), however as soon as PV is unavailable then it's back to the same behavior again.
Any ideas would be welcome!