Although Sunny Boy has a neutral wire, it doesn't use it for anything other than looking at voltage. That may be required for compliance now, but earlier models used neutral just to auto-detect 208V, 240V, 277V. Without neutral connected, other jumper positions dictate what voltage it is to use. There was a paper from SMA suggesting an AHJ ought to accept neutral wire same gauge as ground wire, and smaller than L1/L2.
BobK -
For the model I think you have, "Compatible if country data set CA Rule 21 is set"
Early models had to be manually set to backup or island, later came with backup enabled (responded to RS-485).
Yours, it may have locked into "UL-1741" after 10 hours of operation. A grid-guard code issued by SMA is needed to change the setting. A password may be required - perhaps written inside cover of inverter by installer. A personal unlocking key (PUK) from SMA will let you get in.
"UL1741/2016/120 L-N-L is factory-set."
"• UL1741/2016/120 L-N-L • HECO_OHM Rule 14H SDR 1.1/120 L-N-L • CA Rule 21 / 120 L-N-L • NE-ISO / 120 L-N-L"
I've never used your model:
"Procedure: 1. Open the user interface (see Section 4.2, page 24). 2. Log into the user interface (see Section 4.3, page 28). 3. Call up the menu Device Parameters. 4. Click on [Edit parameters]. 5. Log in using the SMA Grid Guard code to change those parameters designated by a lock (only for installers): • Select the menu User Settings (see Section 4.4, page 30). • In the subsequent context menu, select [SMA Grid Guard login]. • Enter the SMA Grid Guard code and select [Login]. 6. Expand the parameter group that contains the parameter which is to be configured. 7. Change the desired parameters. 8. Select [Save all] to save the changes. ☑ The inverter parameters are set."