If you are thinking about putting your batteries 60 feet from your inverters, I think you should re-think what you are doing. Some biblical thing about mountains and Mohamed comes to mind. 240V/50A is #6 for 60 feet Or you can run 4/0 for 60 feet for your 250A of 50V. You can run as small as 3/4 conduit for the #6 I'd probably run #4 in 1 inch. Or whatever for a pair of 4/0. I'm not sure I'd want to pull 4/0 60 feet unless it was an absolutely straight line run. If you decide to pair up the inverters, everything doubles. Likely you are going to run two or three independently fused 4/0's, or you need to get MCM1000 or something, or you could just run THHN 2AWG for 240v to a 100A sub panel. The cost of the cable alone is going to kill you, and the loss for 50V at the current loads we are talking are going to be annoying. Your inverter(s) should be as close as possible to your batteries.