I'm getting ready to install an EG4 6000 watt 48 volt AIO unit. It has a built in 200 amp circuit breaker on the pos. battery input terminal. Do I need a T-Class fuse down near the battery as well.
The blue seas ones are pretty nice, I’ve got 3 of the small ones coming down with me in October. Just watch the two different sizes, guessing you’ll want the bigger one for a power pro.
Related question, do the breakers in the EG4 14.3kWh Wallmount units equate to a T-Class fuse or is it advisable to add one between battery and inverter?
I'll post this as a new thread if it's not appropriate here.