Green Garden
New Member
Hi,
I was sizing wires for the arrays and to achieve a 2% (mathematically) voltage loss was going to require 6 awg wire (2500w with low voltage of around 90). Well my engineer mind kicked in and said this is utterly ridiculous. It’s not possible for me to have lowest voltage and highest current together!!!! That’s like being hot in the winter. So I did all the math for my location and if I use 12awg on all my arrays I end up with a real world site conditions of the following.

As you can see my wiring losses are tiny. These are showing an entire month by hour for a year. I have all 8766 hours if you want it. While looking into chart make sure you pay attention to the units. I couldn’t keep them consistent and still be able to show the losses they totally disappear.
Take June for instance we made just over 2mwh and had line losses of 53kwh this is 2.65% voltage loss this is on the absolute worst month of the year. I would not feel stupid if I use six gauge wire.
I strongly suggest everyone analyze their own system for their own location with hourly calculations for each voltage (power) loss as I have. You might be really surprised what you learn. I’ve always been a big fan of do your own research and make sure it applies to what you want what you need and what you have don’t ever listen to what someone else has done. Please don’t listen to what I’ve done please do it for yourself.!
Here is everything in consistent units.

I was sizing wires for the arrays and to achieve a 2% (mathematically) voltage loss was going to require 6 awg wire (2500w with low voltage of around 90). Well my engineer mind kicked in and said this is utterly ridiculous. It’s not possible for me to have lowest voltage and highest current together!!!! That’s like being hot in the winter. So I did all the math for my location and if I use 12awg on all my arrays I end up with a real world site conditions of the following.

As you can see my wiring losses are tiny. These are showing an entire month by hour for a year. I have all 8766 hours if you want it. While looking into chart make sure you pay attention to the units. I couldn’t keep them consistent and still be able to show the losses they totally disappear.
Take June for instance we made just over 2mwh and had line losses of 53kwh this is 2.65% voltage loss this is on the absolute worst month of the year. I would not feel stupid if I use six gauge wire.
I strongly suggest everyone analyze their own system for their own location with hourly calculations for each voltage (power) loss as I have. You might be really surprised what you learn. I’ve always been a big fan of do your own research and make sure it applies to what you want what you need and what you have don’t ever listen to what someone else has done. Please don’t listen to what I’ve done please do it for yourself.!
Here is everything in consistent units.

Month | PV Generation (kWh) | Load (kWh) | Battery Charge/Discharge (kWh) | Energy Delivered to Load (kWh) | Clipped PV (kWh) | Wire Loss (kWh) | Inverter Loss (kWh) |
| Jan | 923 | 1,503 | 687 | 1,441 | 12 | 23 | 39 |
Feb | 1,098 | 1,331 | 672 | 1,274 | 15 | 27 | 46 |
Mar | 1,574 | 1,525 | 722 | 1,466 | 24 | 37 | 54 |
Apr | 1,812 | 1,471 | 653 | 1,416 | 41 | 45 | 63 |
May | 2,019 | 1,503 | 688 | 1,448 | 58 | 51 | 72 |
Jun | 2,091 | 1,471 | 652 | 1,417 | 66 | 53 | 74 |
Jul | 2,049 | 1,525 | 720 | 1,470 | 61 | 52 | 73 |
Aug | 1,900 | 1,503 | 689 | 1,444 | 48 | 49 | 71 |
Sep | 1,552 | 1,471 | 654 | 1,416 | 29 | 40 | 61 |
Oct | 1,310 | 1,525 | 721 | 1,463 | 20 | 34 | 55 |
Nov | 1,041 | 1,471 | 653 | 1,419 | 13 | 28 | 47 |
Dec | 876 | 1,503 | 687 | 1,442 | 10 | 22 | 38 |
Total | 18,245 | 17,801 | 8,498 | 17,616 | 397 | 461 | 663 |
Last edited: