Looking at the datasheet for the EVE 280Ah cells, rated capacity is specified at 25C +/-2C, meaning 73.4F to 80.6F.
At -20C / 4F the capacity drops by 30% to 200Ah but the discharge curve also gets very wonky, dropping to 2.65V right out of the gate then slowly rising to 3.0V (probably due to internal heat generated at 1C discharge rate) before dropping to 2.5V after 200Ah (43 minutes at 1C).
4F is pretty cold and I don’t need to worry about those temps here in California, but it is 52F / 11C outside right now and we frequently dip to 40F / 4C over winter, so I’m wondering two things:
1/ has anyone characterized discharge performance of these EVE 280Ah cells at moderately cold temperatures around freezing (0C / 32F)?
2/ since the shape of the discharge curve changes so radically at colder temperatures, is anyone going to the trouble of heating their LiFePO4 cells to maintain 25C?
I’m planning to use my 280Ah bank as the backbone of a DC-coupled solar system for self-consumption, which all pencils out pretty nicely using standard 25C discharge curves.
But if I leave the bank at ambient temps and get a completely different discharge curve at winter temps of 40-50F, system performance will be a problem.
I was originally worried about keeping my LiFePO4 cells cool enough and not overheating during charge or discharge, but now that I’ve understood my maximum discharge rate will be very modest (0.12C) and even my peak charge current of under 0.3C is below standard charge rates of 0.5C and will only be for a maximum of 1-2 hours during the hottest part of the day, I’m getting more concerned about assuring my cells are kept warm enough to deliver the performance I’m counting on.
Anyone else have similar concerns and if so, interested in solutions anyone has thrown together...
At -20C / 4F the capacity drops by 30% to 200Ah but the discharge curve also gets very wonky, dropping to 2.65V right out of the gate then slowly rising to 3.0V (probably due to internal heat generated at 1C discharge rate) before dropping to 2.5V after 200Ah (43 minutes at 1C).
4F is pretty cold and I don’t need to worry about those temps here in California, but it is 52F / 11C outside right now and we frequently dip to 40F / 4C over winter, so I’m wondering two things:
1/ has anyone characterized discharge performance of these EVE 280Ah cells at moderately cold temperatures around freezing (0C / 32F)?
2/ since the shape of the discharge curve changes so radically at colder temperatures, is anyone going to the trouble of heating their LiFePO4 cells to maintain 25C?
I’m planning to use my 280Ah bank as the backbone of a DC-coupled solar system for self-consumption, which all pencils out pretty nicely using standard 25C discharge curves.
But if I leave the bank at ambient temps and get a completely different discharge curve at winter temps of 40-50F, system performance will be a problem.
I was originally worried about keeping my LiFePO4 cells cool enough and not overheating during charge or discharge, but now that I’ve understood my maximum discharge rate will be very modest (0.12C) and even my peak charge current of under 0.3C is below standard charge rates of 0.5C and will only be for a maximum of 1-2 hours during the hottest part of the day, I’m getting more concerned about assuring my cells are kept warm enough to deliver the performance I’m counting on.
Anyone else have similar concerns and if so, interested in solutions anyone has thrown together...