Hello, and thanks for reading! Today is the day I begin testing the Eco-Worthy 100Ah 12V LiFePO4 battery. I have four of them. All 4 have been tested individually, and I was able to get at or above 100Ah discharge from each battery. I am charging with Victron 12V/25A IP67 charger, which is properly fused at the bus bar. I am monitoring discharge with Victron SmartShunt. I did zero balance calibration. I set battery settings according to best practices. I am happy with the batteries individually.
With all the talk about batteries failing in parallel, thought it was time for me to do some bench testing of my own.
All 4 batteries have only had 5 discharge/charge cycles each. No problems so far. Topped off batteries individually with victron charger.
Fast forward three weeks.
For the parallel test, I reset the smart shunt, cleared all history, upgraded the firmware, and set it according to best practices, changing the Ah rating from 100 (default) to 400. I connected all 4 batteries with Blue Sea Systems 5/16 bus bar, added a T-class fuse, got all new welding cable with tinned lugs and solid crimps and shrink wrap, wired up the batteries to the bus bars, added the shunt, did zero calibration, and then connected with the same 12V/25A charger, which ran for a few minutes in bulk before hitting absorb and quickly into float. I cleared the history, SOC was set to 100% already, so unplugged the charger.
With charger unplugged I connected the inverter to the shunt and the t-class fuse.
Measurements taken with no inverter connected, inverter in standby idle consumption load, and when running a 1200W heat gun. Discharge is running now.
My math is as follows:
400Ah at 12V is abouth 4800W of energy.
1200W load at 90% efficiency of the inverter = 1333W my guess.
Runtime of 1333W through 4800W capacity is about 3.6 hours. 60 minutes per hour, so 216 minutes.
I think that the inverter is higher than 90% efficiency, but who cares.
The shunt will tell me Ah consumed, and I'll report back.
I will charge back up (long time - 16 hours my estimate at 25A).
Maths: 400Ah by 25A = 16 hours
but...because charger tapers off, heat losses, etc, probably 16.8 hours.
Once it is charged back up, I will report back the updated capacity. If it says <400Ah or >400Ah will let you all know.
Photos attached show:
I have fire extinguisher nearby.
Also recording on my camera in case of fire or a cat walks too close to heat gun. We don't have pets.
With all the talk about batteries failing in parallel, thought it was time for me to do some bench testing of my own.
All 4 batteries have only had 5 discharge/charge cycles each. No problems so far. Topped off batteries individually with victron charger.
Fast forward three weeks.
For the parallel test, I reset the smart shunt, cleared all history, upgraded the firmware, and set it according to best practices, changing the Ah rating from 100 (default) to 400. I connected all 4 batteries with Blue Sea Systems 5/16 bus bar, added a T-class fuse, got all new welding cable with tinned lugs and solid crimps and shrink wrap, wired up the batteries to the bus bars, added the shunt, did zero calibration, and then connected with the same 12V/25A charger, which ran for a few minutes in bulk before hitting absorb and quickly into float. I cleared the history, SOC was set to 100% already, so unplugged the charger.
With charger unplugged I connected the inverter to the shunt and the t-class fuse.
Measurements taken with no inverter connected, inverter in standby idle consumption load, and when running a 1200W heat gun. Discharge is running now.
My math is as follows:
400Ah at 12V is abouth 4800W of energy.
1200W load at 90% efficiency of the inverter = 1333W my guess.
Runtime of 1333W through 4800W capacity is about 3.6 hours. 60 minutes per hour, so 216 minutes.
I think that the inverter is higher than 90% efficiency, but who cares.
The shunt will tell me Ah consumed, and I'll report back.
I will charge back up (long time - 16 hours my estimate at 25A).
Maths: 400Ah by 25A = 16 hours
but...because charger tapers off, heat losses, etc, probably 16.8 hours.
Once it is charged back up, I will report back the updated capacity. If it says <400Ah or >400Ah will let you all know.
Photos attached show:
- state of charge at 100% and battery voltage at 13.83 at start, and zero current, and zero power, and zero amp hours consumed.
- History tab page 1 and 2 showing brand new shunt with min/max battery voltage
- Trends tab showing nothing going on
- Inverter when first connected showing 112V, 60Hz, 0 W/Power being used
- How heat gun plugs into outlet on Giandel 2000W inverter
- heat gun specs
- Idle consumption of 9W / .67A at 13.80 volts and zero amp hours consumed yet
- Heat gun startup at 13.44 volts, 81.66A, 1097W, and .4Ah discharge
- Bricks safely holding heat gun handle incase of gust of wind blowing it into the nearby pool (that would suck)
- Inverter showing 1040W load (for a 1200W heat gun? it's old)
- The new ip67 500A victron shunt
- The T-Class fuse in a blue sea holder
- 4 eco-worthy 100Ah 12V batteries in parallel
- positive bus bar with 4 conductuors, charger, shunt positive, and a conductor going to the t-class fuse
- negative bus bar showing the 4 parallel conductors and the negative from the charger and negative going to the shunt
I have fire extinguisher nearby.
Also recording on my camera in case of fire or a cat walks too close to heat gun. We don't have pets.
Attachments
-
IMG_0430.PNG96.5 KB · Views: 5 -
IMG_0447.jpg209.7 KB · Views: 5 -
IMG_0446.jpg252 KB · Views: 5 -
IMG_0445.jpg260.4 KB · Views: 5 -
IMG_0444.jpg471.5 KB · Views: 4 -
IMG_0443.jpg530.1 KB · Views: 4 -
IMG_0442.jpg154.4 KB · Views: 4 -
IMG_0441.jpg331.4 KB · Views: 3 -
IMG_0439.PNG99.4 KB · Views: 4 -
IMG_0438.PNG98.4 KB · Views: 4 -
IMG_0437.jpg111.8 KB · Views: 4 -
IMG_0436.jpg231.2 KB · Views: 4 -
IMG_0435.jpg154 KB · Views: 4 -
IMG_0433.PNG69.2 KB · Views: 3 -
IMG_0432.PNG100.1 KB · Views: 3 -
IMG_0431.PNG96.9 KB · Views: 3