A lot of people become obsessed with their BMS's balance current, thinking that if it is high, it will magically solve their balancing issues.
They also think that the passive dissipative balancer built into their bms with small resistors is not enough to keep up with the balancing requirements of a solar battery being cycled at low rates..
So they will implement active balancers with a high balance current so that every cycle, there is a solid top balance and their voltages stay within .01V.
The actual problem is that your cells are not matched properly by capacity, state of charge or internal resistance.
This is very common with cheap lithium iron phosphate batteries. Typically this occurs because:
1. The cells are not matched by capacity as well as they should be. This should be done at the factory. Cheaper batteries use cells that were obtained at lowest cost and sometimes there is a 1-3% discrepancy between cells.
2. The cells were not charged to full before putting them together. They were shipped at 50% state of charge or stored before they were assembled, which means they will not be at the same state of charge when they are put together. This is very common. Good cells that are matched, but take a few months to balance.
3. And more rare, the internal resistance is not matched. Especially true with grade b cells. Or large parallel cell packa. If battery is used at high c rates, balancing issues will occur. Especially in excessive temperature environments.
4. You are not charging to 100% often enough. Probably the most important one here on the list. If you're hitting over voltage protection and you never charge your battery to the recommended charge volt, your packs will become imbalanced over time.
Something I want people to consider is that a Tesla EV battery is very large. If you open up the BMS you'll notice that it has very small balancing resistors. This is still true in the LFP packs (NCA packs are much easier to balance and the small balance resistors can compensate for cell drift over time).
The reason these 60kWh LFP batteries can balance without issue is because the packs are matched and assembled properly. That's it. Even at high c rates, if the cells are matched and built properly, they will not have balance issues. You still need to charge to 100% to compensate for cell drift and reset SOC indicator, but it takes a matter of minutes.
If your LFP battery which is only a few kilowatt hours in capacity cannot balance properly, you may have mismatched cells. No amount of balancing will fix this. One will always hit LVD before the others if you top balance it often.
If there is a major imbalance then you have a bad cell. Again, no amount of balancing will fix this.
The BMS balancing circuit is designed to work with these large batteries. It is plenty of balance current.
If your batteries were assembled with the cells at 50% state of charge and they need to be balanced, there is a fast way to do it. There's no need to wait for months.
Charge the battery to 100%. Pop off the top of the battery to access the cells. Then charge each one to 3.65 volts individually with the power supply. What's the current drops below 0.1 amps, disconnect power supply. Usually there will be one or two cells that are lagging excessively.
But keep in mind if you were pulling over 98% capacity, and this pack is built with high quality cells, don't worry about it and just cycle it. It will balance in a few months and you still have good capacity today, so it's not an issue.
They also think that the passive dissipative balancer built into their bms with small resistors is not enough to keep up with the balancing requirements of a solar battery being cycled at low rates..
So they will implement active balancers with a high balance current so that every cycle, there is a solid top balance and their voltages stay within .01V.
The actual problem is that your cells are not matched properly by capacity, state of charge or internal resistance.
This is very common with cheap lithium iron phosphate batteries. Typically this occurs because:
1. The cells are not matched by capacity as well as they should be. This should be done at the factory. Cheaper batteries use cells that were obtained at lowest cost and sometimes there is a 1-3% discrepancy between cells.
2. The cells were not charged to full before putting them together. They were shipped at 50% state of charge or stored before they were assembled, which means they will not be at the same state of charge when they are put together. This is very common. Good cells that are matched, but take a few months to balance.
3. And more rare, the internal resistance is not matched. Especially true with grade b cells. Or large parallel cell packa. If battery is used at high c rates, balancing issues will occur. Especially in excessive temperature environments.
4. You are not charging to 100% often enough. Probably the most important one here on the list. If you're hitting over voltage protection and you never charge your battery to the recommended charge volt, your packs will become imbalanced over time.
Something I want people to consider is that a Tesla EV battery is very large. If you open up the BMS you'll notice that it has very small balancing resistors. This is still true in the LFP packs (NCA packs are much easier to balance and the small balance resistors can compensate for cell drift over time).
The reason these 60kWh LFP batteries can balance without issue is because the packs are matched and assembled properly. That's it. Even at high c rates, if the cells are matched and built properly, they will not have balance issues. You still need to charge to 100% to compensate for cell drift and reset SOC indicator, but it takes a matter of minutes.
If your LFP battery which is only a few kilowatt hours in capacity cannot balance properly, you may have mismatched cells. No amount of balancing will fix this. One will always hit LVD before the others if you top balance it often.
If there is a major imbalance then you have a bad cell. Again, no amount of balancing will fix this.
The BMS balancing circuit is designed to work with these large batteries. It is plenty of balance current.
If your batteries were assembled with the cells at 50% state of charge and they need to be balanced, there is a fast way to do it. There's no need to wait for months.
Charge the battery to 100%. Pop off the top of the battery to access the cells. Then charge each one to 3.65 volts individually with the power supply. What's the current drops below 0.1 amps, disconnect power supply. Usually there will be one or two cells that are lagging excessively.
But keep in mind if you were pulling over 98% capacity, and this pack is built with high quality cells, don't worry about it and just cycle it. It will balance in a few months and you still have good capacity today, so it's not an issue.