Generally speaking, so long as you don't exceed the PV input limits, you can over-panel any modern MPPT-based SCC and it will dynamically control the input power to whatever the output needs. For example, if you were charging a 24V battery at 20A, that's a peak power requirement of 584W (
29.2V x 20A = 584W). You could over-panel your array to say 1,000W and your SCC would dynamically manage the input to only use 584W of it i.e. leaving 416W 'on the table' (
ignoring conversion efficiencies).
Generally speaking ... but in your case, this unit's specs are confusing (
maybe it's me?).
According to
here, I have to assume that the "Maximum Solar Charge Current" refers to the maximum charging current it can supply to your battery and not the PV array's Isc (
Current Short Circuit) i.e. the maximum current the array can generate. Why? Because 145V x 80A = 11,600W (!) and your maximum PV power is only 2,000W! So assuming battery charge current, that is 80A x 29.2V = 2,336W, which is still more that the maximum PV power specification. This makes no sense to me.
I am certainly confused by this unit's specifications, but let's see if we can answer your questions.
What happens if I put
10 250W 24V panels out for the charging the system. Since everything will be 24V...
To clarify, these are not 24V panels, that's just a marketing term, they are 37.6V panels i.e. Voc = 37.6V.
While I know these are used and will produce less than 100%,
I doubt you will find much difference. Solar cells can usually be relied upon to deliver their stated output for 25+ years, unless they've been physically damaged or mistreated.
First, Amps. 10 panels at 100% production would be over 80A input. Will the Growatt just not accept the extra, should it be made?
10 panels connected in parallel could potentially generate 10 x Imp (8.27A) = 82.7A at Vmp = 30.3V = circa 2,500W. But you would never, ever do this because this array configuration would maximise losses and minimise the efficiency of your SCC.
Next is Volts. Since the Growatt is limited to 2kW input, what happens if more than 2kW is being generated?
This is more difficult to answer because, as already mentioned, in order to deliver its rated charge current, the SCC would need 2,336W on the input (ignoring conversion efficiencies), which is above the maximum PV rating! ? But to try to answer the question, so long as you didn't attempt to draw more than 2,000W on the output and so long as you do not exceed 145V on the input, you should be OK i.e. install as many panels as you like.
For example, with a 145V input limit you could connect up to 3 panels in series (
3 x 37.6V = 112.8V, which is OK, but 4 x 37.6V = 150.4V BUST!). You would then connect 3S strings in parallel, so:
- 3S1P (3 panels) = 750W
- 3S2P (6 panels) = 1,500W
- 3S3P (9 panels) = 2,250W (but don't draw more than 2,000W on the output)
- 3S4P (12 panels) = 3,000W (but don't draw more than 2,000W on the output)
You might also want to clarify with Growatt how they intend to deliver the rated charge current into a 24V nominal battery with a 2,000W input restriction.
p.s. To clarify, it is quite common for people to over-panel their SCC i.e. leave power 'on the table', because over-panelling in this way maximises the power you can achieve on cloudy/overcast days. But it's a balance. The more you leave 'on the table' the more power you are wasting on sunny days. A common rule of thumb is to over-panel by around 30%.
Edit: added postscript.