Following some advice I saw in another post I put in place a battery rapid cutoff device for those times a fuse or breaker is not enough. It sets next to my battery bank ready to go.
This is exactly what I was wondering about .... wow really brainy stuff but great content! I am glad I put in busbars, but now I may have made them too beefy, I would have thought less resistance would be best... Now if there was a way to guage busbar specs to try and make use of this ... I will for sure be fixing my parallel hookups!
I've recently posted more results for longer parallel strings: https://diysolarforum.com/threads/calculation-of-parallel-string-currents-addendum.94178/When you say string, that typically refers to serial connections. You have 6 12V in parallel and want to add 4 more in parallel.
Honestly, I'm shocked to hear some manufacturer recommended 8. The most is typically 2-4.
The fundamental issue is that the more batteries you have in parallel, the harder it is to get them to share current equally.
Please see line #6 in my signature. Victron discusses it in detail.
This post:
Hi, everybody! I'm a retired EE. I didn't want my EE skills to fade away after retirment, so I exercise them when I can. Whenever I see a non-trivial circuit analysis problem on one of various forums I frequent, I challenge myself to solve it. Recently I watched Will's video about current sharing in a parallel battery string, and it occurred to me that the string is just a circuit. It could be solved using standard circuit analysis techniques giving theoretical values for the battery currents. I wondered if this has been done before and posted on the web. I found a link on this forum...
- Solarod
- Replies: 149
- Forum: General Battery Discussion
Also discusses it.
Haaaa… on that topic, 40 years + ago I used to cook a lot chilie in the eighty’s on a snowy winter day…….there are several good prepared mix of spices you can buy and add the other fresh stuff to suit your need…Thanks Jim,
And, there is only ONE way to bake proper cornbread.
Thank you for all your work, your theory work is really useful to the community. I did read over your work on larger parallel strings. It is definitely what I am seeing with my array.I've recently posted more results for longer parallel strings: https://diysolarforum.com/threads/calculation-of-parallel-string-currents-addendum.94178/
Yes the pentagon would be a good shape for the center connection peace in my proposed design. Thank you for the suggestion!Consider the "posts" configuration:
View attachment 256838
The batteries don't have to be arranged in a straight line as shown in the image. Is your proposed configuration a version of posts but with the batteries in a circle? The copper disc in the center could be like this: https://diysolarforum.com/threads/c...ing-battery-currents.37937/page-5#post-754439
For a circular "posts" type configuration probably no math is needed.![]()
If one of your 10 batteries develops an internal short, the other 9 have a direct path to send all of their current through to that short. Result: Big big fire. Nine on one isn’t a fair fight.I do have a question of ignorance on my part, this is regarding fuses and or breakers in front of each battery. What exactly are we protecting against?
Thank you for your response! You have given me some more insight into important considerations. I hope you can indulge some more of my ignorance. Specifically which "Series" in the midnight lineup would have the best protection. I personally like the idea of a breaker as it functions both as switch and protective element and they are reusable.When paralleling batteries a fault in a cell in a single one can present at the battery post as a lower voltage. This means that the other parallel batteries will dump current into the faulted battery.
Assume 4 x 100ah batteries and 1 has a fault. 3 batteries dump 100amps into the damaged one so you have 300amps coming in. The BMS might stop this depending on the original fault or it might cause catastrophic failure.
All of the LFP vendors state 4p as the max parallel. The reason is the bms is unable to block the current from more than that in parallel in case of a fault.
They also state 4s as max, because the bms can't stand up to the voltage of more than that in series.
The fuse on each battery is to protect a faulted one from the current dump of the neighbors.
For 12v batteries the MRBF fuse has an AIC of 10ka. At 48v it is 2ka. The class T is 20ka. If you use a breaker in place of a fuse you need to check that it has as high an AIC as the fuse would.
For 12v MRBF
For over that class T or breaker with 20ka AIC, the midnite breakers trip from magnetic instead of heat so they are quicker acting and more sensitive to over current. The also have a high AIC in the right series
Thank you for your response! You have given me some more insight into important considerations. I hope you can indulge some more of my ignorance. Specifically which "Series" in the midnight lineup would have the best protection. I personally like the idea of a breaker as it functions both as switch and protective element and they are reusable.When paralleling batteries a fault in a cell in a single one can present at the battery post as a lower voltage. This means that the other parallel batteries will dump current into the faulted battery.
Assume 4 x 100ah batteries and 1 has a fault. 3 batteries dump 100amps into the damaged one so you have 300amps coming in. The BMS might stop this depending on the original fault or it might cause catastrophic failure.
All of the LFP vendors state 4p as the max parallel. The reason is the bms is unable to block the current from more than that in parallel in case of a fault.
They also state 4s as max, because the bms can't stand up to the voltage of more than that in series.
The fuse on each battery is to protect a faulted one from the current dump of the neighbors.
For 12v batteries the MRBF fuse has an AIC of 10ka. At 48v it is 2ka. The class T is 20ka. If you use a breaker in place of a fuse you need to check that it has as high an AIC as the fuse would.
For 12v MRBF
For over that class T or breaker with 20ka AIC, the midnite breakers trip from magnetic instead of heat so they are quicker acting and more sensitive to over current. The also have a high AIC in the right series
Thank you for your response! You have given me some more insight into important considerations. I hope you can indulge some more of my ignorance. Specifically which "Series" in the midnight lineup would have the best protection. I personally like the idea of a breaker as it functions both as switch and protective element and they are reusable.When paralleling batteries a fault in a cell in a single one can present at the battery post as a lower voltage. This means that the other parallel batteries will dump current into the faulted battery.
Assume 4 x 100ah batteries and 1 has a fault. 3 batteries dump 100amps into the damaged one so you have 300amps coming in. The BMS might stop this depending on the original fault or it might cause catastrophic failure.
All of the LFP vendors state 4p as the max parallel. The reason is the bms is unable to block the current from more than that in parallel in case of a fault.
They also state 4s as max, because the bms can't stand up to the voltage of more than that in series.
The fuse on each battery is to protect a faulted one from the current dump of the neighbors.
For 12v batteries the MRBF fuse has an AIC of 10ka. At 48v it is 2ka. The class T is 20ka. If you use a breaker in place of a fuse you need to check that it has as high an AIC as the fuse would.
For 12v MRBF
For over that class T or breaker with 20ka AIC, the midnite breakers trip from magnetic instead of heat so they are quicker acting and more sensitive to over current. The also have a high AIC in the right series
Thank you for your response! You have given me some more insight into important considerations. I hope you can indulge some more of my ignorance. Specifically which "Series" in the midnight lineup would have the best protection. I personally like the idea of a breaker as it functions both as switch and protective element and they are reusable.When paralleling batteries a fault in a cell in a single one can present at the battery post as a lower voltage. This means that the other parallel batteries will dump current into the faulted battery.
Assume 4 x 100ah batteries and 1 has a fault. 3 batteries dump 100amps into the damaged one so you have 300amps coming in. The BMS might stop this depending on the original fault or it might cause catastrophic failure.
All of the LFP vendors state 4p as the max parallel. The reason is the bms is unable to block the current from more than that in parallel in case of a fault.
They also state 4s as max, because the bms can't stand up to the voltage of more than that in series.
The fuse on each battery is to protect a faulted one from the current dump of the neighbors.
For 12v batteries the MRBF fuse has an AIC of 10ka. At 48v it is 2ka. The class T is 20ka. If you use a breaker in place of a fuse you need to check that it has as high an AIC as the fuse would.
For 12v MRBF
For over that class T or breaker with 20ka AIC, the midnite breakers trip from magnetic instead of heat so they are quicker acting and more sensitive to over current. The also have a high AIC in the right series
Just to clarify, would a breaker like this work as overload protection for a battery.When paralleling batteries a fault in a cell in a single one can present at the battery post as a lower voltage. This means that the other parallel batteries will dump current into the faulted battery.
Assume 4 x 100ah batteries and 1 has a fault. 3 batteries dump 100amps into the damaged one so you have 300amps coming in. The BMS might stop this depending on the original fault or it might cause catastrophic failure.
All of the LFP vendors state 4p as the max parallel. The reason is the bms is unable to block the current from more than that in parallel in case of a fault.
They also state 4s as max, because the bms can't stand up to the voltage of more than that in series.
The fuse on each battery is to protect a faulted one from the current dump of the neighbors.
For 12v batteries the MRBF fuse has an AIC of 10ka. At 48v it is 2ka. The class T is 20ka. If you use a breaker in place of a fuse you need to check that it has as high an AIC as the fuse would.
For 12v MRBF
For over that class T or breaker with 20ka AIC, the midnite breakers trip from magnetic instead of heat so they are quicker acting and more sensitive to over current. The also have a high AIC in the right series